Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-28 02:22 AM . Last Modified: 2024-03-18 11:21 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:22 AM . Last Modified: 2024-03-18 11:21 PM
Can we distinguish if the turn off is from front panel actions, remote NMC actions or by the UPS automatically due to input/battery/output conditions?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:22 AM . Last Modified: 2024-03-18 11:21 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:22 AM . Last Modified: 2024-03-18 11:21 PM
Thank you very much, Bill.
I have a new SRT5K coming in the following week.
I will verify the event entries of action by NMC/Front Panel and report back.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:22 AM . Last Modified: 2024-03-18 11:21 PM
Hi,
If the action is due to input/battery condition it will be recorded in the NMC as an input power condition. UPS / outlet group power off caused by the front panel or by users logged into the NMC are recorded as the same type of power off.
If the power off is due to a command by PowerChute Network Shutdown that will be recorded along with the IP address of the PowerChute client/agent that sent the command.
Example of outlet group power off by NMC and front panel
09/09/2015 09:13:17 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
09/09/2015 09:13:17 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off.
09/09/2015 09:13:17 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off.
This is the UPS on battery and the outlet groups are set to power down 120 seconds after power failure
09/09/2015 09:31:33 Device UPS: On battery power in response to distorted input
09/09/2015 09:33:33 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
09/09/2015 09:33:33 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off.
09/09/2015 09:33:33 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:22 AM . Last Modified: 2024-03-18 11:21 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:22 AM . Last Modified: 2024-03-18 11:21 PM
Thank you very much, Bill.
I have a new SRT5K coming in the following week.
I will verify the event entries of action by NMC/Front Panel and report back.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.