Hello,
I'm from Peru (220Vac/60Hz) and we are resellers of APC, we usually sell SURT___XLI, but we always have a doubt about if we can sell SURT___XLT (3kVA, 5kVA, 6kVA), the user manual says both can be programmed with an 220Vac output voltage, and the input voltage is from 160Vac - 280Vac, so I really don't think there's a problem to sell one or the other, or is there a difference between them?
Manual: [SURT6000XLI & SURT6000XLT|http://www.apcmedia.com/salestools/ASTE-6Z8LL8_R1_EN.pdf]
Greetings,
HA
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:49 PM . Last Modified: 2024-03-14 11:35 PM
You cannot program the SURT6000XLT with any output voltages other than 208 or 240. The listed voltages are, unfortunately, a mistake in the user manual.
Another difference between the two is the fact that they take different wiring/power inputs. As you know, a 230 XLI model would look for HNG 230/220, but the XLT models look for "North American/US" HHG (L1,L2,G) wiring setup.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:48 PM . Last Modified: 2024-03-14 11:35 PM
Thank You Erasmus,
I didn't know the user manual have a mistake, good to know.
HA
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:49 PM . Last Modified: 2024-03-14 11:35 PM
You cannot program the SURT6000XLT with any output voltages other than 208 or 240. The listed voltages are, unfortunately, a mistake in the user manual.
Another difference between the two is the fact that they take different wiring/power inputs. As you know, a 230 XLI model would look for HNG 230/220, but the XLT models look for "North American/US" HHG (L1,L2,G) wiring setup.
Link copied. Please paste this link to share this article on your social media post.