Good Day,
I recently discovered that two ACRD units with two different PID settings, first unit P - 7.64, I - 2.81 & D - 0.
The second unit has P- 4.17, I - 2.3 & D - 1.62.
Both units has the latest firmware APP - 3.7.4 & AOS 3.9.0,
Can anyone explain why and which should the units be using? both units were purchased at the same time.
Posted: 2021-07-09 04:29 AM
This reply was originally posted by terrence on APC forums on 11/21/2017
thanks much.
Posted: 2021-07-09 04:29 AM
This reply was originally posted by L2SupportServices-Cooling on APC forums on 11/21/2017
Hello. The PID's should be set to the settings below. Set the first unit to the correct settings. They should not be changed from the factory settings.
Thank you
P = 4.17
I = 2.3
D = 1.62
Posted: 2021-07-09 04:29 AM
This reply was originally posted by terrence on APC forums on 11/21/2017
So that different PID setting is incorrect? Would the unit modify the PID settings to match the environment it is operating in? Because as far I can tell those settings where never touched since it was bought
Posted: 2021-07-09 04:29 AM
This reply was originally posted by L2SupportServices-Cooling on APC forums on 11/21/2017
Hello Terrence. The PID settings will not auto change. The only way to change them is though the front screen or webcard.
Thank you
Posted: 2021-07-09 04:29 AM
This reply was originally posted by terrence on APC forums on 11/21/2017
thanks much.