Can we distinguish if the turn off is from front panel actions, remote NMC actions or by the UPS automatically due to input/battery/output conditions?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:22 AM . Last Modified: 2024-03-18 11:21 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:22 AM . Last Modified: 2024-03-18 11:21 PM
Thank you very much, Bill.
I have a new SRT5K coming in the following week.
I will verify the event entries of action by NMC/Front Panel and report back.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:22 AM . Last Modified: 2024-03-18 11:21 PM
Hi,
If the action is due to input/battery condition it will be recorded in the NMC as an input power condition. UPS / outlet group power off caused by the front panel or by users logged into the NMC are recorded as the same type of power off.
If the power off is due to a command by PowerChute Network Shutdown that will be recorded along with the IP address of the PowerChute client/agent that sent the command.
Example of outlet group power off by NMC and front panel
09/09/2015 09:13:17 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
09/09/2015 09:13:17 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off.
09/09/2015 09:13:17 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off.
This is the UPS on battery and the outlet groups are set to power down 120 seconds after power failure
09/09/2015 09:31:33 Device UPS: On battery power in response to distorted input
09/09/2015 09:33:33 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
09/09/2015 09:33:33 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off.
09/09/2015 09:33:33 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:22 AM . Last Modified: 2024-03-18 11:21 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:22 AM . Last Modified: 2024-03-18 11:21 PM
Thank you very much, Bill.
I have a new SRT5K coming in the following week.
I will verify the event entries of action by NMC/Front Panel and report back.