AP8959, What is the Default cold start behaviour, where can I configure this ?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP8959, What is the Default cold start behaviour, where can I configure this ?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
simondbingham
simondbingham
Cadet

Posted: ‎2022-08-31 11:12 PM

0 Likes
3
616
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-31 11:12 PM

AP8959, What is the Default cold start behaviour, where can I configure this ?

My understanding is coldstart is the behaviour when power input to the APC rail is taken down and restored

I cannot understand the default behaviour, when I first installed the device all interfaces started. 
Now all interfaces are off when power is restored. 

The behaviour I would like is interfaces 9,10,11 always come on after a cold start 

the rest are off 



OR

 

the APC just recalls the state of the outlets at power down, and restores this state. 

Where is this configured. ? I cannot find

Thanks in advance , Simon

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-09-04 10:11 PM

0 Likes
2
571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-04 10:11 PM

Hi @simondbingham 

 

Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query.  Apologies for the inconvenience, since this is a Switched RackPDU you may want to check the Power On/Off delay configurations of outlets 9, 10, and 11.

 

To do this, kindly log in to the web interface of the device and then go to Configuration > rPDU > Switched Outlet > Configuration.  From there, you can either choose to change it by an outlet or use the multiple outlet configurations.

 

I hope this helps.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

simondbingham
simondbingham
Cadet

Posted: ‎2022-09-21 09:47 AM

In response to JonPro
0 Likes
1
515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-21 09:47 AM

Hi
this is an example of a outlet, when power is restored to the APC rail the outlet stays off,  this outlet does does not come on unit I go to the GUI and turn this on manually, what should the behaviour be on power restoration to the APC . ? 

9-
Power On Delay
Immediate
Power Off Delay
180 sec
Reboot Duration
5 sec
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-09-21 08:53 PM

In response to simondbingham
0 Likes
0
509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-21 08:53 PM

Hi @simondbingham 

 

Will you be able to provide the NMC debug file by following the FAQ below?  Also, another procedure that we can do is to reseat the display module.

 

Video: How can I download Event, Data, Configuration, and Debug files from my Network Management Car... 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of