Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

ACSC101 - FTP upload is truncating file

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: ACSC101 - FTP upload is truncating file
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:01 AM

0 Likes
5
333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:01 AM

ACSC101 - FTP upload is truncating file

This question was originally posted by Mike on APC forums on 1/4/2015


ACSC APP v3.5.6
AOS v3.6.1

I've had the FTP upload feature enabled, to collect data and allow me to analyse the performance over an extended period.

I went to use the data today and produce all the pretty graphs, only to find that the file is truncated to match the live data available on the crac  unit itself.

I mean... what is the point of automatically uploading the data, if the upload is going to obliterate the stored history?

With my UPS units, there is an option to start a new file every day, presumably so that this doesn't happen, but no such feature exists on the crac.

This makes it hard to get any long-term information if fine granularity is required.

Is there is fix for this ? 

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • acsc101
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:01 AM

0 Likes
0
333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:01 AM

This reply was originally posted by Mike on APC forums on 1/5/2015


Hi,

This perhaps gives some information on how it is SUPPOSED to work.

However, this is not what is actually happening with my ACSC101.

Instead, it appears to be over-writing the file with the current "live" data, rather than appending as it should.

I have the interval frequency set very low (to try and find out why it is cycling on-off so often) and so the datalog on the CRAC is always full and dropping records as new ones are added.

This means that every time the FTP file is "updated" and being over-written, I am losing all of my historical data.

(Actually, because the CRAC doesn't do a nice smooth push-pop of newest-oldest records, but instead seems to kill the oldest half when it hits full, and then starts to grow the log again... this means that depending on when you view the log and/or saved file, it can be as bad as only having the most recent half-log details available).

FYI: I'm not touching the datalog file on the FTP server, and if I need to view it, I simply make a copy and work with that.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:01 AM

0 Likes
0
333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:01 AM

This reply was originally posted by Angela on APC forums on 1/5/2015


Can you confirm your FTP server supports/has FTP append enabled? I was under the impression the Network Management Card's data log rotation file upload would just append to the same file name if that was enabled which would alleviate the problem you mentioned.

Though, you mentioned ACSC101 as your cooling unit? For these units with v3 firmware, I believe they added the option for unique file name in a later AOS version (I just checked a cooling unit with v3.7.3 which is what I am basing that comment on and it supported Unique File Name which is what option I think you're saying your UPSs have) so I need to ask our cooling tech support if this unit has a newer firmware available with AOS v3.7.X. I don't see one available unfortunately - the only newer versions I see contain an update to the ACSC APP and not the AOS (APC Operating System).

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:01 AM

0 Likes
0
333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:01 AM

This reply was originally posted by Mike on APC forums on 1/5/2015


Hi,

I'm just using IIS-6.0 for the ftp server, and there is not much there to configure - usually just either works or doesn't. I believe that appending rather than overwriting should not be an issue, but admit that I'm not 100% certain on that point.

There is actually no option for unique files in the CRAC version of AOS, as there is with the UPS version of AOS.

Please see the attached screen-cap of the Data Log Rotation tab.

I'm running AOS v3.6.1 and ACSC APP v3.5.6  because these are the latest I could find listed on the APC site, and I didn't want to try loading something else in case I totally screwed the unit. If the ACSC101 will support a later version of AOS then I'm willing to give it a shot, but I'd want to be sure I'm doing the right thing before I try that.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:01 AM

0 Likes
0
333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:01 AM

This reply was originally posted by Angela on APC forums on 1/5/2015


Sorry I was unclear. I was basically saying what you said. I don't see the Unique File Name option in that firmware on the unit I have and was assuming that was what you were referring to when you noted you have a different option on your UPSs. 

I also don't see a newer firmware with a newer AOS but I will double check with our cooling team tomorrow regarding this unit and what may or may not be coming in the future. 

I also am not too familiar with IIS FTP but I will see if I can find anything else out. 

Edit: There is no newer firmware available for this model and it does not appear like a new update is in progress either. I am going to see if I can find out more about the data log rotation on our side and confirm it uses the FTP APPE command. And see if I can find anything on IIS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:01 AM

0 Likes
0
333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:01 AM

This reply was originally posted by Angela on APC forums on 1/5/2015


I found some general information on how our data log rotation works:

By design, the NMC records the last row of the data log that it uploaded after a successful offload of the data log through the data log rotation functions. If the user decides that (s)he wants to delete parts of the data log, then they will never get the missing parts back. What will happen is that when the card offloads the data log again, it will start at that last row it left off at and append those values.

For sake of this example, we will include ID numbers (these are not visible in the data logs to the user): When the card does it's initial unique data log rotation, it sends rows for ID's 0000 through 0399. The pointer is now at ID 0400. The card, at it's next rotation, will offload rows with IDs 0400-0799 (or a shorter list if you manually perform the log offloading). Now let's say you've intervened and deleted rows 0201-0399 in the data log that is sitting on your FTP server before rows 0400-0799 get pushed. The NMC does not parse out which lines are missing - it will continue at row 0400 regardless of what's missing from the file to which it is appending.

So this gives a little detail on how the rotation works.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:01 AM

0 Likes
0
334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:01 AM

This reply was originally posted by Mike on APC forums on 1/5/2015


Hi,

This perhaps gives some information on how it is SUPPOSED to work.

However, this is not what is actually happening with my ACSC101.

Instead, it appears to be over-writing the file with the current "live" data, rather than appending as it should.

I have the interval frequency set very low (to try and find out why it is cycling on-off so often) and so the datalog on the CRAC is always full and dropping records as new ones are added.

This means that every time the FTP file is "updated" and being over-written, I am losing all of my historical data.

(Actually, because the CRAC doesn't do a nice smooth push-pop of newest-oldest records, but instead seems to kill the oldest half when it hits full, and then starts to grow the log again... this means that depending on when you view the log and/or saved file, it can be as bad as only having the most recent half-log details available).

FYI: I'm not touching the datalog file on the FTP server, and if I need to view it, I simply make a copy and work with that.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc