APC 3000 RM XL - Fan noise & firmware upgrade (SUA3000RMXLI3U)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC 3000 RM XL - Fan noise & firmware upgrade (SUA3000RMXLI3U)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:43 AM . Last Modified: ‎2024-03-13 12:40 AM

0 Likes
5
2724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:43 AM . Last Modified: ‎2024-03-13 12:40 AM

APC 3000 RM XL - Fan noise & firmware upgrade (SUA3000RMXLI3U)

Hi all,

A couple of days ago I installed a SUA3000RMXLI3U PSU in a rack together with a 9619 card.

The thing's fan is always on and produces way too much noise for the location the rack is placed in (1 room away from a bedroom). surprisedyell

It seams to me that the fan being always on is more a disadvantage than a gain in my case.

Then I would like to know if the situation could be changed via a firmware upgrade (of the PSU, not of the 9619 card): anyone?

In any case, could someone point me to the procedure to perform a firmware upgrade to the SUA3000RMXLI3U PSU? (apparently I was not able to find it..)
Thank you

Roberto

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 3000
  • fan
  • firmware
  • noise
  • sua3000rmxli3u
  • upgrade
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-29 05:43 AM . Last Modified: ‎2024-03-13 12:39 AM

0 Likes
0
2724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:43 AM . Last Modified: ‎2024-03-13 12:39 AM

Yes you can replace them. No you can't replace them with standard PC fans. These fans are 24V. Additionally they are fairly carefully specced for airflow, so any replacements are going to be pretty much as loud unless you compromise on cooling capacity.

If you want a silent UPS, you should be looking for a previous generation SU unit, although they all hum relatively loudly (the SUA do too, you probably don't hear it above the fan noise).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:43 AM . Last Modified: ‎2024-03-13 12:40 AM

0 Likes
0
2724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:43 AM . Last Modified: ‎2024-03-13 12:40 AM

Depending on the age of your UPS, the fan may always be on.  Below are the reasons it would be on high or on(in earlier models).  Unfortunately, there is no way to upgrade the firmware of the UPS itself.

1. The UPS is on battery.
2. The UPS is charging the battery.
3. The UPS has a load greater than 75%.
4. The internal temperature of the UPS has reached greater than 104 degrees F (40 degrees C).

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:43 AM . Last Modified: ‎2024-03-13 12:40 AM

0 Likes
0
2724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:43 AM . Last Modified: ‎2024-03-13 12:40 AM

Hi Roberto,

The SmartUPS that you have utilizes a fan that has 2 speeds.  On these units the fan will always be on in low speed mode, and will switch to high speed mode should one of the following events occur:

1. The UPS is on battery.
2. The UPS is charging the battery.
3. The UPS has a load greater than 75%.
4. The internal temperature of the UPS has reached greater than 104 degrees F (40 degrees C).


With regards to the firmware upgrade, only the network management card (AP9619) can be upgraded and not the UPS itself.  For the guide on how to perform a firmware upgrade on a network management card, please search for FA156047 from our  FAQ

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:43 AM . Last Modified: ‎2024-03-13 12:40 AM

0 Likes
0
2724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:43 AM . Last Modified: ‎2024-03-13 12:40 AM

Actually, an SUA3000 ups has three fans...there is a large main 4" one which has two speeds and directly cools the Inverter/Charging circuit heat sinks - it's the most critical one. Then there are secondary ~3" ones that cool the battery compartment and the other side of the main board. The 4" fan and the second of the two 3" fans I mentioned also work together to pull cool air in across the transformer pair that is right behind the LED front panel display. You would not want to (nor can you with firmware or other non-intrusive means) defeat the purpose of any of these fans by shutting them down.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:43 AM . Last Modified: ‎2024-03-13 12:39 AM

0 Likes
0
2724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:43 AM . Last Modified: ‎2024-03-13 12:39 AM

Can these fans be replaced with silent running standard PC/Server build fans?

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-29 05:43 AM . Last Modified: ‎2024-03-13 12:39 AM

0 Likes
0
2725
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:43 AM . Last Modified: ‎2024-03-13 12:39 AM

Yes you can replace them. No you can't replace them with standard PC fans. These fans are 24V. Additionally they are fairly carefully specced for airflow, so any replacements are going to be pretty much as loud unless you compromise on cooling capacity.

If you want a silent UPS, you should be looking for a previous generation SU unit, although they all hum relatively loudly (the SUA do too, you probably don't hear it above the fan noise).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore