8941 webUI issue

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 8941 webUI issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

0 Likes
4
2318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

8941 webUI issue

Hi All,

Newbie here- I upgraded an 8941 to 6.5.6 and have the following error on the webUI:

"The application you are trying to load is incompatible with the current APC OS. Please verify the correct firmware is loaded."

I can ping/ftp/telnet to it with no issues. Here's the required info - I think... that I need:

Schneider Electric                      Network Management Card AOS      v6.5.6
(c) Copyright 2018 All Rights Reserved  RPDU 2g APP                      v6.5.6
-------------------------------------------------------------------------------
Name      : apc865400                                 Date : 09/23/2018
Contact   : Unknown                                   Time : 14:03:52
Location  : Unknown                                   User : Super User
Up Time   : 2 Days 7 Hours 49 Minutes                 Stat : P+ N4+ N6+ A!
Type ? for command listing
Use tcpip command for IP address(-i), subnet(-s), and gateway(-g)
apc>system
E000: Success
Host Name Sync: Disabled
Name:           apc865400
Contact:        Unknown
Location:       Unknown
Message:
DateTime:       09/23/2018:14:03:56
User:           apc
Up Time:        2 Days 7 Hours 49 Minutes
Stat:           P+ N4+ N6+ A!
Bootmon:        bootmon:v1.0.8
AOS:            aos:v6.5.6
App:            rpdu2g:v6.5.6
apc>about
E000: Success
Hardware Factory
---------------
Model Number:           AP8941
Serial Number:          5A1423E05606
Hardware Revision:      02
Manufacture Date:       06/07/2014
MAC Address:            00 C0 B7 86 54 00
Management Uptime:      2 Days 7 Hours 49 Minutes
Network Management Card
---------------
Model Number:           AP9537
Serial Number:          5A1423E02009
Hardware Revision:      05
Manufacture Date:       06/07/2014
Application Module
---------------
Name:                   rpdu2g
Version:                v6.5.6
Date:                   Apr 24 2018
Time:                   11:42:41
APC OS(AOS)
---------------
Name:                   aos
Version:                v6.5.6
Date:                   Mar 30 2018
Time:                   16:51:08
APC Boot Monitor
---------------
Name:                   bootmon
Version:                v1.0.8
Date:                   Apr  8 2014
Time:                   10:59:40
apc>dir
E000: Success
     3058944 Mar 30 16:51  apc_hw05_aos_656.bin
     2678276 Apr 24 11:42  apc_hw05_rpdu2g_656.bin
       45000 Sep 23 14:04  config.ini
           0 Jun  7  2014  db/
           0 Jun  7  2014  ssl/
           0 Jun  7  2014  ssh/
           0 Jun  7  2014  logs/
           0 Jun  7  2014  sec/
           0 Jun  7  2014  dbg/
           0 Jun  7  2014  fwl/
           0 Jun  7  2014  email/
           0 Jun  7  2014  lang/
           0 Jun  7  2014  pdu/
           0 Jun  7  2014  rms/

I'm thinking that I uploaded the wrong firmware and want to correct this. I'm having trouble finding the appropriate information to correct the issue. Any assistance would be greatly appreciated!

Thank you
Allan
Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

0 Likes
0
2317
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

On 9/24/2018 4:54 PM, Allan said:

I think I upgraded from 3.7.3 - can I downgrade to that? I have other PDU's running that version. I haven't been able to pull the firmware off an existing PDU via ftp though. 

Hi Allan,

FYI, the 3.X.X firmware versions for PDU are only used with the AP7XXX series models. This model (AP8941) would've never worked with that so you may just have other older models using this.

Question on the original issue - did this happen after you did anything specific - like configure email notifications or some other piece of configuration? What you're describing to me indicates maybe there is something going on here sending the PDU into a reboot loop and it stops after 6 attempts by design since the app won't load properly which then displays the message you're seeing in the web UI. If you did the reboot Szabi suggested, did you happen to be near the unit and observe if it was continually rebooting?

My first thought here is to potentially reset the PDU to defaults (keep TCP/IP settings option) or if you can afford to lost remote access and the IP address and reconfigure, to "format" it an wipe EVERYTHING. Then, observe if PDU is acting normally. This would potentially get rid of any corruption in the configuration if that is the case here. We can slowly reconfigure it to observe if it is a certain piece of configuration causing this to happen. I am not sure if you have a backup config.ini file as well and can afford to do any of this but it is how I would proceed considering the circumstances.

Of course, before proceeding, let me know if this makes sense or if you have any questions.

More info - to reset to defaults or format, we can issue one of two commands through CLI. Alternatively, to "format" specifically, you can press and hold the pinhole reset button on the PDU display itself. You press and hold for 20 seconds or so and the status LED pulses green. When it changes to amber, you let go and the process completes. Again, format function is optimal but it will wipe the TCP/IP settings. If you cannot afford that, we should try reset to defaults with the keep IP option.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

0 Likes
0
2317
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

Hi Allan,

The Stat section of the control console (A!) indicates that the application module of the firmware is not compatible with the AOS. On the other hand, SFRPDU2G656 (AP8xxx; AP7xxxB Series Rack Power Distribution Unit Firmware Revision 6.5.6) is the appropriate firmware for the AP8941. There's a chance the application failed to load - you can issue a reboot command from the console, this will cause the application to attempt to reload. If the behavior persists after reboot, reflashing the PDU firmware should restore it to normal behavior.

For convenience, I'll include the link to the firmware file as well as the knowledge base article that covers a couple of upgrade methods.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

0 Likes
0
2317
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

Hi Szabi,

I ran the reboot command, didnt fix, and then ran the firmware update based on the link you provided. It successfully upgraded the firmware but did not rectify the issue with the webUI.

Starting Upgrade 09/24/18 16:42:27 
-----------------
[09/24/18 16:42:27] 10.2.2.172: Pinging (via ICMP) device
[09/24/18 16:42:27] 10.2.2.172: Device connection passed
[09/24/18 16:42:28] 10.2.2.172: Testing FTP Log-in
[09/24/18 16:42:31] 10.2.2.172: FTP Log-in passed
[09/24/18 16:42:32] 10.2.2.172: Saving data file
[09/24/18 16:42:33] 10.2.2.172: Information --> Unable to verify previous version 
[09/24/18 16:42:33] 10.2.2.172: Saving event & configuration files
[09/24/18 16:42:33] 10.2.2.172: Transferring firmware file (1/3): Boot Monitor
[09/24/18 16:42:40] 10.2.2.172: Boot Monitor transfer successful
[09/24/18 16:42:42] 10.2.2.172: Restarting network interface
[09/24/18 16:43:34] 10.2.2.172: Device connection passed
[09/24/18 16:43:36] 10.2.2.172: Testing FTP Log-in
[09/24/18 16:43:36] 10.2.2.172: FTP Log-in passed
[09/24/18 16:43:37] 10.2.2.172: Transferring firmware file (2/3): OS
[09/24/18 16:44:25] 10.2.2.172: OS transfer successful
[09/24/18 16:44:27] 10.2.2.172: Restarting network interface
[09/24/18 16:44:47] 10.2.2.172: Pinging (via ICMP) device
[09/24/18 16:45:20] 10.2.2.172: Device connection passed
[09/24/18 16:45:22] 10.2.2.172: Testing FTP Log-in
[09/24/18 16:45:23] 10.2.2.172: FTP Log-in successful
[09/24/18 16:45:24] 10.2.2.172: Transferring firmware file (3/3): application
[09/24/18 16:46:08] 10.2.2.172: Restarting network interface
[09/24/18 16:46:18] 10.2.2.172: Pinging (via ICMP) device
[09/24/18 16:51:41] 10.2.2.172: No language pack selected
[09/24/18 16:51:41] 10.2.2.172: OS & Application transfer completed



Do you have any recommended next steps? I think I upgraded from 3.7.3 - can I downgrade to that? I have other PDU's running that version. I haven't been able to pull the firmware off an existing PDU via ftp though. 

Thank you for any assistance you can offer.
Allan

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

0 Likes
0
2318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

On 9/24/2018 4:54 PM, Allan said:

I think I upgraded from 3.7.3 - can I downgrade to that? I have other PDU's running that version. I haven't been able to pull the firmware off an existing PDU via ftp though. 

Hi Allan,

FYI, the 3.X.X firmware versions for PDU are only used with the AP7XXX series models. This model (AP8941) would've never worked with that so you may just have other older models using this.

Question on the original issue - did this happen after you did anything specific - like configure email notifications or some other piece of configuration? What you're describing to me indicates maybe there is something going on here sending the PDU into a reboot loop and it stops after 6 attempts by design since the app won't load properly which then displays the message you're seeing in the web UI. If you did the reboot Szabi suggested, did you happen to be near the unit and observe if it was continually rebooting?

My first thought here is to potentially reset the PDU to defaults (keep TCP/IP settings option) or if you can afford to lost remote access and the IP address and reconfigure, to "format" it an wipe EVERYTHING. Then, observe if PDU is acting normally. This would potentially get rid of any corruption in the configuration if that is the case here. We can slowly reconfigure it to observe if it is a certain piece of configuration causing this to happen. I am not sure if you have a backup config.ini file as well and can afford to do any of this but it is how I would proceed considering the circumstances.

Of course, before proceeding, let me know if this makes sense or if you have any questions.

More info - to reset to defaults or format, we can issue one of two commands through CLI. Alternatively, to "format" specifically, you can press and hold the pinhole reset button on the PDU display itself. You press and hold for 20 seconds or so and the status LED pulses green. When it changes to amber, you let go and the process completes. Again, format function is optimal but it will wipe the TCP/IP settings. If you cannot afford that, we should try reset to defaults with the keep IP option.

Reply

Link copied. Please paste this link to share this article on your social media post.

teramundi
teramundi
Cadet

Posted: ‎2024-04-29 01:27 PM

0 Likes
0
1402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-29 01:27 PM

Hi,

 

Since AP8941 was discontinued I can't download SFRPDU2G656 anymore. Does anyone know where I can find the latest released for AP8941 before it got discontinued? 6.5.6 would be great -- currently I run such old version that HTTPS doesn't work anymore due to outdated ciphers.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.