AP9606 will not recognize SU700RM2U

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9606 will not recognize SU700RM2U
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
139
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:44 AM

0 Likes
10
1648
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:44 AM

AP9606 will not recognize SU700RM2U

I installed a AP9606 into a SU700RM2U and it will not recognize the UPS. After I upgraded the firmware on the AP9606 (to 326b via APC Managment Card Wizard v 2.0.1) I am no longer able to establish standard communications through HyperTerminal via Smart cable. (settings 2400 baud, 8 bit, no parity, 1 stop bit, no flow control). If I remove the AP9606 and connect with HyperTerminal and hit ENTER I recieve NA (I belive this to be Smart Mode?). I have restarted the UPS several times to include a power down and disconect batteries, but still recieve same pompt when connecting to HyperTerminal. If the AP9606 is removed I am able to see the Model of UPS in Power Chute Plus. If I shut the UPS down and install the AP9606 I am unable to see the Model of UPS in Power Chute Plus. During this process I have installed and removed Power Chute Business Edition 7.0.5 (will not connect to UPS), Power Chute Plus (will talk to UPS only if AP9606 is not installed), Power Chute Network Shutdown.

Questions:
1. How to return to standard communication mode in HyperTerminal?
2. How get AP9606 to recognize UPS model?

Any and all help will be appreciated as I am about to go bald from this.

Thank you,
Dennis

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:43 AM

0 Likes
0
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:43 AM

This came up 3rd in my search in Google so I wanted to let others having problems updating their Web/SNMP. I found out updating the aos***.bin works using FTP according to the [Official Guide|http://nam-en.apc.com/app/answers/detail/a_id/768] but updating the sumx***.bin wouldn't. It kept failing to properly upload no matter which version mix and match I did. It did however work using TFTP. After you update the aos according to their guide I just telnet to it then went to 3 for system, then 4 for file transfer, then 3 for TFTP and it asks for the server and file name. I just used tftpd32.exe which is an easy standalone program you can Google. You can also refer to [this thread 3rd post|http://forums.apc.com/spaces/18/server-room-data-center-design-best-practices/forums/general/5791/th...] for the file downloads.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:44 AM

0 Likes
0
1648
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:44 AM

Kevin,

The cable I have is a 940-1524c. From what I have been told the only difference is the length. Is this correct? I have a spare AP9605 do you think I could try that to test the UPS?

Thanks,
Dennis

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:44 AM

0 Likes
0
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:44 AM

Yes the 1524 is just a 15' cable of the 24 cable. If you have a different card I would try just to see if you can get a status LED on the card, but it would be easier to have another Smart-UPS on hand to test the SmartSlot in that.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:44 AM

0 Likes
0
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:44 AM

Hello,

Please keep in mind that so long as the AP9606 is installed, you will not be able to use either PowerChute Plus or PowerChute Business Edition with the UPS. The accessory supercedes serial communication when installed. However, to reset the UPS and install the card properly, do the following:

1. Turn Load/UPS off.
2. Disconnect UPS from utiliy power
3. Depress TEST button for 4-6 seconds until you hear a click and the front LED's flash
4. Install card
5. Turn UPS/Load on.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:43 AM

0 Likes
0
1648
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:43 AM

Kevin,
Thanks for the quick response. I have already inserted the card in accordance with the manufacturers instructions (the same you listed in your reply). This will cause the card AP9606 to work but it still does not recognize the UPS type. The message on the web interface page is something to the extent "Searching for Smart-Ups or Matrix..." Once the card is removed and the RS-232 cable is installed Power Chute Plus will recognize the USP type as Smart-Ups 700.

Questions still out there?
1. How to get out of "Smart Mode?" in hyperterminal?
2. How to get AP9606 to recognize model of Smart-Ups?

Thanks again for the quick response,
Dennis

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:43 AM

0 Likes
0
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:43 AM

I am not sure I understand what you're trying to accomplish in Hyperterminal. There is no interface if the web card is not installed. All you can basically do is press shift+y and get an "SM" repsonse telling you, that with the 940-0024 cable, that it is communicating in smart mode.

As for the firmware, I would re-flash it and see what happens. It's possible that the application layer did not take during the first upload.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:43 AM

0 Likes
0
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:43 AM

Kevin,

Thanks again. Ok, my total misunderstanding on the serial communications. I have that resolved and now understand. But as far as the AP9606 recognizing the SU700, this still has me perplexed.

What I have done:
Installed AP9606 I.A.W. APC instructions.

Flashed firmware downloaded from APCC.com, files aos311.bin and sumx310.bin via Web/SNMP Management Card Wizard v2.0.1. "File transfer complete" was reported.
Complete power down and restart.
Access the the AP9606 via the web interface and the UPS Status reports "Searching for a Smart-UPS or a Matrix-UPS..."


Flashed firmware downloaded from APCC.com, files aos321.bin and sumx321.bin via Web/SNMP Management Card Wizard v2.0.1. "File transfer complete" was reported. Complete power down and restart.
Access the the AP9606 via the web interface and the UPS Status reports "Searching for a Smart-UPS or a Matrix-UPS..."

Flashed firmware downloaded from APCC.com, files aos326b.bin and sumx326.bin via Web/SNMP Management Card Wizard v2.0.1. "File transfer complete" was reported. Complete power down and restart.
Access the the AP9606 via the web interface and the UPS Status reports "Searching for a Smart-UPS or a Matrix-UPS..."

All 3 firmware versions had the same result.

I have loaded PowerChute Business Edition 7.0.5 server and console on machine #1 (winxp sp2) and machine #2 (winxp sp2) which is connected to the SU700 via RS232, has Windows Agent loaded.

While loading Windows Agent on the machine #2 it was unable to identify UPS type and manually configured the serial cable to com1 and make Smart-Ups.

While using Console on Machine #1 to connect to machine #2 I received the following message in the Device List Configuration window: "Failed to apply the configuration to Machine #2"

It seems if I am unable to get the AP9606 to recognize the SU700 then I will not be able to utilize PowerChute Business Edition.

Once again your help would be greatly appreciated.

Thank you,
Dennis

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:43 AM

0 Likes
0
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:43 AM

Dennis,

I understand your comparison now of the 9606 and PCCBE. If the 9606 cannot find the Smart-UPS on three different firmware revisions, and cannot auto-detect, then there may be a problem with the communication on the UPS overall. If that brain-dead procedure has been done numerous times over and still ending up at this, I would definitely lean on that. You are using the 940-0024 cable just to verify correct?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:43 AM

0 Likes
0
1648
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:43 AM

Hello,

I just purchased an apc22003U which came with an AP9606 network card. I just tried to connect it to my network and see no connectivity lights at all. Either at the back of the card or at my network switch. I am running Win 2003 SBS and tried to run PowerChute Network Shutdown 2.2.3 (Pcns223win.zip) I am fine until I get to the part it asks me for the Management Card IP address. I was looking through some threads and noticed that you had advised another person to
1. Turn Load/UPS off
2. Disconnect UPS from utility power
3. Depress TEST button for 4-6 seconds until you hear a click and the front LED's flash
4. Install Card
5. Turn UPS/Load on

Then I read another place where you said Shift-y.

Am I thinking correctly that the above mentioned will also work for me?
Also shouldn't I be seeing at least a link light at the card when connected to my switch?

Thanks,

Tony

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:43 AM

0 Likes
0
1648
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:43 AM

You won't be seeing a link if there's no status. Definitely do steps 1-5. However, if you put the card in hot, there's a chance that either a) the card didn't work to begin with, or b) you fried the card by installing it on the fly. Only UPS's with a bypass circuit can isolate power away from the Smart-Slot and stop the end result of frying cards.

The Shift+Y procedure is just to ensure with, or without the card installed, you can connect to Hyperterminal, and receive an "SM" response ensuring that the SmartSlot is communicating properly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:43 AM

0 Likes
0
1648
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:43 AM

This came up 3rd in my search in Google so I wanted to let others having problems updating their Web/SNMP. I found out updating the aos***.bin works using FTP according to the [Official Guide|http://nam-en.apc.com/app/answers/detail/a_id/768] but updating the sumx***.bin wouldn't. It kept failing to properly upload no matter which version mix and match I did. It did however work using TFTP. After you update the aos according to their guide I just telnet to it then went to 3 for system, then 4 for file transfer, then 3 for TFTP and it asks for the server and file name. I just used tftpd32.exe which is an easy standalone program you can Google. You can also refer to [this thread 3rd post|http://forums.apc.com/spaces/18/server-room-data-center-design-best-practices/forums/general/5791/th...] for the file downloads.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore