Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

AP7920B firmware

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP7920B firmware
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
OmegaPoint6
OmegaPoint6
Cadet

Posted: ‎2025-10-29 06:19 AM

0 Likes
3
265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-29 06:19 AM

AP7920B firmware

I just purchased a used AP7920B and I'm having trouble updating the firmware.

 

It has NMC2 so I download the NMC2 firmware from the product page but for both 7.2.4 & 7.1.4 I get the following errors from the upgrade too

[10/29/2025 11:56:13] Firmware distribution does not match target device platform; this could be due to a corrupt distribution.
[10/29/2025 11:56:15] Unable to update device 192.168.1.7 with Boot Monitor; stopping all further processing of this device!

 

The PDU is currently running v6.4.4, I can see references online to newer 6.x versions but haven't been able to find a download.

 

Does anyone know if it is safe to manually upgrade to the latest 7.x version? If not where can I get the latest version my PDU can support.

 

Full version info:

pc>about
E000: Success
Hardware Factory
Model Number:           AP7920B
Serial Number:          xxxxxxxx
Hardware Revision:      B2
Manufacture Date:       02/08/2017
MAC Address:            xxxxxxxx
Management Uptime:      0 Days 0 Hours 38 Minutes

Network Management Card
Model Number:           0G-1238
Serial Number:          xxxxxxxx
Hardware Revision:      05
Manufacture Date:       02/07/2017

Application Module
Name:                   rpdu2g
Version:                v6.4.4
Date:                   Aug 16 2016
Time:                   10:44:51

APC OS(AOS)
Name:                   aos
Version:                v6.4.4
Date:                   Jun 13 2016
Time:                   16:21:53

APC Boot Monitor
Name:                   bootmon
Version:                v1.0.8
Date:                   Apr  8 2014
Time:                   10:59:40

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Kirk Teken
Kirk

Posted: ‎2025-10-30 07:48 AM . Last Modified: ‎2025-10-30 07:49 AM

1 Like
2
252
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-30 07:48 AM . Last Modified: ‎2025-10-30 07:49 AM

Generally speaking, this ridiculous nonsensical message indicates the following conditions:

 

User: The user is not an Administrator with privileges as such do not use a Device / Network / Read Only account when entering the credentials.

 

Protocol: Do not use SCP but FTP during the upgrade process and insure FTP is enabled in the NMC.

 

Logs: Do not save logs if present as this sometimes causes a delay in the upgrade process as such results in a failure. 

If all the above has failed than the next option is to use the CLI and upload the individual files as outlined in the APC NMC FAQ.

 

NOTE: You’re best served by contacting APC Technical Support to obtain any interim 6.X.X NMC rPDU firmware before jumping to the 7.X.X branch to avoid bricking the rPDU.

 

Have them confirm the NMC hardware in place and relevant rPDU firmware. 

 

Questions Ask . . . 👍

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Teken
Kirk Teken
Kirk

Posted: ‎2025-10-30 07:48 AM . Last Modified: ‎2025-10-30 07:49 AM

1 Like
2
253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-30 07:48 AM . Last Modified: ‎2025-10-30 07:49 AM

Generally speaking, this ridiculous nonsensical message indicates the following conditions:

 

User: The user is not an Administrator with privileges as such do not use a Device / Network / Read Only account when entering the credentials.

 

Protocol: Do not use SCP but FTP during the upgrade process and insure FTP is enabled in the NMC.

 

Logs: Do not save logs if present as this sometimes causes a delay in the upgrade process as such results in a failure. 

If all the above has failed than the next option is to use the CLI and upload the individual files as outlined in the APC NMC FAQ.

 

NOTE: You’re best served by contacting APC Technical Support to obtain any interim 6.X.X NMC rPDU firmware before jumping to the 7.X.X branch to avoid bricking the rPDU.

 

Have them confirm the NMC hardware in place and relevant rPDU firmware. 

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

OmegaPoint6
OmegaPoint6
Cadet

Posted: ‎2025-10-30 09:08 AM

In response to Teken
0 Likes
1
226
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-30 09:08 AM

Thank you, it was the FTP/SCP thing. I risked the direct upgrade and it worked

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-10-31 04:55 AM

In response to OmegaPoint6
0 Likes
0
222
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-31 04:55 AM

That’s great to hear and appreciate you following up with the solution and final outcome.

 

Rock On . . . 🤟

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore