Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

APC 2200 Question

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC 2200 Question
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

0 Likes
5
1032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

APC 2200 Question

Hopefully this is an easy question for the board.

I have a 2200 (SUA2200R2X147) UPS that hosts two of our three 3750 -E Core switches, 1 2960 G Access switch and 1 SonicWall. Over the last two months we have taken two power hits that have caused this particular UPS to have to switch to battery power. When the UPS does so, the two core switches drop and reboot. The other two devices plugged into this UPS remain online and operational. I called and spoke to the tech support from APC yesterday and they recommended doing a brain dead test on the UPS. I did so this morning then took a spare 2960 and a fan and plugged both devices into the UPS and began testing. I switched the Cisco switch to test out all the plugs in the back of the device and the end result is the UPS works with the 2960. At no time did this switch reboot or lose power. Is there a known issue with the 3750s and this particular model? I read the boards and have seen that the reaction time of the devices is anywhere from 2-4 ms...is there a way to change this setting if in fact this is the reason we keep rebooting those devices? Or sadly will a replacement UPS need to be bought to support these particular devices, seeing as how the current UPS is not able to keep the power going to them?

Thanks in advance for any help given.

Jeff

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 2200
  • 2960
  • 3750
  • apc
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

0 Likes
0
1031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

All,
It looks as if the sensitivity setting on that particular UPS was turned off, which may be the culprit of this issue. Also, the third 3750 is plugged into another UPS, this one an older SU2200RM3U which did not drop the last time we had a power spike. I will be doing some testing to see if in fact the sensitivity setting was the reason that those devices were being rebooted, if not I will come back and post additional information in regards to this issue.

Thanks for all the suggestions and help.

Jeff

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

0 Likes
0
1031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

The SUA family of Smart-UPS exhibit a 2-4 millisecond transfer time to battery and back online. It seems as if this is definitely the problem with the other components dropping during that transfer. In order to rectify this problem, you would need a Smart-UPS with a lower transfer time, and the only family line that covers that is the Smart-UPS RT.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

0 Likes
0
1031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

hi jeff,

you are indeed right. the transfer time to battery is 2-4ms and it is not adjustable because it is a characteristic of the UPS topology, in this case, line interactive. we have UPSs that use a double online conversion which has no transfer time - Smart UPS RT. any of those UPSs or anything larger, should have no transfer time to battery which is needed for some sensitive equipment/servers, etc as you've discovered.

i personally have never come across this particular switch to say i've seen it before

[here is a link to a document that explains UPS topologies|http://www.apcmedia.com/salestools/SADE-5TNM3Y_R5_EN.pdf]

[here is a link to the Smart UPS RT family|http://www.apc.com/products/family/index.cfm?id=223]

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

0 Likes
0
1031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

Before automatically assuming it is in fact a transfer issue, I would recommend doing some research about the power draw of the devices you've mentioned.

Your testing was done using a 2960 which you said never dropped in the first place. If at all possible I'd recommend doing the test with a 3750. I looked up the 3750 and it seems the power supply can differ depending upon how it was purchased, so I can't safely guess how much power it might draw.

Looking at an image of the back of this unit it looks like there are seperate breakers for the outlet groups. Do you currently have the access switch and the sonicwall on the top two outlets and the 3750s on the bottom two?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

0 Likes
0
1031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

All,


It looks as if the sensitivity setting on that particular UPS was turned off, which may be the culprit of this issue. Also, the third 3750 is plugged into another UPS, this one an older SU2200RM3U which did not drop the last time we had a power spike. I will be doing some testing to see if in fact the sensitivity setting was the reason that those devices were being rebooted, if not I will come back and post additional information in regards to this issue.



Thanks for all the suggestions and help.


Jeff

Message was edited by: sysadmin

Message was edited by: sysadmin

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

0 Likes
0
1032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:54 AM . Last Modified: ‎2024-03-08 03:54 AM

All,
It looks as if the sensitivity setting on that particular UPS was turned off, which may be the culprit of this issue. Also, the third 3750 is plugged into another UPS, this one an older SU2200RM3U which did not drop the last time we had a power spike. I will be doing some testing to see if in fact the sensitivity setting was the reason that those devices were being rebooted, if not I will come back and post additional information in regards to this issue.

Thanks for all the suggestions and help.

Jeff

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of