Posted: 2025-09-12 10:36 AM
Hi there,
I need to get a couple of terminators for an AP8959 PDU and followed @BillP's advice in handful of other posts to call local SE support and request 0W05545A or 0J-0W05545A.
They told me that they no longer carry spare parts (in Australia at least), and if a terminator failed while the PDU is covered under warranty they would send me an entirely new PDU with a terminator. Unfortunately the PDU is no longer under warranty, so I am hoping there is an alternate channel to source them from.
Are there any recommendations of where I can get them from that isn't incredibly expensive (there are a couple on Ebay that are almost AU$100 shipped)? If not, are there any published specifications detailing what resistors are required and what pins them need to be terminated to so I can make my own?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-15 11:36 PM
Good Morning
Hope you are well.
The terminator has a 120ohm resistor between pin 1 and 2 of the RJ45 connector. If SE cant support , its best to make one up yourself.
Best Regards
You may have to measure the pins, and figure out where the resistor is located.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-25 10:57 PM
Hi @MorneMeintjes,
Thanks for the information and apologies for the late reply.
My AP8959 had a stuck blue display and was showing communication lost errors which I saw some people were able to resolve by adding a terminator. I made one up myself following your advice re the pinout, but it didn't fix the problem. I have since swapped the NMC and communication cable with another unit (which also included an original terminator), and while the new display works and I can see the status, I am still getting communication lost errors.
I think the PDU itself has failed unfortunately, but I measured the resistance across pins 1 and 2 of the terminator that came with the new NMC and can confirm you are 100% correct, there is 120 ohms across pins 1 and 2 of the RJ45 connector.
It is easier to see the wires on the older 0W04161 terminator as they are orange and make it pretty clear.
Thanks again!