Posted: 2021-06-28 12:12 AM . Last Modified: 2024-03-18 11:35 PM
Hello,
I am trying to connect a AP9520TH temperature sensor on a PDU AP8659.
Is this supported for the AP8659 or do i need another sensor?
When i connect the sensor to the temperature port on the pdu it goes on for a few seconds but after that display turns off.
I've got only 1 sensor and also changed the switches on the AP9520TH with no effect.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:12 AM . Last Modified: 2024-03-18 11:35 PM
Hello - AP9520TH is not supported for AP8XXX series Rack PDUs like AP8659. AP9520TH is only for use with our environmental monitoring products like NetBotz.
You must use AP9335T (temperature only) or AP9335TH (temp and humidity) with the Rack PDU. If you obtain the correct sensor model and it does not show up correctly when you connect it to the designated sensor port, you may want to press and release the pinhole reset button once on the display as connecting the incorrect sensor could cause errors. A reboot (will not affect outlet status) will clear any of those errors up if they don't automatically clear.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:12 AM . Last Modified: 2024-03-18 11:35 PM
Hello - AP9520TH is not supported for AP8XXX series Rack PDUs like AP8659. AP9520TH is only for use with our environmental monitoring products like NetBotz.
You must use AP9335T (temperature only) or AP9335TH (temp and humidity) with the Rack PDU. If you obtain the correct sensor model and it does not show up correctly when you connect it to the designated sensor port, you may want to press and release the pinhole reset button once on the display as connecting the incorrect sensor could cause errors. A reboot (will not affect outlet status) will clear any of those errors up if they don't automatically clear.