Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

AP7941 latest firmware breaks Bank 2 power

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP7941 latest firmware breaks Bank 2 power
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
nerdsite_apc
Crewman nerdsite_apc
Crewman

Posted: ‎2021-07-11 10:29 PM

0 Likes
2
465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-11 10:29 PM

AP7941 latest firmware breaks Bank 2 power

This was originally posted on APC forums on 1/6/2021


I have some AP7941s that were upgraded to the latest firmware. It *mostly* works except for bank 2 power output readings are blank. On the PDU LED output it's zero when it switches to bank2. The web interface reads zero, as well as SNMP readings:

[SNMPv2-SMI::enterprises.318.1.1.12.2.3.1.1.2.1] => Gauge32: 62
[SNMPv2-SMI::enterprises.318.1.1.12.2.3.1.1.2.2] => Gauge32: 58
[SNMPv2-SMI::enterprises.318.1.1.12.2.3.1.1.2.3] => Gauge32: 0

There are 3 of the latest versions that I can find and neither work (e.g. v3.9.2). The original firmware is this (I have this running on a working one):

--wx-wx-wx 1 apc apc 1310720 Oct 12 2005 apc_hw02_aos_270.bin
drwxrwxrwx 1 apc apc 0 Oct 12 2005 sec/
--wx-wx-wx 1 apc apc 2555904 Nov 07 2005 apc_hw02_rpdu_273.bin
-r--r--r-- 1 apc apc 41687 Jan 05 2021 event.txt
-r--r--r-- 1 apc apc 69 Jan 05 2021 data.txt
-rw-rw-rw- 1 apc apc 23159 Jan 05 2021 config.ini

Does anyone have any older firmware to which I can downgrade these? Possibly AOS: 2.7.0/RPDU 2.7.3? I did a pretty exhaustive search and cannot find any older/archived firmware. Does this exists?

Is there anyway to download the existing firmware files? The are marked as wx, not read, so I believe this is the reason for which you cannot download the files (ftp, xmodem, etc). Don't know if there's a maintenance mode or something that allows one to download these.

BTW, when one was upgraded the power logs continued to run but the bank2 logs were zero. Prior to the upgrade they had values so it's not a hardware failure.

Is there any other fix to this other than replacing them?

Thanks.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • ap7941
  • bank2
  • downgrade
  • firmware
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
nerdsite_apc
Crewman nerdsite_apc
Crewman

Posted: ‎2021-07-11 10:29 PM

0 Likes
0
465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-11 10:29 PM

This was originally posted on APC forums on 1/8/2021


Thanks. No such luck though. The actual power values are not even written internally so not in the SNMP anywhere either. Even the web interface/telnet doesn't show. Look like my only route is to fine someone with some older archived firmware. It sucks that I cannot download it. It's right there but I cannot access it!

See Answer In Context

Reply
Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-11 10:29 PM

0 Likes
0
465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-11 10:29 PM

This reply was originally posted by Garry on APC forums on 1/7/2021


I ran into something that might be relevant when trying to connect some supposed Gen 1 PDU's to Data Centre Expert.

Usually Gen 1 PDU's use the 'rPDU' branch of the APC PowerNET MIB (.1.3.6.1.4.1.318.1.1.12) but I have come across some - all on later firmware - that use the rPDU2 branch (.1.3.6.1.4.1.318.1.1.26)

Try using .1.3.6.1.4.1.318.1.1.26.8.3.1.5.1 for Bank 1, .1.3.6.1.4.1.318.1.1.26.8.3.1.5.2 for Bank 2 etc.

If this works then it is probably worth considering moving to the rPDU2 branch if you are measuring individual outlet measurements too.

 

To confirm - you cannot download the existing firmware from the PDU.

 

I don't have a copy of early Firmware so can't help you there.  Good luck finding it if you go that route

 

Regards

 

Reply
nerdsite_apc
Crewman nerdsite_apc
Crewman

Posted: ‎2021-07-11 10:29 PM

0 Likes
0
466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-11 10:29 PM

This was originally posted on APC forums on 1/8/2021


Thanks. No such luck though. The actual power values are not even written internally so not in the SNMP anywhere either. Even the web interface/telnet doesn't show. Look like my only route is to fine someone with some older archived firmware. It sucks that I cannot download it. It's right there but I cannot access it!

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc