I recently got a AP9619 refurbished. Connected it into my apc symmetra. Not sure what to do to access it. Network cable is connected, just don't know what the IP would be to connect to it.
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:38 AM . Last Modified: 2024-03-11 12:55 AM
The easiest way is to connect one OUR(need to use ours, it should have came with the UPS) serial cables(part # 940-0024 or 940-1524). You would then need to use hyperterminal and try to login to the NMC. The next step would be to configure the IP settings. Please see the link below for instructions on how to do so. Check the instructions labeled as "2.) Terminal Emulation (Local/direct connection)" If you have any trouble accessing the management card, you may want to check the LEDs on the network card itself. If you have any issues with this, i would recommend contacting tech support at 1-800-800-4272.
http://nam-en.apc.com/app/answers/detail/a_id/3061/kw/configure%20NMC
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:38 AM . Last Modified: 2024-03-11 12:55 AM
The easiest way is to connect one OUR(need to use ours, it should have came with the UPS) serial cables(part # 940-0024 or 940-1524). You would then need to use hyperterminal and try to login to the NMC. The next step would be to configure the IP settings. Please see the link below for instructions on how to do so. Check the instructions labeled as "2.) Terminal Emulation (Local/direct connection)" If you have any trouble accessing the management card, you may want to check the LEDs on the network card itself. If you have any issues with this, i would recommend contacting tech support at 1-800-800-4272.
http://nam-en.apc.com/app/answers/detail/a_id/3061/kw/configure%20NMC