AP8841 PDU, IP Assignment in malfunction

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP8841 PDU, IP Assignment in malfunction
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-19 12:00 AM

0 Likes
3
3003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-19 12:00 AM

AP8841 PDU, IP Assignment in malfunction

I have APC PDU AP8841 with AOS 6.1.3 and APP 6.0.X. I am attempting to assign it an IP address through console connectivity.

The connection through console successfully turns up but the commands given in Manual gives error 102.

tcpip -i X.X.X.X    (error)

tcpip -s X.X.X.X    (error)

tcpip -g X.X.X.X    (error)

tcpip -S enable     (success)

tcpip -i X.X.X.X -s X.X.X.X  -g X.X.X.X    (error)

tcpip -S enable -i X.X.X.X -s X.X.X.X  -g X.X.X.X    (success).   But this command neither before reboot and nor after reboot change the IP address and remains 0.0.0.0

Also  the IPv4 address stays on DHCP Acquiring on LCD and none command to override DHCP IP selection works.

boot -b manual    (error)

Currently, I turned the PDU to Factory default reset with "rstdflt" and reboot it. since then the PDU LCD is responding very very slow and console connections are failing as well. 

Any suggestions?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-19 12:00 AM

0 Likes
0
3003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-19 12:00 AM

Hi,

You're welcome.FYI, I'd recommend upgrading if you're on rpdu2g APP v6.0.9. We had a bad bug on that version which was fixed in newer versions. Here is the knowledge base on the issue and has links and instructions to upgrade your PDU(s) -> http://www.schneider-electric.us/en/faqs/FA237061  

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-19 12:00 AM

0 Likes
0
3003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-19 12:00 AM

Hi,

If you can log into the serial console, can you share the output of the "about" command? 

Also, was this PDU ever working or configured? If it was installed previously, how long was it in operation for? Or is it a new install? It'd be helpful to understand if there have been other problems or if you're just setting it up for the first time.

If you are able to after answering the above questions, you may try the "format" command which is a step beyond reset to defaults command. You need to type YES to confirm, then type "reboot" and YES to confirm that. This option wipes ALL settings and I like it a little more than reset to defaults to ensure all possible configuration items or corruption is removed from the system.

I also can't tell if it is a problem with how I am viewing what you typed (using Chrome on our site sometimes removes spaces for an odd reason) or if you typed it the way I see it but the spacing on your commands should be:

tcpip-iX.X.X.X-sX.X.X.X-gX.X.X.X

If it was not typed like I just mentioned, you can get an error. If you enter them all on separate lines, the spacing is the same except it is tcpip-iX.X.X.X and repeat for -s and -g options.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-19 12:00 AM

0 Likes
0
3003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-19 12:00 AM

On 5/23/2016 7:11 AM, Angela said:

Hi,

If you can log into the serial console, can you share the output of the "about" command? 

Also, was this PDU ever working or configured? If it was installed previously, how long was it in operation for? Or is it a new install? It'd be helpful to understand if there have been other problems or if you're just setting it up for the first time.

If you are able to after answering the above questions, you may try the "format" command which is a step beyond reset to defaults command. You need to type YES to confirm, then type "reboot" and YES to confirm that. This option wipes ALL settings and I like it a little more than reset to defaults to ensure all possible configuration items or corruption is removed from the system.

I also can't tell if it is a problem with how I am viewing what you typed (using Chrome on our site sometimes removes spaces for an odd reason) or if you typed it the way I see it but the spacing on your commands should be:

tcpip-iX.X.X.X-sX.X.X.X-gX.X.X.X

If it was not typed like I just mentioned, you can get an error. If you enter them all on separate lines, the spacing is the same except it is tcpip-iX.X.X.X and repeat for -s and -g options.

I followed the procedure of formatting you stated and after that, it worked smoothly.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-19 12:00 AM

0 Likes
0
3004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-19 12:00 AM

Hi,

You're welcome.FYI, I'd recommend upgrading if you're on rpdu2g APP v6.0.9. We had a bad bug on that version which was fixed in newer versions. Here is the knowledge base on the issue and has links and instructions to upgrade your PDU(s) -> http://www.schneider-electric.us/en/faqs/FA237061  

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore