Hi, I would like to know the voltage present at the C13 and C19 outlets of this PDU. The C19 should be 208v. But I have a Sun rack that has C13 cables and they are 208v so I'm confused.
Thanks
Greg
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:53 AM . Last Modified: 2024-02-14 10:39 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:53 AM . Last Modified: 2024-02-14 10:39 PM
Most excellent, thanks K-Dog
Greg
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:53 AM . Last Modified: 2024-02-14 10:39 PM
Both C13 and C19 are 208v on the output. Generally speaking the C19s are used for equipment that draws more amps. I have seen C13-C14 cords that shipped with some brands of IT equipment that was made from 18 gauge and smaller wiring, meaning it is not rated for higher current carrying capacity. You will see the C19s on rack pdus powering blade servers with 50-60 amp input into the rpdus spread out over 4 C13s for maximum allowable current draw on each of the receptacles.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:53 AM . Last Modified: 2024-02-14 10:39 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:53 AM . Last Modified: 2024-02-14 10:39 PM
Most excellent, thanks K-Dog
Greg