Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

AP8881 management constantly reboots

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: AP8881 management constantly reboots
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
peterskovgaard_apc
Crewman peterskovgaard_apc
Crewman

Posted: ‎2021-07-29 10:56 PM

0 Likes
16
2825
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-29 10:56 PM

AP8881 management constantly reboots

This was originally posted on APC forums on 7/29/2014


We have an AP8881 PDU that constantly restarts its management interface. I have managed to grab a debug zip from the PDU, it is attached. Any clues as to what is happening?

When the management interface is up for a short while, the lastrst command yields "05 Failsafe Reset". The firmware versions are:

Bootmon:        bootmon:v1.0.2

AOS:            aos:v6.1.3

App:            rpdu2g:v6.0.9

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 10:57 PM

0 Likes
0
2823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-29 10:57 PM

This reply was originally posted by Angela on APC forums on 6/24/2015


It is something over my head but something inside of the TCP/IP stack that we modified.

See Answer In Context

Reply
Replies 16
peterskovgaard_apc
Crewman peterskovgaard_apc
Crewman

Posted: ‎2021-07-29 10:56 PM

0 Likes
0
2823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-29 10:56 PM

This was originally posted on APC forums on 8/27/2014


Hi again. Sorry for the wait, I have been on holiday.

The config.ini was posted directly from the device without modifications. I have performed a format of the device, but the result is the same, it continuously restarts. We have more than 50 devices, of which a few have started exhibiting these problems. This may be linked to a firmware upgrade that was performed months ago. All the devices are under control of StruxureWare, if that makes any difference.

I'll upload a configuration dump from a device that is working, maybe you can see some sort of difference.

Thanks!

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 10:57 PM

0 Likes
0
2823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-29 10:57 PM

This reply was originally posted by Angela on APC forums on 8/27/2014


Thanks! We are investigating a few issues of this type. A few possible guesses at this time are NTP or something related to StruxureWare Data Center Expert. Can you tell me, are the devices that are working/not working on the Data Center Expert public network interface or private LAN? What other devices are on the same network as these PDUs (APC devices, non-APC devices, etc)?

I don't know if on one that's not working, you want to see if disabling NTP does anything different. If you do disable it, it was recommended to me to still put 0.0.0.0 in the server field to rule out a possible issue of a valid IP (yet inactive) causing a problem.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 10:57 PM

0 Likes
0
2823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-29 10:57 PM

This reply was originally posted by Angela on APC forums on 8/28/2014


Did you reboot the management card after? And when you disabled NTP, did you put 0.0.0.0 in the field afterwards?

Reply
peterskovgaard_apc
Crewman peterskovgaard_apc
Crewman

Posted: ‎2021-07-29 10:57 PM

0 Likes
0
2823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-29 10:57 PM

This was originally posted on APC forums on 8/28/2014


Disabling NTP didn't make any difference. The management card still reboots regularly with the reason "05 Failsafe Reset".

Reply
peterskovgaard_apc
Crewman peterskovgaard_apc
Crewman

Posted: ‎2021-07-29 10:57 PM

0 Likes
0
2826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-29 10:57 PM

This was originally posted on APC forums on 7/29/2014


We have an AP8881 PDU that constantly restarts its management interface. I have managed to grab a debug zip from the PDU, it is attached. Any clues as to what is happening?

When the management interface is up for a short while, the lastrst command yields "05 Failsafe Reset". The firmware versions are:

Bootmon:        bootmon:v1.0.2

AOS:            aos:v6.1.3

App:            rpdu2g:v6.0.9

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 10:57 PM

0 Likes
0
2826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-29 10:57 PM

This reply was originally posted by Angela on APC forums on 7/29/2014


Let me check into it. Based on the frequency, I think something is corrupted but I would like to ask someone else to review the logs and then report back to you.

Reply
peterskovgaard_apc
Crewman peterskovgaard_apc
Crewman

Posted: ‎2021-07-29 10:57 PM

0 Likes
0
2826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-29 10:57 PM

This was originally posted on APC forums on 8/3/2014


Hi Angela,

Thanks, that would be very helpful. I suspect that it may be the management processor itself that is faulty somehow.

Peter

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 10:57 PM

0 Likes
0
2826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-29 10:57 PM

This reply was originally posted by Angela on APC forums on 8/3/2014


99.9% of the time it is a firmware thing - like a particular setting combination, memory issue, etc. Sort of like mini Windows BSOD in a certain sense (assuming it is not am expected reboot).

Let net me check in on this to see where we are at with the logs. Usually if there is nothing very obvious, we suggest "formatting" the PDU (the Network Card inside it technically) and seeing if it continues to do it with the same configuration in case something became corrupted. If it still does it, then we format and reconfigure slowly to see if a particular setting triggers it and then we go from there. Before I had you do that though, I just wanted to have someone look at the logs to make sure I did not miss anything since I have seen this on a few other PDUs recently and it peaked my interest.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 10:57 PM

0 Likes
0
2826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-29 10:57 PM

This reply was originally posted by Angela on APC forums on 8/4/2014


Hello again. So from what we can tell, one of the "tasks" in the operating system is not checking in properly. I need to try and replicate that. I am going to load your config.ini from your PDU onto my simulator and see if I can re-produce it. Did you remove any settings from config.ini before posting that file? From what I can see, you have an almost factory default setting and are using DHCP - is that fair to say?

In the meantime, I'd suggest that the quickest thing will be to do what I suggested and see if any improvement on your end - "format" the device and see if it reacts differently at all and stops rebooting or if it starts doing the same thing. This will wipe every setting/item on the PDU beyond the firmware so it'd have to have its TCP/IP settings set up again but it looks like you just use DHCP anyway. You could issue the format command via CLI and follow the instructions it gives you after entering it to begin the process.

Let me know if you have any questions before you get started and if you can confirm what I said on config.ini so I can try to see if my simulator will do the same thing.

Thanks!

P.S. - do you have any PDUs in the same network location with similar or different network configurations that are behaving properly? And did you recently do anything, like upgrade the firmware or anything that rings a bell?

Reply
robertsa_apc
Crewman robertsa_apc
Crewman

Posted: ‎2021-07-29 10:57 PM

0 Likes
0
2826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-29 10:57 PM

This was originally posted on APC forums on 6/23/2015


Was a cause or solution ever figured out for this? I have the the same problem with my PDUs even after upgrading from 6.1.3 to 6.3.2. 

  • Tags:
  • firmware
  • management
  • pdu
Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 10:57 PM

0 Likes
0
2826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-29 10:57 PM

This reply was originally posted by Angela on APC forums on 6/23/2015


The versions you're mentioning are the AOS or APC Operating System version. We did identify a problem with a PDU application version outlined here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA237061 

Did you have rpdu2g v6.0.9 or v6.1.0? I am not aware of any other "known" issues beyond a memory leak with SSH enabled or the above issue.

Reply
robertsa_apc
Crewman robertsa_apc
Crewman

Posted: ‎2021-07-29 10:57 PM

0 Likes
0
2826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-29 10:57 PM

This was originally posted on APC forums on 6/23/2015


I had 6.0.9 I went through part of the process. I was hoping I wouldn't have to power cycle the PDU. I will do a power cycle and see how it goes.

I also have another problem that the firmware update didn't fix. I am not able to connect to the PDUs web interface through from a different network. I can ssh, telnet, and ftp to the PDU from a different network but not connect to the web interface. I have two different networks 10.150.150.x and 10.149.149.x they are able to communicate just fine.

I had a PDU that was still running firmware 5.1.9 on 10.149.149.x, and could connect to it from 10.150.150.x. As soon as I upgraded to 6.1.3 it wouldn't connect to the web interface anymore from 10.150.150.x. I would have to be on 10.149.149.x to connect to the web interface. I replicated this test again except going from 5.1.9 to 6.3.2 and came out with the same results. I have already tried reseting to factory defaults, and clearing all the logs. 

Also with ftp I am not able to GET or PUT things from a different network I have to be on the local network. 

  • Tags:
  • apc
  • firmware
  • management
  • network
  • network-management-card
  • pdu
  • power
  • reset
Reply
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-29 10:57 PM

0 Likes
0
2825
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-29 10:57 PM

This was originally posted on APC forums on 6/24/2015


This sounds like the MTU issue described in Knowledge Base article FA235265. I'd post a link to it, but the APC web site is rather unhelpful in providing direct links to articles. You can view it in PDF form here, hopefully.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 10:57 PM

0 Likes
0
2826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-29 10:57 PM

This reply was originally posted by Angela on APC forums on 6/24/2015


I agree with you Terry on it being this MTU issue. Here is the link format I have to use and just replace the kbase ID at the end: http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA235265 

We are in the process of testing a fix for that. So far, one person has said it has fixed the issue for them on a UPS Network Mgmt Card and I am waiting on a second confirmwation. No promises, but I might be able to get you a beta for Rack PDU to try if you're willing to (though the disclaimer is it wouldn't be an official release that has gone through full testing, etc). It would be a very low risk beta though and just one tweak.

Reply
robertsa_apc
Crewman robertsa_apc
Crewman

Posted: ‎2021-07-29 10:57 PM

0 Likes
0
2826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-29 10:57 PM

This was originally posted on APC forums on 6/24/2015


I ended up not power cycling the PDU. Instead, I cleared all the log and data files off of the PDU and that along with the upgrade to 6.3.2 fixed the restarting issue. Setting the MTU to 1382 allowed me to access the web interface, but ftp download still doesn't work. That would be great if you could get me the beta to try. What is the one tweak?

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 10:57 PM

0 Likes
0
2824
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-29 10:57 PM

This reply was originally posted by Angela on APC forums on 6/24/2015


It is something over my head but something inside of the TCP/IP stack that we modified.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc