Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

AP9630 Firmware Issue

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: AP9630 Firmware Issue
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
sharperedge_apc
sharperedge_apc
Cadet

Posted: ‎2021-07-01 04:14 AM

0 Likes
1
256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 04:14 AM

AP9630 Firmware Issue

This was originally posted on APC forums on 8/20/2013


Hello, I just recently bought several dozen Smart-UPS 2200's with AP9630's in them, and while initially configuring the network interfaces, I noticed no matter what I did I couldn't get it to send out logs to a standard SMTP server.  In the process of testing and troubleshooting, I saw that there was a new firmware 6.0.6 out, and decided to update to it.   The executable install went perfect and said that it was fully updated.  After waiting a couple minutes I tried to pull up the configuration page to be greeted with "The Application Is Incompatible With This APC OS".  I tried updating the firmware again to see if there was an issue with the firmware, but the program just kicks out "Information --> Unable to verify previous version " and stops dead in its tracks.   I then tried FTP'ing directly into it, switching to binary, and uploading the first of the three firmware files that way, and it halts immediately when the transfer starts.

The network card seems to be in a boot loop, and within the first 10 seconds of it booting up, I am able to log into the configuration page, and when pulling up the logs I get this:

08/18/201302:48:22apcWeb user 'apc' logged in from (edited for security).
08/18/201302:48:19DeviceUPS: Restored the local network management interface-to-UPS communication.
08/18/201302:48:09SystemNetwork service started. IPv6 address (edited for security) assigned by link-local autoconfiguration.
08/18/201302:48:06SystemNetwork service started. System IP is (edited for security) from manually configured settings.
08/18/201302:48:01SystemNetwork Interface restarted.
08/18/201302:47:47SystemTCP/IP stack failure. Module: tfDnsGetMailHost-assertion error line 1266, file(.\treck\source\trresolv.c)
08/18/201302:47:28apcWeb user 'apc' logged in from (edited for security).
08/18/201302:47:21DeviceUPS: Restored the local network management interface-to-UPS communication.
08/18/201302:47:12SystemNetwork service started. IPv6 address (edited for security) assigned by link-local autoconfiguration.
08/18/201302:47:09SystemNetwork service started. System IP is (edited for security) from manually configured settings.
08/18/201302:47:03SystemNetwork Interface restarted.
08/18/201302:42:47SystemTCP/IP stack failure. Module: tfDnsGetMailHost-assertion error line 1266, file(.\treck\source\trresolv.c)

It seems that the TCP-IP stack is failing completely and going into a reboot loop.   What can be done at this point?


The firmware upgrade wasn't stopped prematurely.  The card has been in the unit since right after I bought them.   So on both cases, there's no chance of card / firmware corruption due to a mis-flash of the firmware.

Thanks

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:14 AM

0 Likes
0
256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 04:14 AM

This reply was originally posted by Angela on APC forums on 8/20/2013


You're having the problem that was already posted here -> AP9630 issue with FW6.0.6, reboot loop with TCP/IP stack failure?

If you read through the responses, we've found this to be due to a mail server that is not cached on your local DNS server. Once it is cached, it does not occur anymore. Does this sound possible? The message you get on the web page is because the card goes into a reboot loop and eventually stops after six times of being unable to boot properly.

Alternatively, you could downgrade to v5.1.7 if this is not something you could look into but then you'll miss out on all the new features of v6.0.6 but this is helpful if caching the mail server on the DNS server is not an option. If you do decide to downgrade, I suggest you read this link first: http://www.apc.com/support/index?page=content&country=US〈=en&id=FA167693

If you choose to do that, let me know and I'll have to give you the firmware.

See Answer In Context

Reply
Share
Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:14 AM

0 Likes
0
257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 04:14 AM

This reply was originally posted by Angela on APC forums on 8/20/2013


You're having the problem that was already posted here -> AP9630 issue with FW6.0.6, reboot loop with TCP/IP stack failure?

If you read through the responses, we've found this to be due to a mail server that is not cached on your local DNS server. Once it is cached, it does not occur anymore. Does this sound possible? The message you get on the web page is because the card goes into a reboot loop and eventually stops after six times of being unable to boot properly.

Alternatively, you could downgrade to v5.1.7 if this is not something you could look into but then you'll miss out on all the new features of v6.0.6 but this is helpful if caching the mail server on the DNS server is not an option. If you do decide to downgrade, I suggest you read this link first: http://www.apc.com/support/index?page=content&country=US〈=en&id=FA167693

If you choose to do that, let me know and I'll have to give you the firmware.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc