Posted: 2025-01-0902:48 AM
AP9631 vs successor AP9641
Hello all, maybe there is a second for that issue. It's about the successor to AP9631. AP9631 has been discontinued. Question: Is the successor AP9641 1:1 compatible with AP9631?. Many thanks for an answer in advance. Grettings
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-0905:25 AM
Short Answer: A direct replacement
Long Answer: The latest AP9640 / 9641 incorporate a more powerful computer processor to allow higher strength encryption.
Some improvements over the legacy AP9630 / 9631 NMC:
Micro USB Serial, replaceable coin cell, 1GB Ethernet, 30,000 vs 1500 logs, Customer Experience Tab?!?
The AP9640 / 9641 can accept all firmware branch of 7.XX from AP9630 / 9631 legacy. 2.XX for the AP9640 / 9641 and 3.XX SNS firmware that requires a paid subscription.
Questions Ask - If not, and this answered your query please mark this reply as a solution so it may help the next person asking the same. 👍
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-0905:25 AM
Short Answer: A direct replacement
Long Answer: The latest AP9640 / 9641 incorporate a more powerful computer processor to allow higher strength encryption.
Some improvements over the legacy AP9630 / 9631 NMC:
Micro USB Serial, replaceable coin cell, 1GB Ethernet, 30,000 vs 1500 logs, Customer Experience Tab?!?
The AP9640 / 9641 can accept all firmware branch of 7.XX from AP9630 / 9631 legacy. 2.XX for the AP9640 / 9641 and 3.XX SNS firmware that requires a paid subscription.
Questions Ask - If not, and this answered your query please mark this reply as a solution so it may help the next person asking the same. 👍