Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

AP8959 PDU Terminator

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP8959 PDU Terminator
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
ausmrfusion
ausmrfusion
Cadet

Posted: ‎2025-09-12 10:36 AM

0 Likes
2
262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-12 10:36 AM

AP8959 PDU Terminator

Hi there,

 

I need to get a couple of terminators for an AP8959 PDU and followed @BillP's advice in handful of other posts to call local SE support and request 0W05545A or 0J-0W05545A.

 

They told me that they no longer carry spare parts (in Australia at least), and if a terminator failed while the PDU is covered under warranty they would send me an entirely new PDU with a terminator.  Unfortunately the PDU is no longer under warranty, so I am hoping there is an alternate channel to source them from.

 

Are there any recommendations of where I can get them from that isn't incredibly expensive (there are a couple on Ebay that are almost AU$100 shipped)?  If not, are there any published specifications detailing what resistors are required and what pins them need to be terminated to so I can make my own?

 

Thanks.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
MorneMeintjes
Ensign MorneMeintjes
Ensign

Posted: ‎2025-09-15 11:36 PM

0 Likes
1
253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-15 11:36 PM

Good Morning

Hope you are well.

 

The terminator has a 120ohm resistor between pin 1 and 2 of the RJ45 connector. If SE cant support , its best to make one up yourself.

 

Best Regards

 

You may have to measure the pins, and figure out where the resistor is located.

Reply

Link copied. Please paste this link to share this article on your social media post.

ausmrfusion
ausmrfusion
Cadet

Posted: ‎2025-10-25 10:57 PM

In response to MorneMeintjes
0 Likes
0
150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-25 10:57 PM

Hi @MorneMeintjes,

 

Thanks for the information and apologies for the late reply.

 

My AP8959 had a stuck blue display and was showing communication lost errors which I saw some people were able to resolve by adding a terminator.  I made one up myself following your advice re the pinout, but it didn't fix the problem.  I have since swapped the NMC and communication cable with another unit (which also included an original terminator), and while the new display works and I can see the status, I am still getting communication lost errors.

 

I think the PDU itself has failed unfortunately, but I measured the resistance across pins 1 and 2 of the terminator that came with the new NMC and can confirm you are 100% correct, there is 120 ohms across pins 1 and 2 of the RJ45 connector.

 

It is easier to see the wires on the older 0W04161 terminator as they are orange and make it pretty clear.

 

Thanks again!

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore