ACRP 502 Multiple Units Installation With ONE Chiller

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ACRP 502 Multiple Units Installation With ONE Chiller
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

0 Likes
7
1285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

ACRP 502 Multiple Units Installation With ONE Chiller

Dear Folks,

Please let me know if how 5 units of ACRP502, chilled water, 70 kW each, can be installed with a single chiller. Basically With ACRP502, it doesn't have CDU (Cooling Distribution Unit) Therefore how piping of 5 units would be done???

In Installation Manual of ACRP, Chilled water, I couldn't find any fruitful info.

Please help.

Thanks in advance.

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

0 Likes
0
1284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

Dear Folks,

Please let me know if how 5 units of ACRP502, chilled water, 70 kW each, can be installed with a single chiller. Basically With ACRP502, it doesn't have CDU (Cooling Distribution Unit) Therefore how piping of 5 units would be done???

In Installation Manual of ACRP, Chilled water, I couldn't find any fruitful info.

Please help.

Thanks in advance.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

0 Likes
0
1284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

Dear Karbonphiber,

Thanks for the detailed info. I got it. but your given attachment is a 'blank page'. It has nothing. Please re attach, if it has some error.

I appreciate your reply.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

0 Likes
0
1284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

As long as the chiller has enough capacity for all the unit connected, multiple ACRC units can be attached to the one chiller. The main concern in the piping is to make sure the the ACRC units get the required water flow to operate properly. This can be done without a CDU but the piping needs to be designed for each individual Data Center. Manifolds are an option for this. To get the best design for your data center, please contact the local sales team, and they can work with you to design the Data Center to meet the cooling needs.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

0 Likes
0
1284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

Dear L2,

Thanks for the detailed reply. But please notice that we are talking about ACRP502 not ACRC units.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

0 Likes
0
1284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

Recently you requested personal assistance from the Schneider Electric Customer Care Center through our on-line support center supporting APC products. Below is a summary of your request and our response.


We will assume your issue has been resolved if we do not hear from you within 21 days.


Thank you for allowing us to be of service to you.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

0 Likes
0
1284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

Dear L2,

Sorry to say but I don't remember that when I posted a request at Schneider Electric Customer Care Center and I can not see any summary below?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

0 Likes
0
1284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

Recently you requested personal assistance from the Schneider Electric Customer Care Center through our on-line support center supporting APC products. Below is a summary of your request and our response.


We will assume your issue has been resolved if we do not hear from you within 21 days.


Thank you for allowing us to be of service to you.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

0 Likes
0
1285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:53 AM . Last Modified: ‎2024-03-19 12:30 AM

Dear Folks,

Please let me know if how 5 units of ACRP502, chilled water, 70 kW each, can be installed with a single chiller. Basically With ACRP502, it doesn't have CDU (Cooling Distribution Unit) Therefore how piping of 5 units would be done???

In Installation Manual of ACRP, Chilled water, I couldn't find any fruitful info.

Please help.

Thanks in advance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore