Hi,
Im currently running one ACRC 103 Chilled water.
The cooling effect displayed is in the range 2-4 KW.
The Fan speed is on max, with 1500 litres of air per second.
And the temperature is to high.
How can I "debug" this situation?
Since this is a 18KW cooler that never goes above 4, there has to be something wrong.
Waterflow? Water temp?
Any hints would be appreciated.
Terje
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:58 AM . Last Modified: 2024-03-18 01:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:58 AM . Last Modified: 2024-03-18 01:04 AM
I am a little confused by the data: the "Supply Air" is reporting as 17.8 C which looks good, but the "Rack Inlet" - which is what is reported by the remote sensor you said is attached to the front of the rack, and is where the cool supply air should reach - is reporting 29 C ? Its almost like the InRow AC is installed backwards or something. Do you have the InRow right beside this rack and thus create is a nice cold aisle ?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:57 AM . Last Modified: 2024-03-18 01:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:57 AM . Last Modified: 2024-03-18 01:04 AM
So you are getting a reading for "cooling output" of 2 to 4 kw. Have you installed the supply air probe (remote temperature sensor) on the face of the server rack you are cooling ? What is your "Cool Setpoint" ? It might also help to pass on the readings that are coming up for "Supply Air", "Return Air", "entering water temperature" and "fluid valve position"....
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:58 AM . Last Modified: 2024-03-18 01:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:58 AM . Last Modified: 2024-03-18 01:04 AM
I even mad notes of the values, but for some reason I submitted without this information:
Sensor is installed -> Supply Air 17,8c
Return air: 26,2c
Rack Inlet: 28,9c
Cool setpoint: 22.2c
MaxRack: 29,3c
Fluid in: 11,7c
Fluid out: 13,9c
Fluid flow: 0,5l / s
Fluid valve pos: 52%
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:58 AM . Last Modified: 2024-03-18 01:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:58 AM . Last Modified: 2024-03-18 01:04 AM
I am a little confused by the data: the "Supply Air" is reporting as 17.8 C which looks good, but the "Rack Inlet" - which is what is reported by the remote sensor you said is attached to the front of the rack, and is where the cool supply air should reach - is reporting 29 C ? Its almost like the InRow AC is installed backwards or something. Do you have the InRow right beside this rack and thus create is a nice cold aisle ?