Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

AP8941 - IPv4 Address Could Not Start

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP8941 - IPv4 Address Could Not Start
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
zack.coffey_apc
Crewman zack.coffey_apc
Crewman

Posted: ‎2021-07-11 10:28 PM . Last Modified: ‎2024-02-14 03:20 AM

0 Likes
6
2921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:28 PM . Last Modified: ‎2024-02-14 03:20 AM

AP8941 - IPv4 Address Could Not Start

We have a PDU that's been in service and working fine for about 3 years, suddenly drop off the network.

On the LCD screen we get the message "IPv4 Address Could Not Start". IPv6 screen is just blank where an IP would be. The MAC address screen is all 0's.

We've power cycled a few times, done the reset button for 30 seconds a few times, and done a firmware update to 6.8.0 via USB. Firmware update shows the correct version numbers on the LCD screen, but the IPv4 still cannot start and MAC address is all zeros. Tried power cycling and resetting after firmware update, same issue.

We have a spare AP8941, it's been reconfigured and we should be replacing it this afternoon.

What's wrong with this PDU? We have hundreds of these AP8941's in services and they've been good, this one just died without warning and nothing we've done has brought it back to life. Probably no longer under warranty either, sadface.exe

I'll have it in my lab later today and can diagnose things on it. What else can I look for?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • address
  • ap8941
  • firmware
  • ipv4
  • mac
  • zeros
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-11 10:28 PM . Last Modified: ‎2024-01-31 03:01 AM

0 Likes
0
2922
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:28 PM . Last Modified: ‎2024-01-31 03:01 AM

Hi Zack,

I'd be surprised if the the capacitor wasn't soldered down correctly, the main reason being that if that was the case you would have seen issues well before this, it wouldn't have worked for 5 years first. 

No replacements can be given via the forums, you'd need to contact your local APC by SE support team but with a 5 year old unit and no extended warranty I don't know if they will be able to replace it.

-Gavan  

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
zack.coffey_apc
Crewman zack.coffey_apc
Crewman

Posted: ‎2021-07-11 10:28 PM . Last Modified: ‎2024-02-14 03:20 AM

0 Likes
0
2924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:28 PM . Last Modified: ‎2024-02-14 03:20 AM

Got serial connection. Here's some info:

apc>tcpip
E000: Success

Active IPv4 Settings
--------------------
  Active IPv4 Address:          0.0.0.0
  Active IPv4 Subnet Mask:      0.0.0.0
  Active IPv4 Gateway:          0.0.0.0

Manually Configured IPv4 Settings
---------------------------------

  IPv4:                 enabled
  Manual Settings:      disabled

  IPv4 Address:         0.0.0.0
  Subnet Mask:          0.0.0.0
  Gateway:              0.0.0.0
  MAC Address:          00 00 00 00 00 00
  Domain Name:          example.com
  Host Name:            apc000000

apc>system
E000: Success
Host Name Sync: Disabled
Name:           apc000000
Contact:        Unknown
Location:       Unknown
Message:
DateTime:       09/20/2015:00:09:15
User:           apc
Up Time:        0 Days 0 Hours 9 Minutes
Stat:           P N4- N6- A
Bootmon:        bootmon:v1.0.9
AOS:            aos:v6.8.2
App:            rpdu2g:v6.8.0

apc>about
E000: Success
Hardware Factory
---------------
Model Number:           AP8941
Serial Number:          5A1539E00281
Hardware Revision:      02
Manufacture Date:       09/20/2015
MAC Address:            00 00 00 00 00 00
Management Uptime:      0 Days 0 Hours 9 Minutes

Network Management Card
---------------
Model Number:
Serial Number:
Hardware Revision:
Manufacture Date:       02/09/2007

Application Module
---------------
Name:                   rpdu2g
Version:                v6.8.0
Date:                   Jul 22 2019
Time:                   16:05:06

APC OS(AOS)
---------------
Name:                   aos
Version:                v6.8.2
Date:                   Jul 22 2019
Time:                   15:32:47

APC Boot Monitor
---------------
Name:                   bootmon
Version:                v1.0.9
Date:                   Mar 27 2019
Time:                   16:23:06

apc>boot
E000: Success

Boot Mode:      dhcp
DHCP Cookie:    disabled
Vendor Class:   APC
Client ID:      00 00 00 00 00 00
User Class:     RPDU2G

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-11 10:28 PM . Last Modified: ‎2024-01-31 03:01 AM

0 Likes
0
2924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:28 PM . Last Modified: ‎2024-01-31 03:01 AM

Hi Zack,

The PDU appears to be 4-5 years old, judging by the serial number, it looks like something might have shorted out the network card, you could try reseating the module but I don't know if it will help in this case:

https://www.youtube.com/watch?v=lGbt6typjRQ

Did you by any chance purchase the extended warranty, if so support should be able to help you with getting the part replaced?

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

zack.coffey_apc
Crewman zack.coffey_apc
Crewman

Posted: ‎2021-07-11 10:28 PM . Last Modified: ‎2024-02-14 03:20 AM

0 Likes
0
2923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:28 PM . Last Modified: ‎2024-02-14 03:20 AM

As far as I know, no we did not get extra warranty.

How much does a replacement Network module typically cost?

Reply

Link copied. Please paste this link to share this article on your social media post.

zack.coffey_apc
Crewman zack.coffey_apc
Crewman

Posted: ‎2021-07-11 10:28 PM . Last Modified: ‎2024-02-14 03:20 AM

0 Likes
0
2924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:28 PM . Last Modified: ‎2024-02-14 03:20 AM

Interesting note, just removed the Network module and a passive electrical component fell out. Looking at where it goes, it doesn't look like it was ever properly soldered on.

F5 VZH 220 25V

Reply

Link copied. Please paste this link to share this article on your social media post.

zack.coffey_apc
Crewman zack.coffey_apc
Crewman

Posted: ‎2021-07-11 10:28 PM . Last Modified: ‎2024-02-14 03:20 AM

0 Likes
0
2923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:28 PM . Last Modified: ‎2024-02-14 03:20 AM

Here's some pics. To my untrained eye, this looks like a manufacturing defect as it does not appear to have ever been properly soldered.

I'd be happy to ship this unit to you if you'd like to FA it, in exchange for a replacement.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-11 10:28 PM . Last Modified: ‎2024-01-31 03:01 AM

0 Likes
0
2923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:28 PM . Last Modified: ‎2024-01-31 03:01 AM

Hi Zack,

I'd be surprised if the the capacitor wasn't soldered down correctly, the main reason being that if that was the case you would have seen issues well before this, it wouldn't have worked for 5 years first. 

No replacements can be given via the forums, you'd need to contact your local APC by SE support team but with a 5 year old unit and no extended warranty I don't know if they will be able to replace it.

-Gavan  

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of