Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

AP7724 and Phase Sync:Out of sync

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP7724 and Phase Sync:Out of sync
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
hachete_apc
Crewman hachete_apc
Crewman

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-19 12:00 AM

0 Likes
3
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-19 12:00 AM

AP7724 and Phase Sync:Out of sync

Hello everyone,

We have two different AP7724 ATSs which show the "Phase Sync: Out of sync" message.

This is the setup:

ATS feed 1: Smart-UPS RT 8000 RM XL  with this data:

Date  Time  Vmin  Vmax  Vout  Iout  %Wout  Freq  %Cap  Vbat  TupsC  %VAout  TIambC  %HumI 

  Smart-UPS RT 8000 RM XL Integrated EMU
Date  Time  Vmin  Vmax  Vout  Iout  %Wout  Freq  %Cap  Vbat  TupsC  %VAout  TIambC  %HumI 
 23.05.2016   11:53:12   221.7   224.6   231.6   10.17   32.0   50.01   100.0   216.0   32.4   29.0         
 23.05.2016   11:43:12   221.7   224.6   231.6   10.28   32.0   49.98   100.0   216.0   31.9   29.0         
 23.05.2016   11:33:12   221.7   226.0   231.6   10.07   33.0   50.00   100.0   214.9   32.4   29.0         
 23.05.2016   11:23:12   223.2   224.6   231.6   10.07   32.0   50.00   100.0   216.0   31.9   29.0         
 23.05.2016   11:13:12   221.7   226.0   231.6   10.07   33.0   49.99   100.0   216.0   32.4   29.0         
 23.05.2016   11:03:12   221.7   226.0   231.6   10.17   32.0   49.97   100.0   216.0   32.4   29.0         
 23.05.2016   10:53:12   223.2   226.0   231.6   10.17   32.0   50.00   100.0   216.0   32.4   29.0         
 23.05.2016   10:43:12   223.2   226.0   231.6   10.28   32.0   50.00   100.0   216.0   32.4   29.0         
 23.05.2016   10:33:12   223.2   226.0   231.6   10.07   32.0   50.01   100.0   216.0 

ATS feed 2: Smart-UPS RT 10000 RM XL  with this data: 

Date  Time  Vmin  Vmax  Vout  Iout  %Wout  Freq  %Cap  Vbat  TupsC  %VAout  TIambC  %HumI 
  Smart-UPS RT 10000 RM XL Integrated EMU
Date  Time  Vmin  Vmax  Vout  Iout  %Wout  Freq  %Cap  Vbat  TupsC  %VAout  TIambC  %HumI 
 23.05.2016   11:01:11   226.0   228.9   230.4   0.00   0.0   49.98   100.0   213.8   33.0   0.0         
 23.05.2016   10:51:11   227.5   228.9   230.4   0.00   0.0   50.00   100.0   216.0   33.0   0.0         
 23.05.2016   10:41:11   226.0   228.9   230.4   0.00   0.0   49.98   100.0   216.0   33.0   0.0         
 23.05.2016   10:31:11   227.5   228.9   230.4   0.00   0.0   49.99   100.0   216.0   33.0   0.0         
 23.05.2016   10:21:11   227.5   228.9   230.4   0.00   0.0   49.99   100.0   216.0   33.0   0.0 

 I've spent all morning reading about this and I can`t seem to find the problem because both feeds seem to me to be in sync.

Anyone around to give a hand?

Thanks

Daniel

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • ap7724
  • of
  • out
  • sync
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-18 11:59 PM

0 Likes
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-18 11:59 PM

I think that FAQ was written in response to a discussion I had with APC...

It can still be an issue in 3.9.2, so we now insist on our datacenter A and B power being on the same phase (but from different sources) to avoid it.

There isn't really an ideal solution for this other than the above. Theoretically, you'd want to switch over as fast as you can. But the units use mechanical relays, so there is unavoidably some time delay during the cutover. As an example, if the ATS waited 1 second between opening (disconnecting) one source relay and closing (connecting) the other, the problem would never happen. But your equipment will get power cycled because most things can't tolerate a 1 second interval without power. So the delay gets shortened to something most equipment will tolerate. The other configuration options work to prevent reverting back to the original source (preferred source none), not switching for minor disturbances (sensitivity low), etc.

BTW, the reason the release notes warn you to disconnect one source when upgrading firmware is that there are 2 pieces of firmware - one for the (slow but complicated) management card, and one for the (fast but simple) ATS microcontroller. If there is a new version of microcontroller firmware, when it is written to the micrcontroller it will reset when done (like a reboot after Windows Update). While the microcontroller is rebooting it has no control over the source relays and they can be in an indeterminate state. If they happen to end up with source A and B on different phases, that is the same as trying to do a short circuit between the phases. That causes the breaker(s) to trip and damages the ATS relays.

It might be better for the hardware to use DPDT relays, with one side being source A and the other being B, with the common being the load. I'm not sure why the units don't do that - perhaps it does not meet isolation requirements.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-18 11:59 PM

0 Likes
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-18 11:59 PM

Hi Daniel,

The Rack ATS products, such as AP7724, report phase out of sync when your input power sources are as little as around 10-11º out of phase. The ATS can switch sources that are as much as 180º out of phase (with firmware v3.5.7 or higher).

I would say it is extremely rare to have two input sources that are exactly 0º out of phase and thus many users see this message. You'll notice that this a status item on the ATS but not an alarm. The information you showed from the UPS data log really cannot show anything related to this message. You just need to make sure your UPSs are fed from different sources themselves and not use two UPS's that are on the same input source to avoid any problems with the ATS operation. This phase sync item won't be able to detect or report that to you though - I just meant it as a side note.

Beyond that, there is no problem here if your UPSs are fed from different input power feeds themselves as you won't be able to sync two power sources to exactly 0º majority of the time.

I hope that helps. Let me know if I was not clear.

Reply

Link copied. Please paste this link to share this article on your social media post.

hachete_apc
Crewman hachete_apc
Crewman

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-18 11:59 PM

0 Likes
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-18 11:59 PM

Hi Angela,

We indeed feed from two different sources, but we're now running into this problem when swithching sources although we're following all the recommendations : http://www.apc.com/us/en/faqs/FA156201/

  1. Dropping the load when the ATS switches sources while both appear to have power

The tripping of the circuit breakers during the switching process has been determined to be the result of switching between two sources that are out of phase with each other producing a voltage potential that exceeds the rating of the internal relays responsible for switching from one power source to the other. ATS firmware v3.5.7 and higher aims to resolve this issue and will help prevent the ATS from tripping the upstream circuit breakers
Any idea of what the solution could be to this problem?
Thank you,
Daniel
Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-18 11:59 PM

0 Likes
0
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:41 PM . Last Modified: ‎2024-03-18 11:59 PM

I think that FAQ was written in response to a discussion I had with APC...

It can still be an issue in 3.9.2, so we now insist on our datacenter A and B power being on the same phase (but from different sources) to avoid it.

There isn't really an ideal solution for this other than the above. Theoretically, you'd want to switch over as fast as you can. But the units use mechanical relays, so there is unavoidably some time delay during the cutover. As an example, if the ATS waited 1 second between opening (disconnecting) one source relay and closing (connecting) the other, the problem would never happen. But your equipment will get power cycled because most things can't tolerate a 1 second interval without power. So the delay gets shortened to something most equipment will tolerate. The other configuration options work to prevent reverting back to the original source (preferred source none), not switching for minor disturbances (sensitivity low), etc.

BTW, the reason the release notes warn you to disconnect one source when upgrading firmware is that there are 2 pieces of firmware - one for the (slow but complicated) management card, and one for the (fast but simple) ATS microcontroller. If there is a new version of microcontroller firmware, when it is written to the micrcontroller it will reset when done (like a reboot after Windows Update). While the microcontroller is rebooting it has no control over the source relays and they can be in an indeterminate state. If they happen to end up with source A and B on different phases, that is the same as trying to do a short circuit between the phases. That causes the breaker(s) to trip and damages the ATS relays.

It might be better for the hardware to use DPDT relays, with one side being source A and the other being B, with the common being the load. I'm not sure why the units don't do that - perhaps it does not meet isolation requirements.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of