AP7723 failed during Firmware Upgrade

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP7723 failed during Firmware Upgrade
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:20 AM

0 Likes
11
2015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:20 AM

AP7723 failed during Firmware Upgrade

Result.TXT
===

Starting Upgrade 10/10/12: 10:51:21
-----------------
10/10/12: 10:51:21 xxx.xxx.xxx.xxx: Testing device connection
10/10/12: 10:51:21 xxx.xxx.xxx.xxx: Device connection passed
10/10/12: 10:51:22 xxx.xxx.xxx.xxx: Testing FTP Log-in
10/10/12: 10:51:25 xxx.xxx.xxx.xxx: FTP Log-in passed
10/10/12: 10:51:26 xxx.xxx.xxx.xxx: Saving data file
10/10/12: 10:51:37 xxx.xxx.xxx.xxx: AOS Prior to firmware transfer: Network Management Card AOS v3.7.4
10/10/12: 10:51:37 xxx.xxx.xxx.xxx: APP Prior to firmware transfer: Automatic Transfer Switch APP v3.7.0
10/10/12: 10:51:44 xxx.xxx.xxx.xxx: Saving event & configuration files
10/10/12: 10:51:49 xxx.xxx.xxx.xxx: Transferring OS
10/10/12: 10:53:21 xxx.xxx.xxx.xxx: ERROR --> OS transfer failed
===

Afterwards, when access by Browser, I only got:
===

Error: The application was not able to load.

You are attempting to access an APC device.

There was a problem loading the application. Please login to the device via telnet for more details.

===

I still can telnet into the device. Reset to factory default does not help.

How to rescue my ATS AP7723?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • apc
  • ats
  • firmware
  • power
  • smart-ups
  • snmp
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:19 AM

0 Likes
0
2015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:19 AM

ok, that helped me at least - what you pasted there.

what i would like you to do is still make sure the secondary source is removed (very important) and i want you to refer to the manual FTP instructions for NMC1 in the knowledge base article below i reference. You will need to FTP to the ATS and manually copy over the apc_hw02_g2ats_370.bin file ONLY (since your AOS file is already updated) you probably have extracted from when you ran the upgrade. are you familiar with this type of thing? do you know where teh apc_hw02_g2ats_370.bin is?

instructions are in FA156047 @ http://www.apc.com/site/support/index.cfm/faq/

once this file has transferred over, log out of FTP with the device and give it about 5 minutes before you reconnect to it to see if the upgrade will complete itself.

let me know how that goes and please let me know if you have any questions before you begin this procedure.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:20 AM

0 Likes
0
2015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:20 AM

can you tell me whether or not you followed these instructions?

FA156178 @ http://www.apc.com/site/support/index.cfm/faq/

these are required.

also, could you please provide your event.txt from the NMC?

instructions are @ FA156131 using the knowledge base link above.

this will help tell me where you are at so we can figure out how to proceed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:20 AM

0 Likes
0
2015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:20 AM

Yes. I followed that article.

Before the upgrade, I only have one input with power supplied.

Actually, the upgrade do not show "completed" and just exit with error.

From the Upgrade Directory, I found a IP_events.txt. Is that what you are looking for?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:20 AM

0 Likes
0
2015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:20 AM

alrighty. and no, i need event.txt from the NMC which is downloaded via FTP - instructions in the article I provided. you should still be able to get this file even in the state the ATS is in.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:20 AM

0 Likes
0
2015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:20 AM

Finally, I use the EXE updater and updated to 3.7.1 without issues.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:20 AM

0 Likes
0
2015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:20 AM

From the ftp session, I can only found a "apc_hw02_aos_374.bin" and subfolder "sec".

I cannot list files inside "sec".

Thanks a lot!

====
Connected to XXX.XXX.XXX.XXX
220 AP7723 Network Management Card AOS v3.7.4 FTP server ready.
User (XXX.XXX.XXX.XXX:(none)): apc
331 User name okay, need password.
Password:
230 User logged in, proceed.
ftp> dir
200 PORT Command okay.
150 File status okay; about to open data connection.
--wx-wx-wx 1 apc apc 1572864 Nov 09 2011 apc_hw02_aos_374.bin
drwxrwxrwx 1 apc apc 0 Nov 09 2011 sec/
226 Closing data connection.
ftp: 134 bytes received in 0.00Seconds 134.00Kbytes/sec.
ftp> cd sec
250 CWD requested file action okay, completed.
ftp> dir
200 PORT Command okay.
150 File status okay; about to open data connection.
226 Closing data connection.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:20 AM

0 Likes
0
2015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:20 AM

strange. can you go to through the telnet interface and hit ctrl-L and try to get me the most recent events right after the upgrade happened.

are you familar with the telnet interface?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:19 AM

0 Likes
0
2015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:19 AM

I can telnet into the device.

American Power Conversion Network Management Card AOS v3.7.4
(c) Copyright 2009 All Rights Reserved
-------------------------------------------------------------------------------
Name : Unknown Date : 10/11/2012
Contact : Unknown Time : 12:58:46
Location : Unknown User : Administrator
Up Time : 1 Day 0 Hours 55 Minutes Stat : P+ N+ A-


------- Control Console -------------------------------------------------------

1- Device Manager
2- Network
3- System
4- Logout

- Main Menu, - Refresh


As I am not local, I only telnet over network to the ATS.

For Item 1, it is empty when I go into it.

has no effect.

On Menu 2, 3, 4, there is no mention of Event Log.

Thanks a lot.

Message was edited by: sampson_fung@executivecentre.c

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:19 AM

0 Likes
0
2016
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:19 AM

ok, that helped me at least - what you pasted there.

what i would like you to do is still make sure the secondary source is removed (very important) and i want you to refer to the manual FTP instructions for NMC1 in the knowledge base article below i reference. You will need to FTP to the ATS and manually copy over the apc_hw02_g2ats_370.bin file ONLY (since your AOS file is already updated) you probably have extracted from when you ran the upgrade. are you familiar with this type of thing? do you know where teh apc_hw02_g2ats_370.bin is?

instructions are in FA156047 @ http://www.apc.com/site/support/index.cfm/faq/

once this file has transferred over, log out of FTP with the device and give it about 5 minutes before you reconnect to it to see if the upgrade will complete itself.

let me know how that goes and please let me know if you have any questions before you begin this procedure.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:19 AM

0 Likes
0
2015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:19 AM

Just want to clarify:

1. "Secondary Input". Does it always mean "Input B"? Or just make sure only one input is connecting to ATS will be OK?
- In my case, it happened "Input A" is unplugged as "Secondary"

2. When I logoff from FTP, the ATS will auto reload the firmware file and I do not need to force a reboot via telnet, am I correct?

Thanks very much!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:19 AM

0 Likes
0
2015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:19 AM

After upload of the file to ATS via ftp, in 5 seconds, the Web Console is up again: (About information include at the end)

As I wanted to upgrade to 3.71, should I re-use the EXE updater or just upload the 3.71 BIN file via ftp?

Thank you very much for the help!


Hardware Factory

Model Number: AP7723
Serial Number: 5A1224T08149
Hardware Revision: 01
Manufacture Date: 06/15/2012
MAC Address: 00 C0 B7 9B CB 0B
Management Uptime: 0 Days 0 Hours 3 Minutes



Application Module

Name: g2ats
Version: v3.7.0
Date: 11/09/2011
Time: 12:29:05



APC OS (AOS)

Name: aos
Version: v3.7.4
Date: 11/09/2011
Time: 11:45:09

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:19 AM

0 Likes
0
2015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:34 AM . Last Modified: ‎2024-03-18 01:19 AM

i would run through the .exe again or manual FTP. this time, you'll need to put both the AOS 3.7.4 file (first) and then the g2ats 3.7.1 file (second).

your secondary source does not always need to be input B - it just means your unloaded source.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of