Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82128members
349642posts

UPS switching to battery and back to mains

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
7
249

UPS switching to battery and back to mains

This question was originally posted by Erez on APC forums on 8/28/2013


Hi,

About once a week our UPS switches to battery and immediately back to mains power.

Example from the log:

08/24/2013     02:09:42     UPS: A discharged battery condition no longer exists.

08/24/2013     02:09:41     UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.


We have reduced sensitivity to Low (UPS\Configuration\Power Settings\Sensitivity) but the issue persists.


We've had an electrician monitor the line for 4 days and the results came out within normal range.


Can anyone please advise why this is happening and how we can stop it?


http://s11.postimg.org/t817c2kpv/UPS.png


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
250

Re: UPS switching to battery and back to mains

This reply was originally posted by Angela on APC forums on 9/11/2013


You do have some on battery events between mid-end July and early August..

07/25/2013 20:22:57 UPS: No longer on battery power. 0x010A

07/25/2013 20:22:56 UPS: On battery power in response to distorted input. 0x0109

07/24/2013 07:05:35 UPS: No longer on battery power. 0x010A

07/24/2013 07:05:35 UPS: On battery power in response to distorted input. 0x0109

So the sensitivity might have helped with those and preventing battery transfers but it does not have anything to do with these types:

08/20/2013 14:40:19 UPS: A discharged battery condition no longer exists. 0x0108

08/20/2013 14:40:10 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately. 0x0107

Anyway, I believe the root cause is low reported runtime being within two minutes of your low battery duration which you've now lowered..

See Answer In Context

7 Replies 7
BillP
Administrator Administrator
Administrator
0 Likes
0
251

Re: UPS switching to battery and back to mains

This reply was originally posted by Angela on APC forums on 9/11/2013


You do have some on battery events between mid-end July and early August..

07/25/2013 20:22:57 UPS: No longer on battery power. 0x010A

07/25/2013 20:22:56 UPS: On battery power in response to distorted input. 0x0109

07/24/2013 07:05:35 UPS: No longer on battery power. 0x010A

07/24/2013 07:05:35 UPS: On battery power in response to distorted input. 0x0109

So the sensitivity might have helped with those and preventing battery transfers but it does not have anything to do with these types:

08/20/2013 14:40:19 UPS: A discharged battery condition no longer exists. 0x0108

08/20/2013 14:40:10 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately. 0x0107

Anyway, I believe the root cause is low reported runtime being within two minutes of your low battery duration which you've now lowered..

BillP
Administrator Administrator
Administrator
0 Likes
0
250

Re: UPS switching to battery and back to mains

This reply was originally posted by Erez on APC forums on 9/11/2013


Thanks Angela, glad we got this sorted.

BillP
Administrator Administrator
Administrator
0 Likes
0
250

Re: UPS switching to battery and back to mains

This reply was originally posted by Erez on APC forums on 9/5/2013


Can anyone please advise?

BillP
Administrator Administrator
Administrator
0 Likes
0
249

Re: UPS switching to battery and back to mains

This reply was originally posted by Angela on APC forums on 9/5/2013


Could you please attach the full logs from your Network Management Card, which you can get via FTP?

My thought is that the load is fluctuating and goes a little higher and what happens is your runtime is shrinking with the higher load, probably within 2 minutes of your low battery signaling time (the runtime remaining value that the UPS deems "low battery"), so it is trying to tell you that maybe your battery is "discharged" and doesn't have much runtime left if this is a power outage at that time. Your runtime is on the screen at about 7 minutes. The default low battery signaling time is 2 minutes so if its dropping down to 4, this could be the issue. The log files will help me verify all of this. I need event.txt, config.ini, and data.txt. Feel free to remove any IP addresses, etc before posting if you'd like.

Instructions on obtaining log files are here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...

Lastly, what model UPS is this? How old is the battery in the UPS? How long does the UPS normally run on battery with your average load (7 minutes or so)?

BillP
Administrator Administrator
Administrator
0 Likes
0
249

Re: UPS switching to battery and back to mains

This reply was originally posted by Erez on APC forums on 9/6/2013


Thanks for your response Angela, please see logs attached to this post.

Regarding your thought about the high load, the issue with the unit switching to battery and immediately back to mains started from Day 1. The load then was 55%, it has since increased as per the image in the first post.

To answer your questions I've copied this from the About page (the unit was purchased and installed on 4/2013):

Model:     Smart-UPS X 1500

Serial Number:     AS1234125326

Firmware Revision:     UPS 09.1 / MCU 09.1 / UBL 06.9 / MBL 06.0 (ID20)

Manufacture Date:     08/23/2012

Apparent Power Rating:     1440 VA

Real Power Rating:     1200 W

When the load was 55%, I ran a  test and the battery lasted for around 17 minutes. I haven't performed a test since the load has increased.

Attachments
BillP
Administrator Administrator
Administrator
0 Likes
0
249

Re: UPS switching to battery and back to mains

This reply was originally posted by Angela on APC forums on 9/6/2013


To clarify, the events from your first post DO NOT indicate the UPS switching back and forth from battery. They indicate your runtime is low and typically that happens when it has been discharged. It can also happen in your situation with no battery events and a charged battery but just plain ol low runtime. The batteries are probably around a year old, just as the UPS is. If there are not frequent battery transfers or a calibration was not done to recalculate available runtime, we may need to do that.

Also, I am missing event.txt and need that place. I did not need dump.txt and debug.txt.

Lastly, your low battery duration in the config.ini has been raised from two minutes to five (LowBatteryDuration=5 per config.ini). This means when your reported runtime comes within two minutes (or below) 7, you'll see this alarms but again, it does not indicate any battery operation.


I'll need event.txt to verify nothing else is going on or that there are not other events you're seeing to indicate battery operation because so far, I see nothing to indicate it has been transferring. So, it makes sense that changing sensitivity did not do anything.

BillP
Administrator Administrator
Administrator
0 Likes
0
249

UPS switching to battery and back to mains

This reply was originally posted by Erez on APC forums on 8/29/2013


Hi,

About once a week our UPS switches to battery and immediately back to mains power.

Example from the log:

08/24/2013     02:09:42     UPS: A discharged battery condition no longer exists.

08/24/2013     02:09:41     UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.


We have reduced sensitivity to Low (UPS\Configuration\Power Settings\Sensitivity) but the issue persists.


We've had an electrician monitor the line for 4 days and the results came out within normal range.


Can anyone please advise why this is happening and how we can stop it?


http://s11.postimg.org/t817c2kpv/UPS.png