A battery charger fault exists, Smart-UPS RT 8000 RM XL

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • A battery charger fault exists, Smart-UPS RT 8000 RM XL
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-14 11:27 PM

0 Likes
7
5347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-14 11:27 PM

A battery charger fault exists, Smart-UPS RT 8000 RM XL

I have a Smart-UPS rackmount RT 8000 RM XL that keeps giving an error message most of the time after doing a self-test. It's been doing this ever since it's was installed, about a year ago.

On the home page Recent Device Events:
05/15/2009 09:57:45 UPS: A battery charger fault no longer exists.
05/15/2009 09:57:42 UPS: A battery charger fault exists.
05/15/2009 09:51:43 UPS: Passed a self-test.
05/15/2009 09:51:27 UPS: Started a self-test.

I get e-mail for each event above. Here's the e-mail that is sent to me for the charger fault:
Name : nameapc
Location : big sky, mt
Contact : big sky resort
http://nameapc.bigsky.boyne.com
http://19.18.5.55

Serial # : NA0619021449
Device Ser #: NS0619010219
Date: 05/15/2009
Time: 09:57:42
Code: 0x012A

Critical - UPS: A battery charger fault exists.


a. Should I worry about this?
b. Can I get it to stop happening?

I've already upgraded to the most recent firmware: 477.15.W

Thanks,
--John

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-14 11:27 PM

0 Likes
0
5347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-14 11:27 PM

well the battery voltage looks fine so it seems like it might be an issue with the UPS itself. as long as the voltage is ~217vDC, then the battery charger is working fine. you could disable this event from happening on the NMC as it seems to be that the battery charger is indeed working correctly. i think its an issue with the UPS firmware which is unfortunately not field upgradable (only the network management card firmware is upgradable).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-14 11:27 PM

0 Likes
0
5347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-14 11:27 PM

I have experienced the exact same fault with our Smart-UPS RT 8000 XL. It does not happen every time a self-test is run however..

This has been ongoing for a long time now. Over a year ago APC replaced the entire unit, this did not resolve the issue. It has operated fine under actual power failures, meeting it's indicated battery runtime of 25mins.

More recently i've begun to get some messages indicating that the UPS Refused a Self Test; UPS is overloaded. (the ups is at 40% capacity all the time)

Unfortunatly i have not been able to get this issue resolved with tech support.. it may be just an issue with the self-test or firmware, but who knows!

Message was edited by: nathanv

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-14 11:27 PM

0 Likes
0
5347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-14 11:27 PM

Zakir,

Are you referring to the UPS hardware firmware? If yes, then it can not be upgraded as i Picked a winna stated above. You can only upgrade the Network Management Card firmware version not the UPS firmware.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-14 11:27 PM

0 Likes
0
5347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-14 11:27 PM

Dear Sir,

Would you please letr me know the procedure how we can upgrade version of controller as you mentioned below? Thanks
've already upgraded to the most recent firmware: 477.15.W

Rgds
zakir

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-14 11:27 PM

0 Likes
0
5347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-14 11:27 PM

the firmware you provided is actually the UPS firmware which is not upgradeable so i assume you upgraded the network management card firmware. this version can be found under Administration->General->About. AOS 3.6.1 and APP sumx 3.5.8 are the latest versions.

can you tell me what the Battery Bus voltage is and battery charge percent? This should be located under the UPS->Status menu. You could also check each battery connector with a voltmeter as well.

has the UPS operated okay during a power outage recently that you know of?

let me know what you see for those items then we can go from there.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-14 11:27 PM

0 Likes
0
5347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-14 11:27 PM

I am seeing a similiar issue with a few Smart-UPS RT 7500 XL systems my company is using.
Please let me know if you find a resolution for this.
I replaced the batteries in my systems and am still having the issue.

Thanks,
Dave

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-14 11:27 PM

0 Likes
0
5347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-14 11:27 PM

Winna,
Sorry for the slow response. I didn't notice your entry into the thread until I got the notice that Dave is having the same problem.
Here's the answers to your questions:
Status


Last Battery Transfer: Detection of low utility voltage

Internal Temperature: 99.5°F

Runtime Remaining: 19 minutes

Power

Input Voltage: 211.6 VAC

Bypass Input Voltage:

Output Voltage: 207.0 VAC

Current:

Input Frequency: 60.00 Hz

Load

Load Power: 52.0 %Watts

Apparent Load Power: 42.0 %VA

Load Current: 16.64 Amps

Battery

Capacity: 100.0 %

Battery Voltage: 213.8 VDC

External Batteries: 1


It has done it's job through several power outages since it was first installed.

I've recently, May 29th, done a Runtime calibration, and that went OK.

And you're right, those are my sumx and aos versions.

Application Module


Name: sumx

Version: v3.5.8

Date: 11/05/2008

Time: 15:08:57



APC OS (AOS)


Name: aos

Version: v3.6.1

Date: 08/13/2008

Time: 18:49:49


Regards,
--John

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-14 11:27 PM

0 Likes
0
5348
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:08 PM . Last Modified: ‎2024-03-14 11:27 PM

well the battery voltage looks fine so it seems like it might be an issue with the UPS itself. as long as the voltage is ~217vDC, then the battery charger is working fine. you could disable this event from happening on the NMC as it seems to be that the battery charger is indeed working correctly. i think its an issue with the UPS firmware which is unfortunately not field upgradable (only the network management card firmware is upgradable).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore