Com'X Analog Input for WAGES

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Com'X Analog Input for WAGES
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
98
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
43
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
Marvin_Foster
Ensign Marvin_Foster Ensign
Ensign

Posted: ‎2015-11-12 07:27 AM

1 Like
2
1076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-11-12 07:27 AM

Com'X Analog Input for WAGES

I am trying to understand how the data logging works for the Analog inputs in the Com'X series.

For most WAGES implementations I would expect to get a flow values via an analog signal (Gal/Min, SCF/Min, etc)  The important information needed from that is usage (Gallons, MSCF of gas, etc).  What I don't see is any local integration of the analog signal to create a usage value.  Am I missing something?

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2015-11-16 12:31 AM

2 Likes
1
941
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-11-16 12:31 AM

Overview

Each Analog Input can accept 4 types of sensor :

  • PT100,
  • PT1000,
  • 0-10V and
  • 4-20 mA.


The 2 first types of sensors are temperature sensors, and their conversion rule "Resistor = f (Temperature)" is known,

Thus the device types of those sensors are already available as a built-in device type in the Com'X


For other sensors (0-10V and 4-20mA), the type of measurement cannot be known by advance.

it will be first necessary to create a custom device type (where you will assign the type of measurement, and the conversion rule)


1st simple Example : PT1000 temperature sensor

You just have to connect your sensor and declare them as PT100  or PT1000,

Declare AI.png

As the PT1000 is a built-in device type, it is already available in the list of sensors (named as Built-in models) :

Standard device type.png

And you will get directly the value of the temperature in the HMI.

Exploit PT1000.png

2nd more complex Example : Humidity sensor SHO-100

Step one : define the custom model

This sensor does not belong to the built-in model. It is thus necessary to define it using the "Custom library"

You have to create a  new model,

Give it a name ("SHO-100"),

Define the measurement provided by this sensor as the "Element" field ("Humidity rate") and

Define the conversion rule by specifying the min and max value

Custom SHO-100.png

NOTE : some measurement are already known (Humidity rate, CO2 Level, Level), if you select one of them, the unit can be selected in a list)

If the measurement of your sensor does not belong to the list, it is possible to create a "Custom" one and enter a "Custom" unit


Using the custom model

Once the model has been created,it will appear in the list of AI choice and it will be possible to use it :

Standard and custom device type.png

And you will get directly the value of the Humidity Rate in the HMI.

Exploit SHO-100.png

NOTE : If you have done a mistake in the model, you can modify it, and all the instances of this model will be changed

You can also import / export your model to another Com'X


About Modbus-TCP server

The AI are also available through the Modbus-TCP server :

If AI-1 is used, its value (coded as Float32) is available at registers 10000 and 10001 (Most significant register first)

If AI-2 is used, its value (coded as Float32) is available at registers 10002 and 10003 (Most significant register first)

If the device type is a built-in model (PT100 or PT1000), the value returned by the Modbus-TCP server is the temperature value

If the device type is a custom model (0-10V or 4-20mA), the value returned by the Modbus-TCP server is the raw value : voltage or current value

Modbus-server.png


     Regards

     Jef

See Answer In Context

Reply
Replies 2
Anonymous user
Not applicable

Posted: ‎2015-11-16 12:31 AM

2 Likes
1
942
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-11-16 12:31 AM

Overview

Each Analog Input can accept 4 types of sensor :

  • PT100,
  • PT1000,
  • 0-10V and
  • 4-20 mA.


The 2 first types of sensors are temperature sensors, and their conversion rule "Resistor = f (Temperature)" is known,

Thus the device types of those sensors are already available as a built-in device type in the Com'X


For other sensors (0-10V and 4-20mA), the type of measurement cannot be known by advance.

it will be first necessary to create a custom device type (where you will assign the type of measurement, and the conversion rule)


1st simple Example : PT1000 temperature sensor

You just have to connect your sensor and declare them as PT100  or PT1000,

Declare AI.png

As the PT1000 is a built-in device type, it is already available in the list of sensors (named as Built-in models) :

Standard device type.png

And you will get directly the value of the temperature in the HMI.

Exploit PT1000.png

2nd more complex Example : Humidity sensor SHO-100

Step one : define the custom model

This sensor does not belong to the built-in model. It is thus necessary to define it using the "Custom library"

You have to create a  new model,

Give it a name ("SHO-100"),

Define the measurement provided by this sensor as the "Element" field ("Humidity rate") and

Define the conversion rule by specifying the min and max value

Custom SHO-100.png

NOTE : some measurement are already known (Humidity rate, CO2 Level, Level), if you select one of them, the unit can be selected in a list)

If the measurement of your sensor does not belong to the list, it is possible to create a "Custom" one and enter a "Custom" unit


Using the custom model

Once the model has been created,it will appear in the list of AI choice and it will be possible to use it :

Standard and custom device type.png

And you will get directly the value of the Humidity Rate in the HMI.

Exploit SHO-100.png

NOTE : If you have done a mistake in the model, you can modify it, and all the instances of this model will be changed

You can also import / export your model to another Com'X


About Modbus-TCP server

The AI are also available through the Modbus-TCP server :

If AI-1 is used, its value (coded as Float32) is available at registers 10000 and 10001 (Most significant register first)

If AI-2 is used, its value (coded as Float32) is available at registers 10002 and 10003 (Most significant register first)

If the device type is a built-in model (PT100 or PT1000), the value returned by the Modbus-TCP server is the temperature value

If the device type is a custom model (0-10V or 4-20mA), the value returned by the Modbus-TCP server is the raw value : voltage or current value

Modbus-server.png


     Regards

     Jef

Reply
Mauricio_G
Crewman Mauricio_G Crewman
Crewman

Posted: ‎2015-11-16 06:07 AM

0 Likes
0
941
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-11-16 06:07 AM

Hi Jef,

That's perfect, I'll check the variables on my devices, but it should be straight forward.

Thanks a lot.

Mauricio

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of