8832 PDUs not getting an IP address via DHCP

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 8832 PDUs not getting an IP address via DHCP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
darrell_apc
darrell_apc
Cadet

Posted: ‎2021-07-09 04:38 AM . Last Modified: ‎2024-02-14 10:16 PM

0 Likes
5
5771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:38 AM . Last Modified: ‎2024-02-14 10:16 PM

8832 PDUs not getting an IP address via DHCP

Just got 4 8832's and am trying to get them on the network. They have link, with flashing amber, but are not able to obtain a dhcp address. Sniffing packets, I don't even see a DHCP attempt. They try for IPv6, but I'm not using it on this network segment. Other devices on this network are able to obtain addresses. They are running 6.4.6, and I've cleared and check configs multiple times, as well as trying 6.4.4, no luck. SHOWS P+ N? A+ (after turning off ipv6 to test, N4? N6+ when it's enabled and has obtained a link local IP). Networking works when configured manual, but I'd really prefer DHCP. 

Any ideas or things to try?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:38 AM . Last Modified: ‎2024-01-31 03:03 AM

0 Likes
0
5766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:38 AM . Last Modified: ‎2024-01-31 03:03 AM

Hi Darrell,

Yes, we can advance replace. I will contact you via private message here in order to proceed with next steps.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:38 AM . Last Modified: ‎2024-01-31 03:03 AM

0 Likes
0
5766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:38 AM . Last Modified: ‎2024-01-31 03:03 AM

Hi Darrell,

I'd try a "format" to factory reset the PDUs, assuming these were already just new with no configuration them to lose.

To do this, hold down the pinhole reset button that is on the display. You'll want to hold it for 20 seconds. It will flash quickly green and then switch to orange/amber when you can let go. Then, it will reboot the management interface and then re-try.

Alternatively, in the console, you can check first by entering 'tcpip' command  with no options to make sure it says IPv4: enabled (as opposed to disabled). Also enter the 'boot' command to make sure it says DHCP is actually enabled for IPv4 and that APC Cookie is NOT required.

Sorry, those suggestions are a little backwards embarassed

Hopefully one of them gets you further in getting DHCP to work.

Reply

Link copied. Please paste this link to share this article on your social media post.

darrell_apc
darrell_apc
Cadet

Posted: ‎2021-07-09 04:38 AM . Last Modified: ‎2024-02-14 10:15 PM

0 Likes
0
5766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:38 AM . Last Modified: ‎2024-02-14 10:15 PM

Tried the pinhole reset, and a 'format' command, no changes. Definitely set for dhcp and no cookie (and my dhcp server has the cookie configured). Still odd that I don't even see an attempt on the wire, don't know what's up with that.

We manually configured them and they are working that way, but not optimal for us, for sure.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:38 AM . Last Modified: ‎2024-01-31 03:03 AM

0 Likes
0
5766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:38 AM . Last Modified: ‎2024-01-31 03:03 AM

Hmm, I have seen something similar once before but never got to the bottom of it. It was on one of the UPS Network Management Cards and it was only a single card as well. But I don't believe IPv4 worked at all.. you got it working on manual IP at least. I recall only seeing IPv6 working in my scenario as well no matter what I did.

If you're interested and I assume these would be in warranty, we could always try to arrange replacing one of the display modules for you in one of the PDUs which includes the network management card module in it. I could also have you return the display to me directly to look at it and the configuration and see if I can pinpoint the problem.

Let me know.

Reply

Link copied. Please paste this link to share this article on your social media post.

darrell_apc
darrell_apc
Cadet

Posted: ‎2021-07-09 04:38 AM . Last Modified: ‎2024-02-14 10:15 PM

0 Likes
0
5766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:38 AM . Last Modified: ‎2024-02-14 10:15 PM

Had to check up with my facilities guys, but it turns out we did buy these new recently, so we should be under warranty. 

I've definitely got the same scenario here, IPv6 works fine, but IPv4 doesn't and I happen to need v4. Can you advance replace the part? We've got these 4 in production with static configs now, so I'd need to get the part in before I sent one back.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:38 AM . Last Modified: ‎2024-01-31 03:03 AM

0 Likes
0
5767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:38 AM . Last Modified: ‎2024-01-31 03:03 AM

Hi Darrell,

Yes, we can advance replace. I will contact you via private message here in order to proceed with next steps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore