AP9618 no network connection - bad MAC address

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9618 no network connection - bad MAC address
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:26 AM

0 Likes
5
1618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:26 AM

AP9618 no network connection - bad MAC address

This is my 2nd APC AP9618 I'm trying on my SmartUPS-1500RM2U, for some reason everything else seems to be working fine but I get no network connectivity.

If I run a serial cable and connect through a terminal session, I see the MAC address showing all FF's instead of the real MAC address. No matter what I do, it would always say no network. Status shows N-, what can I do to make it work?

Card came originally with 2.02 firmware, I'm updating to 3.73 now, but I'm not sure if this would do it? What causes the MAC address to show like that? Do I have hardware issues somewhere? This is my 2nd card I'm trying.

Much appreciate your help.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • address
  • ap9618
  • bad
  • mac
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:25 AM

0 Likes
0
1618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:25 AM

no, this is an issue with the card

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:26 AM

0 Likes
0
1618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:26 AM

did the first card have that same issue with FF FF FF FF FF FF for a MAC? generally, the cards with that problem will need to be replaced as there is no way for the user to fix it. with a bad MAC, you cannot get the card to work properly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:26 AM

0 Likes
0
1618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:26 AM

Do those cards get more than one supply voltage from the UPS or expansion chassis they're in? I could see something like 3.3V working but 5V not working preventing the SEEPROM VPD from being read out properly. To the original poster - do you have a second UPS you could try one of the all-FF's management cards in to see if it shows a proper MAC address there? To Angela - is there any wan to get to the 10Man... menu (during password reset procedures) which would allow the user to update his VPD as necessary from the label on the unit?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:26 AM

0 Likes
0
1618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:26 AM

no, i cant really suggest that here unfortunately.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:25 AM

0 Likes
0
1618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:25 AM

Thanks for your replies, the card is installed into an 1500VARM2U UPS, I had an environmental card there before and it was working. Both cards behave the same with FF FF... bad MAC address, unfortunately I don't have another UPS to try out.

Could it be something with the UPS itself?

Much appreciate your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:25 AM

0 Likes
0
1619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:32 AM . Last Modified: ‎2024-03-18 01:25 AM

no, this is an issue with the card

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore