Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
AP9210 Connection trouble
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2711:42 PM. Last Modified: 2024-03-1811:58 PM
AP9210 Connection trouble
Hey guys, ive tried everything to connect to my secondhand apc ap9210. i have tried to change the IP address using ARP in cmd (request timed out when i attempted to ping). ive tried connecting with hyperterminal which does open a connection but doesnt give me login options when i press enter. i have been following lots of different guides online to try and access my device.
I dont know the ip or login details. all i know is the mac address
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2711:42 PM. Last Modified: 2024-03-1811:58 PM
Hi,
When connecting via HyperTerminal what baud rate are you setting?
These are the correct settings 2400 bps, no parity, 8 data bits, 1 stop bit, and no flow control. If you can access it via HyperTerminal and send me the serial number I can create a password that will allow you to access the unit. If you cannot connect via HyperTerminal then the unit cannot be reset.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2711:42 PM. Last Modified: 2024-03-1811:58 PM
Hi,
When connecting via HyperTerminal what baud rate are you setting?
These are the correct settings 2400 bps, no parity, 8 data bits, 1 stop bit, and no flow control. If you can access it via HyperTerminal and send me the serial number I can create a password that will allow you to access the unit. If you cannot connect via HyperTerminal then the unit cannot be reset.