i am trying to configure a network card on a 3000XL. i added the arp entry to the computer but the card does not respond when i ping it. any thoughts? network connectivity is fine, and the mac address was double checked.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:51 AM . Last Modified: 2024-03-08 01:54 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:51 AM . Last Modified: 2024-03-08 01:54 AM
to clarify, after i did the reset procedure i outlined i was then able to set its ip by pinging it.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:51 AM . Last Modified: 2024-03-08 01:55 AM
Good to know!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:51 AM . Last Modified: 2024-03-08 01:55 AM
Hi,
Below is the information from our knowledge base, [Article ID 3061|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=3061]
Open up a command prompt and type the following (replacing
Arp
(MacAddress format: xx-xx-xx-xx-xx-xx)
On Mac OS X: sudo
Next, use Ping with a size of 113 bytes to assign the IP address defined by the ARP command.
For the IP address defined in step 1, use one of the following Ping commands:
Windows command format: ping
LINUX and Mac OS X command format: ping
Now, you can Telnet to the card by typing: Telnet
Use "apc" for username and password.
The biggest road block I commonly see is missing the 113 packet size specification in the ping command (which I made bold above). This is essential in getting the procedure to work.
Did you make sure you specified the switch -L or -S (depending on OS you are using) and 113 packet size noted above?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:51 AM . Last Modified: 2024-03-08 01:55 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:51 AM . Last Modified: 2024-03-08 01:55 AM
i properly did the static arp entry, and did add the -l switch and 113 byte packet size when i pinged it.
I shut the ups down, unplugged the battery and AC power, powered it back up, hit the reset button on the card, and then it worked.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:51 AM . Last Modified: 2024-03-08 01:54 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:51 AM . Last Modified: 2024-03-08 01:54 AM
to clarify, after i did the reset procedure i outlined i was then able to set its ip by pinging it.