2200 XL repeatedly cuts power

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 2200 XL repeatedly cuts power
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:43 AM

0 Likes
4
1185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:43 AM

2200 XL repeatedly cuts power

Hi,
We have an SU2200XL Tower UPS with a few servers attached to it. It appears the battery recently went out and needs to be replaced, but while we're waiting for that to happen, we're noticing that power is getting cut to the servers 2-3 times every day and it's getting critical. My hypothesis is that the power in the area isn't the greatest and there are surges or brown-outs. However, I would think the UPS should still condition the power (boost and trim) even if the battery needs replacing. Is that so? What else can I check to see if the UPS has problems or not?
Thanks,
Cameron

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:43 AM

0 Likes
0
1185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:43 AM

Hi,
We have an SU2200XL Tower UPS with a few servers attached to it. It appears the battery recently went out and needs to be replaced, but while we're waiting for that to happen, we're noticing that power is getting cut to the servers 2-3 times every day and it's getting critical. My hypothesis is that the power in the area isn't the greatest and there are surges or brown-outs. However, I would think the UPS should still condition the power (boost and trim) even if the battery needs replacing. Is that so? What else can I check to see if the UPS has problems or not?
Thanks,
Cameron

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:43 AM

0 Likes
0
1185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:43 AM

Thanks clarkson. Things just got scarier. We hunted down a serial cable (no net mgmt card) and connected one end to the UPS and as soon as the other cable end touched the serial port on a server, everything immediately powered off and the UPS no longer powers on at all (even with things unplugged). That almost sounds like a grounding issue or some nasty problem with the UPS itself.

Anyone ever seen something like that?
Many thanks in advance,
Cameron

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:43 AM

0 Likes
0
1185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:43 AM

@clarkson,
Thanks again. I did not know there was a special pin-out, though the thought crossed my mind afterward. We used a straight-through serial cable. Do you know if using the wrong pin-out could kill the UPS? I certainly wouldn't think so, but even with the cable removed, it won't power on now.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:43 AM

0 Likes
0
1185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:43 AM

Well, after the last series of events, another person I'm working with on this concluded the UPS was faulty and as it's no longer under warranty, is looking into getting a new UPS. I'm interested in trying to find out if the UPS really is damaged or not.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:43 AM

0 Likes
0
1186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:43 AM

Hi,
We have an SU2200XL Tower UPS with a few servers attached to it. It appears the battery recently went out and needs to be replaced, but while we're waiting for that to happen, we're noticing that power is getting cut to the servers 2-3 times every day and it's getting critical. My hypothesis is that the power in the area isn't the greatest and there are surges or brown-outs. However, I would think the UPS should still condition the power (boost and trim) even if the battery needs replacing. Is that so? What else can I check to see if the UPS has problems or not?
Thanks,
Cameron

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore