Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82251members
349809posts

About Smart-UPS SMT1000I line interactive ups Issue

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
3
194

About Smart-UPS SMT1000I line interactive ups Issue

This question was originally posted by john on APC forums on 4/12/2016


I am using smart ups smt 1000I ups for over two years old. Recently I found my network device (Cisco   Router ,Cisco  switch) was rebooted when  power  outage occurred.

From event log,I can only see the ups was switch  to battery from utility power when network device was rebooted

I have no idea that why my network device will rebooted when ups start to switch to battery from utility power 

Do you have any comments for that?

Please Advise


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
194

Re: About Smart-UPS SMT1000I line interactive ups Issue

This reply was originally posted by Bill on APC forums on 4/14/2016


Hi,

On 4/14/2016 3:00 AM, john said:

I would like to know there is any different of ups power transfer method between smt1000I and SMX3000RMHV2U when power outage occurred .

No. There is no difference in transfer times between a SMT1000i and SMX3000RMHV2U. They are both line interactive Smart-UPS. 

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
194

Re: About Smart-UPS SMT1000I line interactive ups Issue

This reply was originally posted by Bill on APC forums on 4/13/2016


Hi,

The Smart-UPS has a transfer time from when it is passing AC to running on battery. If the sensitivity is set to Normal the transfer time should be 2-4 milliseconds. Using the UPS front panel scroll to Configuration hit the enter key to enter Configuration. Scroll down to Menu Type and verify the menu is in Advanced mode. When in Advanced mode scroll down to Sensitivity. It should be set for Normal. If it is not set to Normal then monitor the equipment the next time there is an outage. If the Router and Switch still drop that indicates their power supplies cannot handle the slight transfer time and you will need to replace the Line Interactive UPS with an On-line model. With an On-line UPS the power is always flowing from the batteries and inverter so there is no transfer time.

BillP
Administrator Administrator
Administrator
0 Likes
0
193

Re: About Smart-UPS SMT1000I line interactive ups Issue

This reply was originally posted by john on APC forums on 4/14/2016


   On 4/13/2016 9:56 PM, Bill said:

Hi,

The Smart-UPS has a transfer time from when it is passing AC to running on battery. If the sensitivity is set to Normal the transfer time should be 2-4 milliseconds. Using the UPS front panel scroll to Configuration hit the enter key to enter Configuration. Scroll down to Menu Type and verify the menu is in Advanced mode. When in Advanced mode scroll down to Sensitivity. It should be set for Normal. If it is not set to Normal then monitor the equipment the next time there is an outage. If the Router and Switch still drop that indicates their power supplies cannot handle the slight transfer time and you will need to replace the Line Interactive UPS with an On-line model. With an On-line UPS the power is always flowing from the batteries and inverter so there is no transfer time.

Hi Bill,

Thanks for your reply.

I have checked the sensitivity setting  on smt1000I ups , it is set to Normal.

However I have no any network device power drop on another site office. There is be using SMX3000RMHV2U line interactive ups and same model & specification of cisco  switch & cisco  router.Also,the sensitivity setting of ups is set to Normal.   

The network device power still normal when power outage occurred.

I would like to know there is any different of ups power transfer method between smt1000I and SMX3000RMHV2U when power outage occurred .

Please Advise

John

BillP
Administrator Administrator
Administrator
0 Likes
0
195

Re: About Smart-UPS SMT1000I line interactive ups Issue

This reply was originally posted by Bill on APC forums on 4/14/2016


Hi,

On 4/14/2016 3:00 AM, john said:

I would like to know there is any different of ups power transfer method between smt1000I and SMX3000RMHV2U when power outage occurred .

No. There is no difference in transfer times between a SMT1000i and SMX3000RMHV2U. They are both line interactive Smart-UPS.