AP8681 Switching Rack PDU Metered Communication has been lost | No Data
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Due to the turn of the year (2021/2022) we tried to get our metered data from the units. Unfortunately the is no metered data like kWh/Amps/Temperature.
We checked the log and all 8 devices lost the communication:
RPDU Rack PDU 1: Component communications lost with Bank Meter 3. 0x3404 RPDU Rack PDU 1: Component communications lost with Bank Meter 2. 0x3404 RPDU Rack PDU 1: Component communications lost with Bank Meter 1. 0x3404
RPDU Rack PDU 1: Communications lost. 0x3402 RPDU Rack PDU 1: Component communications lost with Phase Meter. 0x3404
At time of writing we tried this:
1) Verify that a terminator is inserted in either the In or Out (It is in Out)
2) Upgraded Firmware to 6.8.0 and after some research to 6.9.6
3) Downgraded Firmware to 6.5.6
4) Factory reset of the hole unit
5) Power-Cycled the whole unit
No luck here - the units do their job delivering power but the internal metering is down.
Strange that all 8 units are affected - would be really bad hardware then!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-1812:58 PM
Hi, I have the same problem. Also 8 rack pdu.s in our datacenter with the same error message. Nothing solves it. The errors happend in 4 weeks time. One after the other. Very strange.