12,000 Watts of electronics. What UPS's and Generator should we use?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 12,000 Watts of electronics. What UPS's and Generator should we use?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

0 Likes
3
1029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

12,000 Watts of electronics. What UPS's and Generator should we use?

Hello we have computers and printers that at max load (all printers printing at the same time):

Total Amps: 207.05

Total Volts: 11,880

Total Watts: 22,793.40

Realistacally normal load would be around:

11,755 Watts / 106 Amps


We are wanting to buy a generator and ups backups that work with the generator and don't keep switching back for forth to battery power...


Any help?


Thanks!


Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

0 Likes
0
1029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

I would highly recommend contacting a local APC partner (not a reseller like Staples or chain store) and get an APC systems engineer to help you with the consulting on this. Things get a little more complicated when printers are involved - their electrical load goes up and down dramatically as they do print jobs. Usually, it is not recommended to have printers on UPS's because of the wide load swings cause issues .. Eg it causes the UPS calculated run time to swing wildly throughout the day and automated graceful shutdowns Eg powerchute that are based on available runtime calculations are impacted.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

0 Likes
0
1030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

So are you looking for one large facility size UPS and generator or multiple UPSs for individual rooms/stations along with a large generator for the facility?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

0 Likes
0
1030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

Think you need to provide a little more info. Also, clarify what you mean when you say 'total Volts: 11,800' since that isn't really a voltage you would normally use for a load.

What is your input voltage? Do you have single phase power (120 volts) or do you have three phase (120/208 or 277/480?)

Is this stuff in a single area? Or spread out?

For your UPS:

You can look at a single UPS (something between 12-16kva) or a series of smaller units (3kva)

Something like a Symmerta 16kva (SYA16K16P) will work just fine. It provides 16kva of power (about 14,000 watts) and has removable batteries, power supplies, etc.

For smaller units, a smart-ups 3000 work well.

For your Generator:

This depends a great deal on your input power. Most commercial buildings have three phase power (look for something that says 208 volts or 480 volts). Most home's have 120 volts single phase. In any case, you will need some sort of automatic transfer switch that can monitor your input power and start your generator and transfer load in the event of a power loss....

It also depends a great deal on the type of fuel you want to use. Typical installations use natural gas or Diesel. Diesel generators have the advantage of having an independent fuel source, but have to be refueled. Natural gas never run out of fuel, unless your fuel source is disrupted due to a disaster that would typically cause you to lose power in the first place (such as a hurricane).

Give us a little more info on what you are looking to do, where you live (region) and what your currently have at your facility.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

0 Likes
0
1030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:55 AM . Last Modified: ‎2024-03-19 12:28 AM

I would highly recommend contacting a local APC partner (not a reseller like Staples or chain store) and get an APC systems engineer to help you with the consulting on this. Things get a little more complicated when printers are involved - their electrical load goes up and down dramatically as they do print jobs. Usually, it is not recommended to have printers on UPS's because of the wide load swings cause issues .. Eg it causes the UPS calculated run time to swing wildly throughout the day and automated graceful shutdowns Eg powerchute that are based on available runtime calculations are impacted.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore