Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

AP7930 Error

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP7930 Error
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:28 AM . Last Modified: ‎2024-03-18 03:31 AM

0 Likes
5
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:28 AM . Last Modified: ‎2024-03-18 03:31 AM

AP7930 Error

Hello,

I upgraded from version 2.7.2 to 3.7.3 at the behest of APC tech support to solve a connection lost and established issue(roughly the issue was just that multiple emails claiming the connection was lost and established). After the firmware upgrade we began receiving "Switched Rack PDU: Overload" messages. I was instructed to try previous firmwares until the issue was resolved. A reboot of the hardware was also requested however we are unable to carry out such an action where business critical appliances are connected.

After loading 2.7.1 connection to the web console was not possible. Firmware 3.7.3 was reloaded in which the system continued the overload messages then promptly went into a cold start. I haven't attempted to log into the web interface again in fear of another cold start. Any information provided will be greatly appreciated!

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:29 AM . Last Modified: ‎2024-03-18 03:20 AM

0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:29 AM . Last Modified: ‎2024-03-18 03:20 AM

I will try that out thank you! There was an Er message on the lcd yesterday. The power cycle like you said is not a feasible option however when the system cold started yesterday it was down for several minutes, would it be safe to rule out that fix possibly?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:28 AM . Last Modified: ‎2024-03-18 03:31 AM

0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:28 AM . Last Modified: ‎2024-03-18 03:31 AM

Hello,

I upgraded from version 2.7.2 to 3.7.3 at the behest of APC tech support to solve a connection lost and established issue(roughly the issue was just that multiple emails claiming the connection was lost and established). After the firmware upgrade we began receiving "Switched Rack PDU: Overload" messages. I was instructed to try previous firmwares until the issue was resolved. A reboot of the hardware was also requested however we are unable to carry out such an action where business critical appliances are connected.

After loading 2.7.1 connection to the web console was not possible. Firmware 3.7.3 was reloaded in which the system continued the overload messages then promptly went into a cold start. I haven't attempted to log into the web interface again in fear of another cold start. Any information provided will be greatly appreciated!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:28 AM . Last Modified: ‎2024-03-18 03:31 AM

0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:28 AM . Last Modified: ‎2024-03-18 03:31 AM

ok here is what I would do to start and see if we get anywhere..

back up your config.ini using those instructions i gave you first. that will back up all of your settings. do a reset to defaults, excluding TCP/IP (so you don't lose your IP) under Administration->General->Reset/Reboot and see what you get.

then you can reapply your config.ini with your settings depending on how we do.

do you see an Er on the LCD display on the front of the PDU too? a power cycle for 5-10 seconds is recommended too in this circumstance but i understand that is not a feasible option.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:28 AM . Last Modified: ‎2024-03-18 03:20 AM

0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:28 AM . Last Modified: ‎2024-03-18 03:20 AM

Thank you for the quick response! I will attach the event.txt to this post. The PDU serial is JA0415.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:28 AM . Last Modified: ‎2024-03-18 03:20 AM

0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:28 AM . Last Modified: ‎2024-03-18 03:20 AM

hi,

can you provide me the event.txt log file from the PDU so we can see what happened? here are some instructions on how to download it if you aren't sure - http://nam-en.apc.com/app/answers/detail/a_id/9321/

also, what is the serial number on the PDU? the first few digits will be fine - such as ZA0910. you can get this via the web interface or on the PDU itself.

thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:29 AM . Last Modified: ‎2024-03-18 03:20 AM

0 Likes
0
883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:29 AM . Last Modified: ‎2024-03-18 03:20 AM

I will try that out thank you! There was an Er message on the lcd yesterday. The power cycle like you said is not a feasible option however when the system cold started yesterday it was down for several minutes, would it be safe to rule out that fix possibly?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of