AP9630 "Application Watchdog"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9630 "Application Watchdog"
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
arj_apc
Crewman arj_apc
Crewman

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:37 AM

0 Likes
7
1170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:37 AM

AP9630 "Application Watchdog"

I would like to implement an "Application Watchdog" using the scheduled outlet restart feature of the UPS AP9630 management card. My plan is to setup a scheduled outlet restart in say half an hours time. My Windows application will then use SNMP to update (say every minute) the scheduled restart time. Whilst the application is happily running the SNMP updates of the scheduled time will prevent the UPS from from ever actually restarting the machine. If the application crashes the SNMP update will not occur and the UPS will perform a soft shutdown and power off restart after half an hour.

Does anyone know if the scheduled timer is happy if the time is constantly updated via SNMP?

Can anyone see any problems with this idea?

Andrew

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
arj_apc
Crewman arj_apc
Crewman

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

0 Likes
0
1170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

Voidstar, Sorry one more question...I assume you have shown the .ini section for shutting down the whole UPS. What is the section name for scheduling a shutdown on just one of the outlet groups?

Andrew

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

0 Likes
0
1170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

The UPS has both a setting and a timer for the outlet off delay. When the outlet is commanded to reboot, the setting is latched into the timer and the timer starts counting down. Today SNMP only exposes the setting, so I think you'll need to cancel the reboot (turn outlet on) and then start a new reboot to get the desired effect.

Reply

Link copied. Please paste this link to share this article on your social media post.

arj_apc
Crewman arj_apc
Crewman

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

0 Likes
0
1170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

voidstar,

But presumably by constantly moving the scheduled time forwards (using SNMP) the reboot command will never actually be issued. I was also wondering if disabling, changing the time and then re-enabling the scheduled event would do the trick. Unfortunately I don't have access to a non-production UPS this week so I cannot test the ideas.

Andrew

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

0 Likes
0
1170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

Hi Andrew, I hadn't considered scheduled reboots, however scheduling is only accessible via the web and INI, not SNMP. I think INI would be the easiest way to do it... upload a new config.ini file (with only the scheduling section) every time you want to kick the watchdog. However this would (depending on duty cycle) complicate FTPing into the NMC for any other reason like updating the firmware so it might be worth doing the work of scripting against the web interface. Might want to either synchronize the NMC's time with the same source as your computer, or take the NMC's time into account when scheduling.

Reply

Link copied. Please paste this link to share this article on your social media post.

arj_apc
Crewman arj_apc
Crewman

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

0 Likes
0
1170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

Are you sure about the scheduled time not being accessible from SNMP? If I look in the powernet417.mib I see...

xATSTestingScheduleTestTime OBJECT-TYPE
   SYNTAX DisplayString
   ACCESS read-write
   STATUS mandatory
   DESCRIPTION
      "The time of day that the scheduled test will occur.
       Specified in the format hh:mm."
   ::= { xATSTestingSchedule 3 }

Which seems to indicate the scheduled time is read/write from SNMP.

Andrew

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

0 Likes
0
1170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

Hi Andrew,

That's the InfraStruXure Automatic Transfer Switch (xATS)... it schedules testing of the attached generator. Great product -- sadly APC never managed to sell it well.

Here's what scheduled shutdown for UPS systems looks like in the INI:

[Scheduling]
; Schedule a shutdown event of the UPS.
; Format: Event# = Status, Interval, Turn Off Time, Turn On Time, PCNS, Name
; Status: Enabled/Disabled/Delete
; Interval: Once, Daily, 1 Week, 2/4/8 Weeks
; Turn Off Time: Time (Daily), Day Time (Weekly), or Date Time (Once)
; Turn On Time: Time (Daily), Day/'Same Day' Time (Weekly), or Date Time (Once)
; PCNS: Enabled/Disabled (PowerChute Network Shutdowns)
; Name: Text description
Event1=Enabled, Once, 01/01/2017 00:00, Immediately, Disabled, Shutdown
Event2=Not Configured
Event3=Not Configured
...
Reply

Link copied. Please paste this link to share this article on your social media post.

arj_apc
Crewman arj_apc
Crewman

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

0 Likes
0
1170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

Ahhh, ok. I did not appreciate that the powernet417.mib file contains details for products other than the Smart-UPS. It's obvious now I know that.

Ok, I'll look into updating the scheduled time by sending a new .INI file.

On the other hand, it would be a great idea to allow the scheduled time to be updated from SNMP. As "Mr Firmware" I'm sure you could squeeze it into the next release!!! 🙂

Anyway, have a good weekend.

Andrew

Reply

Link copied. Please paste this link to share this article on your social media post.

arj_apc
Crewman arj_apc
Crewman

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

0 Likes
0
1171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

Voidstar, Sorry one more question...I assume you have shown the .ini section for shutting down the whole UPS. What is the section name for scheduling a shutdown on just one of the outlet groups?

Andrew

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of