[AP8959EU] Can't access via Serial console

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • [AP8959EU] Can't access via Serial console
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
rabin_apc
Crewman rabin_apc
Crewman

Posted: ‎2021-07-12 04:34 AM . Last Modified: ‎2024-02-14 02:42 AM

0 Likes
6
3081
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 04:34 AM . Last Modified: ‎2024-02-14 02:42 AM

[AP8959EU] Can't access via Serial console

I was tring to access the device via serial console using minicom.

I set my connection setting to "9600 8N1" based on the documetation for password reset but didn't get any prompt.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • com
  • console
  • serial
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
rabin_apc
Crewman rabin_apc
Crewman

Posted: ‎2021-07-12 04:34 AM . Last Modified: ‎2024-02-14 02:38 AM

0 Likes
0
3078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 04:34 AM . Last Modified: ‎2024-02-14 02:38 AM

Found it, it was the hardware flow control, it was under a diffrent config section in the tool i used (minicom).
after disabling it, i was able to get a prompt.

Thank you.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-12 04:34 AM . Last Modified: ‎2024-01-31 02:59 AM

0 Likes
0
3078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 04:34 AM . Last Modified: ‎2024-01-31 02:59 AM

Can you confirm what serial cable you're using? Are you also using any adapters? Is the PDU operating normally and there are LEDs on the display and ethernet jack?

Furthermore, make sure scroll lock is not on.

Reply

Link copied. Please paste this link to share this article on your social media post.

rabin_apc
Crewman rabin_apc
Crewman

Posted: ‎2021-07-12 04:34 AM . Last Modified: ‎2024-02-14 02:42 AM

0 Likes
0
3078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 04:34 AM . Last Modified: ‎2024-02-14 02:42 AM

The cable I use is the one that came with the package,

In the documentation I see it numbered as "940-0144A" and this is what I see embbeded on the connector's head.

I can confirm that the serial port it self is working , becuse i can connect to other devices like Switchs serial console.

but I can't connect to the PDU.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-12 04:34 AM . Last Modified: ‎2024-01-31 02:59 AM

0 Likes
0
3078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 04:34 AM . Last Modified: ‎2024-01-31 02:59 AM

This is a tough one without being right in front of it. Can you comment on the question regarding LEDs on the PDU that I mentioned? 

Reply

Link copied. Please paste this link to share this article on your social media post.

rabin_apc
Crewman rabin_apc
Crewman

Posted: ‎2021-07-12 04:34 AM . Last Modified: ‎2024-02-14 02:42 AM

0 Likes
0
3078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 04:34 AM . Last Modified: ‎2024-02-14 02:42 AM

You can see the LED status in the picture, seems to be OK.

Also the Ethernet is connected.

kb7IJquB1If0LpoKUI%2F9xA%3D%3D.jpegkb7IJquB1If0LpoKUI%2F9xA%3D%3D.jpeg

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-12 04:34 AM . Last Modified: ‎2024-01-31 02:59 AM

0 Likes
0
3078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 04:34 AM . Last Modified: ‎2024-01-31 02:59 AM

Is that a second PDU behind it? Does that one work?

Try holding down that pinhole reset button for 20 seconds. When you are doing that correctly, the status LED on the Ethernet jack (the one that has a checkmark or X next to it) will flash/pulse green. When it's time to let go, it will change to orange and format/wipe flash memory. See if then anything changes regarding your serial access.

Reply

Link copied. Please paste this link to share this article on your social media post.

rabin_apc
Crewman rabin_apc
Crewman

Posted: ‎2021-07-12 04:34 AM . Last Modified: ‎2024-02-14 02:38 AM

0 Likes
0
3079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 04:34 AM . Last Modified: ‎2024-02-14 02:38 AM

Found it, it was the hardware flow control, it was under a diffrent config section in the tool i used (minicom).
after disabling it, i was able to get a prompt.

Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore