AP9211 firmware upgrade

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9211 firmware upgrade
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:22 PM . Last Modified: ‎2024-02-14 11:58 PM

0 Likes
4
1722
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:22 PM . Last Modified: ‎2024-02-14 11:58 PM

AP9211 firmware upgrade

Hello!

I recently acquired a used AP9211 with web management card for my home computer cluster (ovirt running on RHEL7).  I was able to get the AP9211 configured for my network and can telnet and access the web management page of it as well.  Now I would like to determine if the firmware and software needs to be upgraded and with that I have two questions.

1. How can I determine the version of firmware and software currently installed?

2. Where can I download the latest (I understand that this is a very old product and "latest" may be years old) firmware and software?

I have searched these forums and google but all links for the firmware for this device see to be behind password protected sites or deadends.

Thanks for your time and guidance!!

Mike

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:22 PM . Last Modified: ‎2024-02-14 11:57 PM

0 Likes
0
1723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:22 PM . Last Modified: ‎2024-02-14 11:57 PM

Thanks for the response and info!

Since the PDU didn’t cost me very much I figured I didn’t have much to lose so I went ahead and upgraded per the forked.net instructions and links.  The upgrade went fine and I am now running with those versions.  So those do actually work with the ap9606 but both had to be upgraded to get the web app working again.  FTP worked the entire time.  

Cheers!

Mike

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:22 PM . Last Modified: ‎2024-02-14 11:57 PM

0 Likes
0
1723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:22 PM . Last Modified: ‎2024-02-14 11:57 PM

I may have found part of what I was looking for.  In telnet I was able to find the following:

        -----------------------------------------------------------------------

        About System

 

        Model Number      : AP9606       Serial Number     : WA0040013441

        Manufacture Date  : 09/29/2000   Hardware Revision : G9

        MAC Address       :

        Flash Vendor      : AMD

 

        Press to continue...

 

        -----------------------------------------------------------------------

        Module Information 

 

        Description : MasterSwitch APP

        -----------------------------------------------------------------------

        Name        : ms210.bin         Type        : StatApp

        Version     : v2.1.0            Sector      : 4

        Date        : 07/07/2000        Time        : 16:33:46

        CRC16       : 5F32

 

I am guessing that there might be a newer version of the MasterSwitch APP (assuming the date of 7/7/2000 is correct for this version).  So, is there a download link for a newer version of this software?  And, assuming there is a newer version of the MasterSwitch software, is there also a link for the latest AP9211 firmware?  Since the MasterSwitch APP doesn't look upgraded I am assuming the AP9211 firmware also could use a refresh, even if the latest is over 10 years old... 🙂

Thanks again!

Mike

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:22 PM . Last Modified: ‎2024-02-14 11:57 PM

0 Likes
0
1723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:22 PM . Last Modified: ‎2024-02-14 11:57 PM

I was able to find what seems to be the correct software here : http://www.forked.net/forums/viewtopic.php?f=13&t=3490

Latest Firmware for AP9211: 
http://www.forked.net/ap9211/aos309a.bin 
http://www.forked.net/ap9211/ms225a.bin 

These are from 2005 according to the website.  Are these the correct versions?  Is there a more official location to find very old firmware like these?  

Thanks again!

Mike

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:22 PM . Last Modified: ‎2024-02-14 11:57 PM

0 Likes
0
1724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:22 PM . Last Modified: ‎2024-02-14 11:57 PM

Hi Mike,

This is a 1st generation model, so the appropriate firmware revision would be somewhat ancient too. I had a look on our own FTP and the latest release I can find is Masterswitch aos rev. 227 rpdu application rev. 220, this has been released in 2004. I am not sure about the forked.net links, I cannot find anything internally that would confirm Masterswitch supports aos rev. 309.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:22 PM . Last Modified: ‎2024-02-14 11:57 PM

0 Likes
0
1724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:22 PM . Last Modified: ‎2024-02-14 11:57 PM

Thanks for the response and info!

Since the PDU didn’t cost me very much I figured I didn’t have much to lose so I went ahead and upgraded per the forked.net instructions and links.  The upgrade went fine and I am now running with those versions.  So those do actually work with the ap9606 but both had to be upgraded to get the web app working again.  FTP worked the entire time.  

Cheers!

Mike

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore