AP7753 unexpectedly dropped load

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP7753 unexpectedly dropped load
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:02 PM

0 Likes
5
2363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:02 PM

AP7753 unexpectedly dropped load

I had a very unpleasant experience the other night while attempting to update an AP7753 ATS. It was showing "Source B selected, Switchover Possible" so I unplugged the Source A power cable (the firmware update has a huge warning about not updating the ATS with both sources connected, because if there is new ATS microcontroller firmware there is a possibility of shorting the 2 sources together). Immediately after unplugging the Source A cable (remember, Source B was supposedly selected and providing power) the ATS dropped all loads. I checked and the cable was clearly labeled Source A, and even if it was mislabeled, the ATS was reporting "Switchover Possible" so the worst case is (supposedly) a source switch.

Immediately after I heard all the equipment power down, I plugged the source cable back in, but due to power sequencing in the downline AP7900 PDUs it took some time for the connected equipment to power back on, boot, etc. Meanwhile I'm looking at several dozen dead 10GbE links and hundreds of GigE links as all of the network switching gear lost power, along with 4 core routers.

The ATS apparently doesn't think it did anything wrong:

08/26/2017      21:19:29        Automatic Transfer Switch: Fault cleared on Source A.   0x0C13
08/26/2017      21:19:28        Automatic Transfer Switch: Redundancy has been restored. Source A is available. 0x0C03
08/26/2017      21:19:22        Automatic Transfer Switch: Fault exists on Source A.    0x0C12
08/26/2017      21:19:05        Automatic Transfer Switch: ATS has lost redundancy. Source A is not available.  0x0C02
08/26/2017      21:18:26        System: Console user 'root' logged in from xxx.xxx.xxx.xxx.        0x0014

The 23 seconds was my reaction time to get the cable plugged back in. Nowhere in the log does it show the load dropping. The AOS/G2ATS firmware is 374/371 and the ATS microcontroller firmware is 2.0.3.

We have been following the suggested best practices, including having both sources on the same AC phase (though from different circuits on different datacenter PDUs), low sensitivity, preferred source none (non-reverting), etc.

This is very disappointing. I need to replace at least the 4 AP7753 at this site, and probably the units at the other sites as well. The question is, go with APC again and hope things are better / more reliable, or with some other brand. If a different brand, which?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:01 PM

0 Likes
0
2363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:01 PM

This was the first load drop in well over 4 years (and also the first firmware upgrade performed since they were installed). The first unit went fine, this was the second unit, and we abandoned plans to upgrade the 3rd and 4th units that night.

If it comes out, something else needs to replace it - either the new APC unit or something from another vendor. We'd probably schedule a time period to do all four at this site.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
B-DoubleE_apc
Commander B-DoubleE_apc
Commander

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:02 PM

0 Likes
0
2363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:02 PM

Hi Terry,

I'm sorry for this issue with your ATS. Do you happen to remember what LED's were lit up on the front panel (just to confirm if it showed the same information as the web interface)? Additionally, would you be able to send me:

  • Serial number of the ATS
  • Copies of the event/data/config files (instructions to download here: http://www.schneider-electric.com/en/faqs/index?page=content&id=FA156131)
  • A screenshot of the "Event Counts" page in the Web UI, under the "Unit" tab

So you're aware, we have a new generation of ATS launching in the coming weeks (manual here: http://www.apc.com/salestools/HLAE-AJCRQQ/HLAE-AJCRQQ_R1_EN.pdf) that has many improvements over the previous generation, such as improved transfer time and an embedded NMC2.

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:02 PM

0 Likes
0
2363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:02 PM

The front panel showed A and B LEDs green, the lower curved arrow lit, and the load LED green.

I have collected all of the data you requested, but I can't send you a private message with the link due to the way the forum is set up. Can you PM me so I can reply?

I'll look at the detailed specs of the new unit (AP4453) once it is announced.

Reply

Link copied. Please paste this link to share this article on your social media post.

B-DoubleE_apc
Commander B-DoubleE_apc
Commander

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:01 PM

0 Likes
0
2363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:01 PM

Hi Terry,

PM sent with my email address

Reply

Link copied. Please paste this link to share this article on your social media post.

B-DoubleE_apc
Commander B-DoubleE_apc
Commander

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:01 PM

0 Likes
0
2363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:01 PM

Hi Terry,

I've reviewed the files, but there aren't any smoking guns in the logs. Is this ATS still in deployment, or are you able to bench test it? Have you tried to force source switches since the load drop to see how the ATS behaves?

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:01 PM

0 Likes
0
2364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:22 AM . Last Modified: ‎2024-02-14 11:01 PM

This was the first load drop in well over 4 years (and also the first firmware upgrade performed since they were installed). The first unit went fine, this was the second unit, and we abandoned plans to upgrade the 3rd and 4th units that night.

If it comes out, something else needs to replace it - either the new APC unit or something from another vendor. We'd probably schedule a time period to do all four at this site.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of