AP9631 ups total power consumption

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9631 ups total power consumption
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:25 AM . Last Modified: ‎2024-03-12 03:05 AM

0 Likes
5
3169
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:25 AM . Last Modified: ‎2024-03-12 03:05 AM

AP9631 ups total power consumption

Hi,

I have SUA2200I ups with AP9631 NMC (6.1.1 AOS)

I have opened a discussion before about updating NMC firmware. In updated version of the card, I cannot view total power consumption of the UPS?

I can see the logs that calculate percent of UPS capacity that is used every 10 minutes by default. It would be good see total power comsumption at the end of month (in kwh)

Am i missing something?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • ap9631
  • consumption
  • power
  • sua2200i
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:25 AM . Last Modified: ‎2024-03-12 03:05 AM

0 Likes
0
3169
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:25 AM . Last Modified: ‎2024-03-12 03:05 AM

Yes, with a Network Management Card in the UPS, you're supposed to use PowerChute Network Shutdown (PCNS) to achieve graceful shutdown via the network communication in the UPS and your server where PCNS is installed. You don't need PCNS if you don't need to gracefully shutdown anything attached to the UPS.

And yes, you can downgrade if you want to. The new firmware did not add/remove any new features specific to the older SUA UPS platform. Just the look and feel is different. Some new features were added for SMX/SMT model UPSs which are those that for sure support providing kWh and energy usage.

If you downgrade and see something you used to have, see if you can do a screenshot and it will help me get on the same page as you with this.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:25 AM . Last Modified: ‎2024-03-12 03:05 AM

0 Likes
0
3169
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:25 AM . Last Modified: ‎2024-03-12 03:05 AM

This UPS does not support kWh natively. It only provides Voltage, Amperage, % wattage and % VA of capacity. The newer style UPSs (with model prefix SMT/SMX) I believe do. I checked my SMX1000 and it did provide Output Energy Usage: 173.47 kWh. But, this is because the UPS is capable of providing the values to the management card for you to view. The network management card doesn't provide or calculate them directly. On SMT/SMX models, we also provided some information on CO2 usage which is located under Logs->Energy Usage for those UPSs or any other future supported UPS.

The data log is one location to see what this UPS provides as well as under Status -> UPS menu. You can check Logs->Energy Usage but you likely won't see it on your model.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:25 AM . Last Modified: ‎2024-03-12 03:05 AM

0 Likes
0
3169
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:25 AM . Last Modified: ‎2024-03-12 03:05 AM

Ok but i remember i have checked kwh values before updating firmware or by connecting ups directly with usb. I think it is a software issue that could be solved easily.

II also remember my old back ups rs model could give CO2 and kwh values.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:25 AM . Last Modified: ‎2024-03-12 03:05 AM

0 Likes
0
3169
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:25 AM . Last Modified: ‎2024-03-12 03:05 AM

Yes I remember but this feature depends on the UPS, not the AP9631 or PowerChute if you've used that. Did you move your AP9631 to a different model UPS? Is SUA2200I what you read of the sticker on the back?


This UPS, assuming the model is correct, is on an older platform and would not provide kWh natively by itself.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:25 AM . Last Modified: ‎2024-03-12 03:05 AM

0 Likes
0
3169
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:25 AM . Last Modified: ‎2024-03-12 03:05 AM

I have this exactly http://www.apc.com/resource/include/techspec_index.cfm?base_sku=sua2200i

I didnt move NMC to anything else. I only have one smart ups.

I have read that with NMC like AP9631, i can only use powerchute network shutdown utility because it is connected to local network.

I also tried using regular powerchute software which didn't worked with AP9631.

I'm pretty sure i have seen total kwh from web interface before the firmware update. I have checked it couple of times to see my weekly power consumption too. After the update, whole web interface is changed completely, that feature went missing.

In previous firmware,  menu links were placed to left side instead of the top. I may revert back to previous firmware and check it if you are sure about this UPS not supporting this feature

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:25 AM . Last Modified: ‎2024-03-12 03:05 AM

0 Likes
0
3170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:25 AM . Last Modified: ‎2024-03-12 03:05 AM

Yes, with a Network Management Card in the UPS, you're supposed to use PowerChute Network Shutdown (PCNS) to achieve graceful shutdown via the network communication in the UPS and your server where PCNS is installed. You don't need PCNS if you don't need to gracefully shutdown anything attached to the UPS.

And yes, you can downgrade if you want to. The new firmware did not add/remove any new features specific to the older SUA UPS platform. Just the look and feel is different. Some new features were added for SMX/SMT model UPSs which are those that for sure support providing kWh and energy usage.

If you downgrade and see something you used to have, see if you can do a screenshot and it will help me get on the same page as you with this.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of