AP7922: Error: The application was not able to load.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP7922: Error: The application was not able to load.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:15 AM . Last Modified: ‎2024-03-18 11:33 PM

0 Likes
6
6093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:15 AM . Last Modified: ‎2024-03-18 11:33 PM

AP7922: Error: The application was not able to load.

I am getting 'Error: The application was not able to load' when I tried to access it after updating the firmware with apc_hw02_aos392 package using SCP method.The SCP method seemed to be successful. apc_hw02_aos_392.bin and apc_hw02_rpdu_392.bin were copied acroos, and the PDU rebooted automatically after each of the 2 .bin files. Unfortunately the GUI interface was not accessible.

Below is the hardware details:

Hardware Factory

Model Number:     AP7922
Serial Number:     ZA1302010923
Hardware Revision:     B2
Manufacture Date:     01/11/2013
MAC Address:     00 C0 B7 99 E0 EF
Management Uptime:     49 Days 23 Hours 32 Minutes
     
Application Module
Name:     rpdu
Version:     v3.7.4
Date:     03/13/2012
Time:     16:16:54


APC OS (AOS)
Name:     aos
Version:     v3.7.4
Date:     11/09/2011
Time:     11:45:09

Using the upgrd_util.exe in the apc_hw02_aos392 package, it failed with 'Firmware download failed'.

*************************

C:\Users\apc\Desktop\apc_hw02_aos392>upgrd_util.exe
NMC Upgrade Tool v1.2


American Power Conversion               Network Management Card AOS    v3.9.2
(c) Copyright 2004 All Rights Reserved  Rack PDU APP                   v3.9.2
-----------------------------------------------------------------------------
        Configuration detected ( iplist.txt ).
        Found 1 upgrade configuration(s)

        1:  Use parameters in configuration file
        2:  Enter new parameters for single upgrade
        3:  Exit Firmware upgrade tool
        Action: 1

        ***************************************************
        Starting Upgrade to 192.168.50.51.
        Checking network connection ...                  OK
        Testing login ...                                OK
        Checking version information ...                 OK
        Attempting to log in to 192.168.50.51 ...         OK
        Loading OS, please wait ...     Firmware download failed.
        Attempting to log in to 192.168.50.51 ...
        Could not log in to 192.168.50.51.

        *********** Upgrade Summary ***********

        Encountered 1 failures during upgrade.
        View 'result.txt' for details
        Warning: A file called 'iplist.txt' exists in this directory
        that may contain user names and passwords in clear text.
        You may want to delete this file if other users have access
        to this directory.


        Thank you for using APC products

        Press to exit.

*************************

Using the ftp method. There was not a single hash showing up in 10 minutes, so I have to abort it.

C:\Users\apc\Desktop\apc_hw02_aos392>ftp 192.168.50.51
Connected to 192.168.50.51.
220 AP7922 Network Management Card AOS v3.7.4 FTP server ready.
User (192.168.50.51:(none)): apc
331 User name okay, need password.
Password:
230 User logged in, proceed.
ftp> bin
200 TYPE Command okay.
ftp> hash
Hash mark printing On  ftp: (2048 bytes/hash mark) .
ftp> put apc_hw02_aos_392.bin
200 PORT Command okay.
150 File status okay; about to open data connection.
Aborting any active data connections...
425 STOR can't open data connection.
ftp>

Anyone has any idea what to do next? Thanks.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • ap7922
  • firmware
  • network-management-card
  • pdu
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:15 AM . Last Modified: ‎2024-03-18 11:32 PM

0 Likes
0
6087
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:15 AM . Last Modified: ‎2024-03-18 11:32 PM

Hi Angela,

I managed to upload rpdu 3.7.4 successfully and am able to login through the GUI now. Many thanks for your assistance.

Will try to upgrade to 3.9.2 again soon.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:15 AM . Last Modified: ‎2024-03-18 11:33 PM

0 Likes
0
6087
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:15 AM . Last Modified: ‎2024-03-18 11:33 PM

Hi Antonio,

Based on what you've shared, I would try rebooting the PDU's management interface and then re-try the manual FTP push. If you were not aware, this reboot does not affect outlet status on the PDU.

You'll need to do this through the Telnet (or SSH) interface with the web being inaccessible. Log in via Telnet or SSH and then go to the System Menu->Tools->Reboot Management Interface and you'll have to type YES to confirm that. Then, let the PDU reboot and you can see if the web interface comes back as well. Then, proceed and re-try the upgrade via manual FTP like you tried to at the bottom of your post.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:15 AM . Last Modified: ‎2024-03-18 11:33 PM

0 Likes
0
6087
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:15 AM . Last Modified: ‎2024-03-18 11:33 PM

Hi Angela,

Tried SSH using PuTTY, and it returned:

Disconnected: Received SSH2_MSG_CHANNEL_SUCCESS for nonexistent channel 65536.

Any idea why I am getting this error? As far as I can remember, the PDU was setup using SSH, not Telnet.

If I used Telent, it returned 'Network error: Connection refused'. Do you know of any way to reboot the PDU without affecting the outlets?

Thanks again.

Regards,
Antonio

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:15 AM . Last Modified: ‎2024-03-18 11:33 PM

0 Likes
0
6087
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:15 AM . Last Modified: ‎2024-03-18 11:33 PM

Oh, I found the problem with the SSH access.

http://www.apc.com/us/en/faqs/FA242581/

This is due to some incompatibility with newer PuTTy client versions and older SSH server versions in NMC1 products, this error message is received and access is not allowed. This will also likely affect WinSCP users since WinSCP and PuTTy share similar SSH and SCP code.

Unfortunately rebooting the management interface did not fix the problem. I logged in via SSH again and see the following screen:

American Power Conversion               Network Management Card AOS      v3.7.4
(c) Copyright 2009 All Rights Reserved  Rack PDU APP                     v3.9.2
-------------------------------------------------------------------------------
Name      : APCPDU1                                   Date : 24-Mar-17
Contact   : ICTS                                      Time : 08:44:33
Location  : OTEN                                      User : Administrator
Up Time   : 0 Days 0 Hours 2 Minutes                  Stat : P+ N+ A!


------- Control Console -------------------------------------------------------

     1- Device Manager
     2- Network
     3- System
     4- Logout

     - Main Menu, - Refresh

Interestingly the NMC AOS is v3.7.4 while the Rack PDU APP is v3.9.2. I ran the SCP command again to upload 'apc_hw02_aos_392.bin' and 'apc_hw02_rpdu_392.bin' again, but the AOS stayed on v3.7.4.

I also tried 'Reset to Defaults Except TCP/IP' and the problem persists.

  • Tags:
  • ap7922
  • nmc1
  • pdu
  • ssh
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:15 AM . Last Modified: ‎2024-03-18 11:32 PM

0 Likes
0
6087
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:15 AM . Last Modified: ‎2024-03-18 11:32 PM

Tried the 'NMC Upgrade Tool v1.2' again and failed. But the result.txt shows the following error:

Using AOS file        : AOS = apc_hw02_aos_392.bin
Using Application file: APP = apc_hw02_rpdu_392.bin

Checking network connection ...  Checking version information ...
 *************** Next **************

Before Upgrading the NMC the AOS is: ÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌÌ̈È
* Detected early version, two AOS upgrades required
Attempting to log in to 192.168.50.51 ... Log in sucessful
Loading OS, please wait ... Firmware download failed.
Attempting to log in to 192.168.50.51 ...
Could not log into 192.168.50.51.

Not all Network Management Cards were upgraded successfully:
    192.168.50.51: Could not log into the Management Card's FTP server.

Encountered 1 failures during upgrade.

According to the System Info, my AOS is 3.7.4 and the latest version is 3.9.2. I could not find anything other version available between them.

 -----------------------------------------------------------------------
        Module Information
        Description : Rack PDU APP
        -----------------------------------------------------------------------
        Name        : rpdu              Type        : StatApp
        Version     : 392               Sector      : 16
        Date        : 07/07/2016        Time        : 10:40:30
        CRC16       : D94B

        Press to continue...

        Description : Network Management Card AOS
        -----------------------------------------------------------------------
        Name        : aos               Type        : APC OS
        Version     : 374               Sector      : 47
        Date        : 11/09/2011        Time        : 11:45:09
        CRC16       : 49C6

        Press to continue...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:15 AM . Last Modified: ‎2024-03-18 11:32 PM

0 Likes
0
6087
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:15 AM . Last Modified: ‎2024-03-18 11:32 PM

Hi Angela,

Still working on it. Tried scp again, but it now returns 'Fatal: Network error: Connection refused'.

Can you also give me the aos 3.7.4 too?

Yes, I have been following FA156047 since day one. Thanks for the link.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:15 AM . Last Modified: ‎2024-03-18 11:32 PM

0 Likes
0
6088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:15 AM . Last Modified: ‎2024-03-18 11:32 PM

Hi Angela,

I managed to upload rpdu 3.7.4 successfully and am able to login through the GUI now. Many thanks for your assistance.

Will try to upgrade to 3.9.2 again soon.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore