Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82421members
349938posts

Changing SNMP trap reporting interval from NMC/SmartUPS 2200XL

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

Solved
sdineen_at_orchid.com_apc
Crewman
Crewman
0 Likes
4
168

Changing SNMP trap reporting interval from NMC/SmartUPS 2200XL

This was originally posted on APC forums on 10/5/2007


Hi. We've just installed NMC cards into all our 2200 RMXL UPS units. Firmware has been upgrade to 3.5.5 across the board. We setup our What'sUp Pro reporting server to capture traps and send emails for on battery, batteryfailed, powerRestored alerts,etc. Recently we had a battery fail a self test and it sent traps every 2 minutes, all night so that all folks on the distribution received about 400 + alerts/emails. Is there away to change this interval? I don't see anything on the NMC. Is there a way to modify the MIB itself? Thanks!

Message was edited by: sdineen@orchid.com


Accepted Solutions
Cap1_apc
Lt. Commander
Lt. Commander
0 Likes
0
168

Re: Changing SNMP trap reporting interval from NMC/SmartUPS 2200XL

This was originally posted on APC forums on 1/13/2009


Also - you probably only have to make the configuration change once.

From there you can FTP to the NMC and get the config.ini file. You can upload that config.ini file (or parts of it) to your other cards and they will assume the same settings.

More info here:
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=8979

See Answer In Context

4 Replies 4
Faceman22_apc
Ensign
Ensign
0 Likes
0
168

Re: Changing SNMP trap reporting interval from NMC/SmartUPS 2200XL

This was originally posted on APC forums on 10/9/2007


Hi.

Most the traps are persistent by default, as you found out.=)

Under Administration>Notification section, you can select Event Actions, by event, and under Power Events, Input Line Status you can then select On Battery event and set delays, and repeat intervals for any configured SMTP, SNMP, etc..... reciever on the card.

BillP
Administrator Administrator
Administrator
0 Likes
0
168

Re: Changing SNMP trap reporting interval from NMC/SmartUPS 2200XL

This reply was originally posted by Angela on APC forums on 1/12/2009


yes, you should be able to configure by severity and change the delays for information, warning, or critical events or events by group such as power events, system events, etc

this is under Administration->Notifications and on left hand side of the 3.x firmware.

thebassetthound_apc
Cadet
0 Likes
0
168

Re: Changing SNMP trap reporting interval from NMC/SmartUPS 2200XL

This was originally posted on APC forums on 1/9/2009


IS there a way to do a "bulk" update of all traps to say 15mins, I don't fancy having to go through 100 options to set them all manually. I also don't fancy getting an email every 2 mins that the power is off or the room is 1 degree over temp 😉

Cap1_apc
Lt. Commander
Lt. Commander
0 Likes
0
169

Re: Changing SNMP trap reporting interval from NMC/SmartUPS 2200XL

This was originally posted on APC forums on 1/13/2009


Also - you probably only have to make the configuration change once.

From there you can FTP to the NMC and get the config.ini file. You can upload that config.ini file (or parts of it) to your other cards and they will assume the same settings.

More info here:
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=8979