Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82415members
349924posts

Smart UPS 2200 as additional batteries??

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

Solved
Michal_apc
Cadet
0 Likes
1
94

Smart UPS 2200 as additional batteries??

This was originally posted on APC forums on 11/3/2008


I have two Smart UPs 2200
currently they support one server each and I dont have any UPS software installed at all
for shutdown or monitoring software or connection cables as they came "second hand"

If i was to get two new UPS say SmartUPS 1500VA USB

Would I be able to use and control these Older but larger UPS 2200 as additional battery storage
for the new ones by connecting them together somehow??

thanks


Accepted Solutions
Erasmus_apc
Sisko
Sisko
0 Likes
0
94

Re: Smart UPS 2200 as additional batteries??

This was originally posted on APC forums on 11/4/2008


No, the Smart-UPS systems cannot be paralleled or daisy-chained for additional capacity or runtime. The only way to get additional runtime is on a Smart-UPS "XL" unit using actual external battery packs.

See Answer In Context

1 Reply 1
Erasmus_apc
Sisko
Sisko
0 Likes
0
95

Re: Smart UPS 2200 as additional batteries??

This was originally posted on APC forums on 11/4/2008


No, the Smart-UPS systems cannot be paralleled or daisy-chained for additional capacity or runtime. The only way to get additional runtime is on a Smart-UPS "XL" unit using actual external battery packs.