AP7941 latest firmware breaks Bank 2 power

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP7941 latest firmware breaks Bank 2 power
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
nerdsite_apc
Crewman nerdsite_apc
Crewman

Posted: ‎2021-07-11 10:29 PM . Last Modified: ‎2024-02-14 03:19 AM

0 Likes
2
2215
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:29 PM . Last Modified: ‎2024-02-14 03:19 AM

AP7941 latest firmware breaks Bank 2 power

I have some AP7941s that were upgraded to the latest firmware. It *mostly* works except for bank 2 power output readings are blank. On the PDU LED output it's zero when it switches to bank2. The web interface reads zero, as well as SNMP readings:

[SNMPv2-SMI::enterprises.318.1.1.12.2.3.1.1.2.1] => Gauge32: 62
[SNMPv2-SMI::enterprises.318.1.1.12.2.3.1.1.2.2] => Gauge32: 58
[SNMPv2-SMI::enterprises.318.1.1.12.2.3.1.1.2.3] => Gauge32: 0

There are 3 of the latest versions that I can find and neither work (e.g. v3.9.2). The original firmware is this (I have this running on a working one):

--wx-wx-wx 1 apc apc 1310720 Oct 12 2005 apc_hw02_aos_270.bin
drwxrwxrwx 1 apc apc 0 Oct 12 2005 sec/
--wx-wx-wx 1 apc apc 2555904 Nov 07 2005 apc_hw02_rpdu_273.bin
-r--r--r-- 1 apc apc 41687 Jan 05 2021 event.txt
-r--r--r-- 1 apc apc 69 Jan 05 2021 data.txt
-rw-rw-rw- 1 apc apc 23159 Jan 05 2021 config.ini

Does anyone have any older firmware to which I can downgrade these? Possibly AOS: 2.7.0/RPDU 2.7.3? I did a pretty exhaustive search and cannot find any older/archived firmware. Does this exists?

Is there anyway to download the existing firmware files? The are marked as wx, not read, so I believe this is the reason for which you cannot download the files (ftp, xmodem, etc). Don't know if there's a maintenance mode or something that allows one to download these.

BTW, when one was upgraded the power logs continued to run but the bank2 logs were zero. Prior to the upgrade they had values so it's not a hardware failure.

Is there any other fix to this other than replacing them?

Thanks.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • ap7941
  • bank2
  • downgrade
  • firmware
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
nerdsite_apc
Crewman nerdsite_apc
Crewman

Posted: ‎2021-07-11 10:29 PM . Last Modified: ‎2024-02-14 03:19 AM

0 Likes
0
2215
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:29 PM . Last Modified: ‎2024-02-14 03:19 AM

Thanks. No such luck though. The actual power values are not even written internally so not in the SNMP anywhere either. Even the web interface/telnet doesn't show. Look like my only route is to fine someone with some older archived firmware. It sucks that I cannot download it. It's right there but I cannot access it!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-11 10:29 PM . Last Modified: ‎2024-01-31 03:00 AM

0 Likes
0
2215
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:29 PM . Last Modified: ‎2024-01-31 03:00 AM

I ran into something that might be relevant when trying to connect some supposed Gen 1 PDU's to Data Centre Expert.

Usually Gen 1 PDU's use the 'rPDU' branch of the APC PowerNET MIB (.1.3.6.1.4.1.318.1.1.12) but I have come across some - all on later firmware - that use the rPDU2 branch (.1.3.6.1.4.1.318.1.1.26)

Try using .1.3.6.1.4.1.318.1.1.26.8.3.1.5.1 for Bank 1, .1.3.6.1.4.1.318.1.1.26.8.3.1.5.2 for Bank 2 etc.

If this works then it is probably worth considering moving to the rPDU2 branch if you are measuring individual outlet measurements too.

 

To confirm - you cannot download the existing firmware from the PDU.

 

I don't have a copy of early Firmware so can't help you there.  Good luck finding it if you go that route

 

Regards

 

Reply

Link copied. Please paste this link to share this article on your social media post.

nerdsite_apc
Crewman nerdsite_apc
Crewman

Posted: ‎2021-07-11 10:29 PM . Last Modified: ‎2024-02-14 03:19 AM

0 Likes
0
2216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:29 PM . Last Modified: ‎2024-02-14 03:19 AM

Thanks. No such luck though. The actual power values are not even written internally so not in the SNMP anywhere either. Even the web interface/telnet doesn't show. Look like my only route is to fine someone with some older archived firmware. It sucks that I cannot download it. It's right there but I cannot access it!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore