Posted: 2021-06-30 09:58 PM
This question was originally posted by Marvin on APC forums on 9/1/2016
I just upgraded my firmware on my APC 3000RM with AP9617 and the upgrade appeared to be successful. But afterwards I couldn't access the router via browser. I can telnet with no problems. All of my settings are intact. I've tried restarting the management interface and that didn't help. We know the network is ok as I can access the device.
Here's the Error
Error: The application was not able to load.
You are attempting to access an APC device.
There was a problem loading the application. Please login to the device via telnet for more details.
About System
Model Number : AP9617
Serial Number : ZA0607004457
Manufacture Date : 02/07/2006
Hardware Revision : A10
MAC Address : 00 C0 B7 7B E5 F6
Flash Type : AMD A29DL322DB
----------------------------------------------------------
Module Information
Description : Network Management Card AOS
----------------------------------------------------------
Name : aos Type : APC OS
Version : 373 Sector : 47
Date : 02/02/2010 Time : 17:05:14
CRC16 : B630
Any ideas on what to try next? Thanks! -Marvin
Posted: 2021-06-30 09:58 PM
This reply was originally posted by Marvin on APC forums on 9/5/2016
That worked great. Thanks!
Posted: 2021-06-30 09:58 PM
This was originally posted on APC forums on 9/2/2016
The first thing to try is running the upgrade again. Since SUMX 372 with AOS 373 is the latest, it looks like AOS successfully updated so the update just needs to put the SUMX app back in.
Posted: 2021-06-30 09:58 PM
This reply was originally posted by Marvin on APC forums on 9/5/2016
That worked great. Thanks!