ACSC100 No Output

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ACSC100 No Output
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:09 AM . Last Modified: ‎2024-03-18 03:45 AM

0 Likes
6
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:09 AM . Last Modified: ‎2024-03-18 03:45 AM

ACSC100 No Output

I am at my end with our ACSC100. We have had it installed in our server closet for about two years. For the first several months it worked great, then due toa failed internal component, it stopped working completely. APC responded promptly by replacing the component and all was back to normal. However, over the last year or so, performance has steadily degraded. We attributed this to two things. One, environmental conditions, we were concerned that our plenum could simply not absorb the exhaust air. And second, because of additional equipment added over the last year. Since these concerns were recognized, we have taken the steps to, exhaust the condenser air out of our plenum, and we have retired equipment no longer in use to offset the equipment added.

Nevertheless, we still cannot get the ACSC to run higher than 600 CFM and no more output than about 2.3kw in In-Row mode, and no more that 4.1kw in Spot Mode.

I have reset and checked factory defaults numerous times and have insured that we have the most current software updates.

Since we have started working on it intensively over the last few days, I have also been getting a "Persistent Low Suction Pressure" alarm causing it to shut down. Upon inspecting the unit, I discovered that when the failed component had been replaced last year, the tech had crimped both of the suction tubes between the side panel and the bar behind it. I fixed this but still am getting the alarm.

Any advice would be much appreciated. My company cannot afford a new AC unit at this time, and I am convinced this one can do what we need it to.

Michael

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • acsc
  • acsc100
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:10 AM . Last Modified: ‎2024-03-18 03:45 AM

0 Likes
0
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:10 AM . Last Modified: ‎2024-03-18 03:45 AM

I spoke with Cooling support and they have advised, as you did earlier, that it is likely that our refrigerant is low. I will post back with results after a recharge.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 05:09 AM . Last Modified: ‎2024-03-18 03:45 AM

0 Likes
0
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:09 AM . Last Modified: ‎2024-03-18 03:45 AM

I will be checking with our Air Support team in regards to this question, and either I or a member of their team will post shortly. If you feel you need quicker support please call 1-800-800-4272 and select the option for Air/Cooling support.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 05:09 AM . Last Modified: ‎2024-03-18 03:45 AM

0 Likes
0
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:09 AM . Last Modified: ‎2024-03-18 03:45 AM

Based on some discussion with our air team, the general understanding of the issue is there is a persistent low suction alarm with the existence of increased load and poor performance? Without more detailed unit status/numerical information or pressure data, the most accurate estimation of the issue is that it is probably a refrigeration-related issue. The best course of action would be to have a refrigeration tech come on side to check for any leaks in the system (system is 410a), or call APC Air Support at 1-888-695-6500 to check on any existing services/entitlements of yours.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:10 AM . Last Modified: ‎2024-03-18 03:45 AM

0 Likes
0
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:10 AM . Last Modified: ‎2024-03-18 03:45 AM

Erasmus, thanks for the response. I think refrigerant would be an easy solution.

Here is the current status of the unit:

Group Overview

Cool Setpoint: 72.0 °F
Supply Air Setpoint: 64.0 °F
Air Flow: 613 CFM

Maximum Rack Inlet Temperature: 81.7 °F
Minimum Rack Inlet Temperature: 81.7 °F
Maximum Return Air Temperature: 88.0 °F
Minimum Return Air Temperature: 88.0 °F

Cool Output: 2.6 kW
Cool Demand: 2.6 kW

Unit Overview

Operating Mode: On
Compressor State: On
Cool Output: 2.5 kW
Cool Demand: 2.5 kW
Rack Inlet Temperature: 81.8 °F
Supply Air Temperature: 75.1 °F
Return Air Temperature: 88.1 °F
Condenser Outlet Temperature: 110.8 °F
Condenser Inlet Temperature: 81.4 °F
Suction Temperature: 86.3 °F
Air Flow: 613 CFM
Evaporator Fan Speed: 51.1 %
Condenser Fan Speed: 40.4 %

Unit Detailed Status

Input State: Open
Output State: Closed
Filter Differential Pressure: 0.02 "WC
Suction Pressure: 114 psi
Discharge Pressure: 391 psi
Superheat Temperature: 48.4 °F

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:10 AM . Last Modified: ‎2024-03-18 03:45 AM

0 Likes
0
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:10 AM . Last Modified: ‎2024-03-18 03:45 AM

One other additional detail. When switched into Spot mode (Discrete), the system will sharply ramp up to 1200CFM/12kw then quickly fall back down to 600CFM/4kw regardless of setpoints.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 05:10 AM . Last Modified: ‎2024-03-18 03:45 AM

0 Likes
0
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:10 AM . Last Modified: ‎2024-03-18 03:45 AM

Ok, well again after some discussion with our air team the amount of information and nature of the issue apparently is believed to be handled best by phone, especially if you need to discuss a site visit. That's at least the "preferred suggestion", the number is the same one I provided in my previous post.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:10 AM . Last Modified: ‎2024-03-18 03:45 AM

0 Likes
0
990
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:10 AM . Last Modified: ‎2024-03-18 03:45 AM

I spoke with Cooling support and they have advised, as you did earlier, that it is likely that our refrigerant is low. I will post back with results after a recharge.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of