AP7952 Defaults on delayed cold start

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP7952 Defaults on delayed cold start
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
kudrow_apc
Crewman kudrow_apc
Crewman

Posted: ‎2021-07-12 04:38 AM . Last Modified: ‎2024-02-14 02:38 AM

0 Likes
5
1309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 04:38 AM . Last Modified: ‎2024-02-14 02:38 AM

AP7952 Defaults on delayed cold start

I have a AP7952 running 3.9.0 which seems to default on a delayed cold start. If I disconnect the power for a few seconds and reconnect it is fine, however if I disconnect for say 15 minutes and reconnect, all settings are default and I need to console in to reconfigure the entire device.

Upon reconnecting power after 15 minutes, only outlets 9-16 are on and the status LED on the Ethernet port is flashing orange indiciating it is waiting for DHCP/BOOTP. Once I've configured a manual IP and I'm able to access the device, it is empty/default with no settings whatsoever.

A warm start is not affected.

The hardware revision is B2. Application module 3.7.4. AOS 3.9.0.

Any ideas?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-12 04:38 AM . Last Modified: ‎2024-01-31 02:58 AM

0 Likes
0
1309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 04:38 AM . Last Modified: ‎2024-01-31 02:58 AM

Hello Brady,

Thanks, I got the files. I do not see the problem in the logs I expected to see and the PDU appears to be communicating properly - or at least not generating alarms. I also don't see that the alarms are disabled and the config.ini shows PDU specific configuration which tells me, along with valid load/amp data in the PDU that it is communicating when you pulled these files  

Is that load reading in the data log accurate for all of the outlets or only half of them? 

When did you notice this problem develop? After a power outage, etc?

Did you clear the event log on the 10th or was that after one of the incidents that it erased itself?

If I had to guess though it seems like it would have to be some type of hardware issue. Config is store in non volitile memory so it should not be lost when the PDU is powered off for any period of time. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-12 04:38 AM . Last Modified: ‎2024-01-31 02:58 AM

0 Likes
0
1309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 04:38 AM . Last Modified: ‎2024-01-31 02:58 AM

This sounds like an internal communication/hardware issue if I had to guess based on what you said. I can verify this if you provide the first six characters of the PDU serial number and also if you can retrieve the event.txt, data.txt, and config.ini log files when the device is configured with TCP/IP settings. (Instructions for log file download are here: 

Reply

Link copied. Please paste this link to share this article on your social media post.

kudrow_apc
Crewman kudrow_apc
Crewman

Posted: ‎2021-07-12 04:38 AM . Last Modified: ‎2024-02-14 02:38 AM

0 Likes
0
1309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 04:38 AM . Last Modified: ‎2024-02-14 02:38 AM

Thanks for that Angela. Sorry for the delay. I have the 3 files you requested. How can I gtet these to you? I would rather not upload the .ini file.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-12 04:38 AM . Last Modified: ‎2024-01-31 02:58 AM

0 Likes
0
1309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 04:38 AM . Last Modified: ‎2024-01-31 02:58 AM

Hi Brady,

You can email them directly to a private Box folder I have set up @ upload.APC_For.obfq3m3rb5@u.box.com .

Reply

Link copied. Please paste this link to share this article on your social media post.

kudrow_apc
Crewman kudrow_apc
Crewman

Posted: ‎2021-07-12 04:38 AM . Last Modified: ‎2024-02-14 02:38 AM

0 Likes
0
1309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 04:38 AM . Last Modified: ‎2024-02-14 02:38 AM

I have sent this now.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-12 04:38 AM . Last Modified: ‎2024-01-31 02:58 AM

0 Likes
0
1310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 04:38 AM . Last Modified: ‎2024-01-31 02:58 AM

Hello Brady,

Thanks, I got the files. I do not see the problem in the logs I expected to see and the PDU appears to be communicating properly - or at least not generating alarms. I also don't see that the alarms are disabled and the config.ini shows PDU specific configuration which tells me, along with valid load/amp data in the PDU that it is communicating when you pulled these files  

Is that load reading in the data log accurate for all of the outlets or only half of them? 

When did you notice this problem develop? After a power outage, etc?

Did you clear the event log on the 10th or was that after one of the incidents that it erased itself?

If I had to guess though it seems like it would have to be some type of hardware issue. Config is store in non volitile memory so it should not be lost when the PDU is powered off for any period of time. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of