AP9630/31 "The Application Is Incompatible With This APC OS"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9630/31 "The Application Is Incompatible With This APC OS"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

0 Likes
9
3456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

AP9630/31 "The Application Is Incompatible With This APC OS"

I appear to have run into the following issue:

http://forums.apc.com/spaces/7/ups-management-devices-powerchute-software/forums/general/10822/the-a...

DpZOF76DaCZIbZ5dryXGFA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngDpZOF76DaCZIbZ5dryXGFA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

I have eight of the Smart-UPS 2200RM.  Seven of them have an AP9630, one has a 9631.  Yesterday, one after another, all of them crashed and got stuck on the incompatible screen on the web interface.  I'm able to FTP and telnet to six of them; those were disabled on two.  It looks like most of them are running 6.0.6, though I haven't looked at all yet.  I've been working with one in particular.  When I try to FTP upgrade files to it, it crashes.

I've attached two of the log files I was able to get.  I downloaded event.txt as well, but it looks like it's corrupt; Notepad++ seems to think it's a binary file.  As far as I can tell it's the firmware issue, but I was hoping the logs would give me something definitive.

Is there a way to get this fixed without losing all settings, and maybe more importantly, without having to cut power?

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

0 Likes
0
3455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

I should have thought of that!  It did go back into a reboot and crash cycle, but the web interface was functional long enough I was able to enable FTP.  Once it crashed enough it was on the "Incompatible" screen, the upgrade tool worked.  Thanks!  All eight of them are on the latest release now.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

0 Likes
0
3455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

Small update, I read my monitoring wrong, one of them did not crash.  Unlike the others, it's running 6.5.0 and bootmon 1.08.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

0 Likes
0
3455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

Hi Bryan,

Yes, we need to get this firmware updated and several years old. I think the behavior is likely due to something we addressed. If the application cannot boot after 6 attempts, you'll receive this error. (You can also receive it if your app file is missing but from your screenshot, yours is not. Typically this is seen in the middle of a firmware upgrade which I know also you did not do to cause this.)

Are you able to check the event log? debug.txt and dump.txt is good but we'd hopefully see a little extra in the event log too - either via eventlog command in Telnet or if you can somehow get event.txt through FTP. It may be a TCP/IP stack failure or something which the event log would show.

Some advice I have would be to potentially disable all your email recipients for email generation temporarily and see if it allows you to upgrade firmware after that. Do you have email recipients configured? Each recipient has a setting - email generation (enable/disable) and when you disable it, it allows you to keep the event configuration but just turn off the actual sending of emails. (I know of one TCP/IP stack failure relating to email that would cause this issue, hence my suggestion to avoid having to do other things you want to avoid.)

And I assume you're trying the specific FTP method and instructions for NMC2 mentioned here? http://www.apc.com/us/en/faqs/FA156047 You need to make sure you're putting the files on in the correct order.

We want to get those updated to the latest firmware. AOS 6.5.6/6.5.6 application was just released a few days ago, not sure if that is what you tried. You can download it here: http://www.apc.com/shop/us/en/products/UPS-Network-Management-Card-v6-5-6-Firmware-for-Smart-UPS-Gal... and also feel free to update your 6.5.0 device to this rev as well.

Let me know if you have any questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

0 Likes
0
3456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

Hi,

Yes, I've been using the FTP method from the NMC2 directions, starting with bootmon.  That so far has been unsuccessful.  When I get to 'put bootmon108.bin', I get the following:

200 PORT Command okay.
150 File status okay; about to open data connection.

Then it just crashes.

I was able to use the eventlog command, it's just a loop of network restarts:

     04/24/2018  11:16:56  Device  UPS: Restored the local network management
                                   interface-to-UPS communication.
     04/24/2018  11:16:41  System  Network service started. IPv6 address
                                   FE80::2C0:B7FF:FE58:3AA5 assigned by
                                   link-local autoconfiguration.
     04/24/2018  11:16:37  System  Network service started. System IP is
                                   10.0.0.12 from manually configured
                                   settings.
     04/24/2018  11:16:31  System  Network Interface restarted.
     04/24/2018  11:16:04  Device  UPS: Restored the local network management
                                   interface-to-UPS communication.
     04/24/2018  11:15:49  System  Network service started. IPv6 address
                                   FE80::2C0:B7FF:FE58:3AA5 assigned by
                                   link-local autoconfiguration.
     04/24/2018  11:15:46  System  Network service started. System IP is
                                   10.0.0.12 from manually configured
                                   settings.
     04/24/2018  11:15:40  System  Network Interface restarted.
     04/24/2018  11:15:12  Device  UPS: Restored the local network management
                                   interface-to-UPS communication.
     04/24/2018  11:14:57  System  Network service started. IPv6 address
                                   FE80::2C0:B7FF:FE58:3AA5 assigned by
                                   link-local autoconfiguration.
     04/24/2018  11:14:54  System  Network service started. System IP is
                                   10.0.0.12 from manually configured
                                   settings.
     04/24/2018  11:14:47  System  Network Interface restarted.

Here's the output of the 'email' command, it was previously enabled but I disabled it this morning:

apc>email
E000: Success

  Recipient:    1
  Generation:   disabled
  Address:      alerts@example.com
  Format:       long
  Language:     enUs - English
  Route:        local

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

0 Likes
0
3456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

On 4/24/2018 2:06 PM, Bryan said:

Yes, I've been using the FTP method from the NMC2 directions, starting with bootmon.  That so far has been unsuccessful.  When I get to 'put bootmon108.bin', I get the following:

200 PORT Command okay.
150 File status okay; about to open data connection.

Then it just crashes.

Hmm, when I see it hang like this, it is typically that the FTP data port is blocked or not working. I've seen this with a firewall somewhere (PC or network) or even personally when my old VPN service was running in the background on my PC. Are you able to try via a different PC or look into potentially why this would be blocked?

No TCP/IP stack failure or other obvious reason at least beyond it rebooting after your FTP transfer attempt. Which I guess aligns with what I saw in debug.txt.

Does the .exe method fail too (it uses FTP but wondering what error it tells you)? On the AP9631, you could try USB upgrade method to fix that one and bypass the FTP problem.

If you can't see about the FTP data port being blocked, then we'll have to try and use one of the other methods - XMODEM, or we could try Secure Copy if we enable SSH but this firmware is older so I am not sure if it will work well as we've fixed issues and also SCP clients changed their things on their side. I've used pscp (in the PuTTy suite) with the most success across all firmware revs.

Thoughts?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

0 Likes
0
3456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

Oddly enough, the .exe method is working now on six of them (including the one that hadn't crashed, with the newer firmware).  That seems to be getting them all back online.  It wasn't working yesterday - maybe letting them sit overnight helped, they might have been stuck rebooting last time I tried.

The USB method worked for the AP9631.  One last AP9630 is still stuck, and FTP and telnet are disabled on it.  Is serial the only option for that one?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

0 Likes
0
3456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

Hi Bryan,

Yes, XMODEM over serial for the last AP9630 would be needed, assuming SSH was not enabled and thus, SCP would be an option.

Glad you got most of them going at least!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

0 Likes
0
3456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

Yeah, apparently nothing but HTTP was enabled on it.  I had to order the required serial cable, these were installed years ago and that probably wasn't kept.  Thanks for the help!  I'll update this when the last one is resolved.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

0 Likes
0
3456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

No problem.

Another thing you could try is press/release the pinhole reset button once to reboot the management interface. See if it recovers and you log in via HTTP to turn the other settings on?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

0 Likes
0
3456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:15 AM . Last Modified: ‎2024-03-18 12:00 AM

I should have thought of that!  It did go back into a reboot and crash cycle, but the web interface was functional long enough I was able to enable FTP.  Once it crashed enough it was on the "Incompatible" screen, the upgrade tool worked.  Thanks!  All eight of them are on the latest release now.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore