Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

A question regarding proper selection

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • A question regarding proper selection
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:43 PM . Last Modified: ‎2024-03-14 01:22 AM

0 Likes
3
945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:43 PM . Last Modified: ‎2024-03-14 01:22 AM

A question regarding proper selection

I recently had yet another power failure, of which we have a number, at home and BOTH current UPS systems failed. One ran for perhaps 30 seconds, the other not at all. They are 2 years or so old and both worked fine before.

I have a mostly Mac network and we recently expanded to consolidate switches, with an HP 1810G, and I am using a couple of routers on two subnets. We support 4 systems nominally and I want two of them on UPS along with the VoIP stuff, routers and switch. Also the NAS if possible.

I would like to install a single UPS for the above equipment.

The APC site recommends the Smart-UPS 1000 VA LCD, SMT1000.

I have a few questions that I cannot seem to find answers for and I wonder if someone who knows might tell me please either where on earth to look or what is the right way to go:

1) The guide says to plug equipment directly into the UPS. I cannot do this. The equipment is in the same room but at either end of it with the switch and routers in the middle. I can run solid core custom power cable or extension cords or any combination. Why is this a requirement and how can I resolve it?

2) I would dearly love to have network management so I can track this thing remotely as well as at home. Can I do this with a Mac site? What is the best software to accomplish this if it can be accomplished at all?

3) What is the distinction between the "Main outlet" and "Switched outlet" groups? I cannot see how that is configured. The SMT1000 appears to have 8 outlets and all are on the main switch. Are these 8 outlets configurable and, if so, how?

4) The SMT1000 appears to have an RJ45 connector and a slot for a network card. What is the difference between the two.

Thanks, I wish I could find these answers on-line or in the reference material, or FAQ. Is there some other documentation I am missing?

Lawrence

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:43 PM . Last Modified: ‎2024-03-14 01:21 AM

0 Likes
0
945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:43 PM . Last Modified: ‎2024-03-14 01:21 AM

Thank you, that is very helpful. I think the NMC 9630 will do very well and I can see I need to figure out how best to use the port management capabilities, it looks like a very capable device. It certainly provides me with a significant enhancement in capability and I very much like the idea of receiving remote status. My router send me email on a daily basis and all the equipment, except the UPSs, are accessible for status via the network.

I fear I cannot use PDUs as none of this is rack mounted. I have good quality surge protectors on the current UPS lines and on regular power, equipment is shared amongst them as necessary. By consolidating my failing existing UPS devices, which being small are located next to the computers they support, I shall need to run power lines specific to our two main computers which connect them to the UPS. The routers, VoIP and switch will need to run off one of the surge protectors which in turn will run off the UPS. I hope this does not void the warranty but there is no other way to handle it.

Again, thanks for your help, much appreciated.

Lawrence

Edit: Thanks KVar, I shall see what Home Depot has to offer if I can ever get out of the house - we are in the middle of the second massive storm and things are bleak indeed. At least we have power so far this time, touch wood. The first storm over the weekend took power from Saturday morning until late Monday. Joy!

Message was edited by: lawrencehare

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:43 PM . Last Modified: ‎2024-03-14 01:22 AM

0 Likes
0
945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:43 PM . Last Modified: ‎2024-03-14 01:22 AM

1) It recommends you plug things in directly because APC has no way of knowing if your extension cords, surge strips, etc. are failing and causing an issue when they get the angry call of "my UPS isn't working." Using unsupported methods of connecting your equipment can interfere with/void your EPP warranty. You can use APC PDUs, for example, to resolve this.

2) For remote management, check out the [AP9630|http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=AP9630] or [AP9631|http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=AP9631] (the latter has environmental monitoring as well). In that sense it doesn't matter what OS you're using as long as you have the internet & a browser, and you can take a look at the interfaces here: http://testdrive.apc.com/card.htm (choose one of the top 2 models)

3) In terms of outlet groups, page 9 (page 12 in PDF terms) in the manual explains the group features & settings. There is outlet group 1 and main outlet group, providing 2 different groups of 4 outlets. You can use the "Control" menu on the unit's LCD screen to configure the groups, or you can do so via the NMC if you get a card. That way you could control the groups remotely - for example, say some of the equipment on one group is hung or otherwise required rebooting. You could login to the card, issue one of the groups to reboot, and it will power cycle those 4 outlets. Or you can assign them a power on delay. Or a power off delay. Or utilize load shedding. That's all in the manual. It's important to note you can NOT control individual outlets, just 2 groups of 4 outlets. If you want to use them for this function, plan what plugs in where accordingly.

4) The RJ45 port is where you would connect the communication cable between a computer and the UPS for monitoring via the PowerChute Business Edition software (not compatible with Mac - see [compatibility chart|http://www.apcmedia.com/salestools/ASTE-6Z5QEV_R13_EN.pdf]). The network card does everything over the network and has its own IP address - it also has more advanced functionality.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:43 PM . Last Modified: ‎2024-03-14 01:21 AM

0 Likes
0
945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:43 PM . Last Modified: ‎2024-03-14 01:21 AM

I recently had yet another power failure, of which we have a number, at home and BOTH current UPS systems failed. One ran for perhaps 30 seconds, the other not at all. They are 2 years or so old and both worked fine before.

I have a mostly Mac network and we recently expanded to consolidate switches, with an HP 1810G, and I am using a couple of routers on two subnets. We support 4 systems nominally and I want two of them on UPS along with the VoIP stuff, routers and switch. Also the NAS if possible.

I would like to install a single UPS for the above equipment.

The APC site recommends the Smart-UPS 1000 VA LCD, SMT1000.

I have a few questions that I cannot seem to find answers for and I wonder if someone who knows might tell me please either where on earth to look or what is the right way to go:

1) The guide says to plug equipment directly into the UPS. I cannot do this. The equipment is in the same room but at either end of it with the switch and routers in the middle. I can run solid core custom power cable or extension cords or any combination. Why is this a requirement and how can I resolve it?

2) I would dearly love to have network management so I can track this thing remotely as well as at home. Can I do this with a Mac site? What is the best software to accomplish this if it can be accomplished at all?

3) What is the distinction between the "Main outlet" and "Switched outlet" groups? I cannot see how that is configured. The SMT1000 appears to have 8 outlets and all are on the main switch. Are these 8 outlets configurable and, if so, how?

4) The SMT1000 appears to have an RJ45 connector and a slot for a network card. What is the difference between the two.

Thanks, I wish I could find these answers on-line or in the reference material, or FAQ. Is there some other documentation I am missing?

Lawrence

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:43 PM . Last Modified: ‎2024-03-14 01:21 AM

0 Likes
0
946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:43 PM . Last Modified: ‎2024-03-14 01:21 AM

Thank you, that is very helpful. I think the NMC 9630 will do very well and I can see I need to figure out how best to use the port management capabilities, it looks like a very capable device. It certainly provides me with a significant enhancement in capability and I very much like the idea of receiving remote status. My router send me email on a daily basis and all the equipment, except the UPSs, are accessible for status via the network.

I fear I cannot use PDUs as none of this is rack mounted. I have good quality surge protectors on the current UPS lines and on regular power, equipment is shared amongst them as necessary. By consolidating my failing existing UPS devices, which being small are located next to the computers they support, I shall need to run power lines specific to our two main computers which connect them to the UPS. The routers, VoIP and switch will need to run off one of the surge protectors which in turn will run off the UPS. I hope this does not void the warranty but there is no other way to handle it.

Again, thanks for your help, much appreciated.

Lawrence

Edit: Thanks KVar, I shall see what Home Depot has to offer if I can ever get out of the house - we are in the middle of the second massive storm and things are bleak indeed. At least we have power so far this time, touch wood. The first storm over the weekend took power from Saturday morning until late Monday. Joy!

Message was edited by: lawrencehare

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore